Discuss EICR, opinions please... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

polo1

-
Arms
Reaction score
633
....on a property rewired approx three years ago with no local isolation for the electric oven (using the cooker circuit) - Code 2 or 3?
Regards.
 
I like local dp isolation, but don't think you can code it. Is it table 3 that states you can use the circuit breaker as means of isolation.?
 
Tbh, I was being a bit lazy in asking the question here, as my byb is in the hands of another. I was/am having brain fade on this. I know there is mention of local & remote isolation, but couldn't recall if isolation beyond the mcb is an actual requirement. I'm suitably embarrassed
 
Tbh, I was being a bit lazy in asking the question here, as my byb is in the hands of another. I was/am having brain fade on this. I know there is mention of local & remote isolation, but couldn't recall if isolation beyond the mcb is an actual requirement. I'm suitably embarrassed
Don't worry about it Polo, we are all here to help each other, My memory is rubbish can't remember what I done yesterday.lol
 
If the equipment or whatever broke down, caught fire whatever the manufacturer would certainly turn around and say "well you did not follow our instructions regards installation so we cant help"
 
Fortunately, we no longer have to comply with manufacturer's instructions, just take account of them.
LOL. It's debateable whether that is really any different. If you "take account" of the instructions you might need good reason to then dismiss them.
 
Fortunately, we no longer have to comply with manufacturer's instructions, just take account of them.

I would be very carefull with that attitude, if an items fails and causes damage and manucarurers instructions have not been followed you are then liable.. extractor fans are prime example of this not being fused down to 3 amp. Ive read of instances where fires caused by extractor fans, the spark not fused down and then liable.
 
You have to remember that the majority of these are just the manufacturer desperately looking for a way out of paying.
For instance the change from a 6A MCB to a 3A fuse will make very little difference in the majority of faults, the "stalled" current of an extractor fan is unlikely to reach 6A and a short circuit will be in hundreds of amps and disconnect instantly either way. The fault current would have to be between 6 and 18A to make a difference and this is unlikely.

If an item has been installed professionally and safely there is little the manufacturer can really do in most cases, except try it on and succeed.
 
That is my point they will try it on and also suceed, in this case why would you you risk not installing a inline fuse, just use a fan iso insert and fuse insert on a 1gang faceplate costs few pounds, in the terrible case of a fan going on fire then the manufacturers have no1 to blame! I know as well as you that a 3amp fuse will make little diference, but a court will see it clearly in the MI and it will look like the installer has ignorered it therefore taking responsibility!
 
The requirement had to be changed.
Some instructions are physically impossible.
Others don't comply with BS7671.

To be honest, a recommendation for the rating of a fuse, is a little different from an instruction as to how fixed wiring should be installed.
 
For those saying the MI must be followed, what would you do if the MI were blatantly wrong (which I've seen on many an occasion)? Would you still follow them blindly, or would you apply a little common sense and decide for yourself the best course of action? If you'd do the latter, how is that any different than choosing not to provide a local isolator for an appliance?

I suppose a common example is if you had to get a fridge cable through a unit. The MI says you must use the fitted plug. Keeping that intact is going to be a nice big hole somewhere in the unit. Option 2 is you could cut the end off, drill a nice snug smaller hole, and attach another plug leaving a tidier job. It's no less safe than it was with the fitted plug.
 
For those saying the MI must be followed, what would you do if the MI were blatantly wrong (which I've seen on many an occasion)? Would you still follow them blindly, or would you apply a little common sense and decide for yourself the best course of action? If you'd do the latter, how is that any different than choosing not to provide a local isolator for an appliance?

I suppose a common example is if you had to get a fridge cable through a unit. The MI says you must use the fitted plug. Keeping that intact is going to be a nice big hole somewhere in the unit. Option 2 is you could cut the end off, drill a nice snug smaller hole, and attach another plug leaving a tidier job. It's no less safe than it was with the fitted plug.

Well reg - 134.1.1 - If you choose to not follow that reg you blatently ignoring bs7671 & MI, i dont think that would look good in a court room. I think a plug top is a diferent situation not being part of the fixed installation, but i for one do not cut sealed plugs on appliances as it invalidates the appliances warranty, and a hole cut just right for plug at the back of the unit which will be full of stuff isnt an eyesore, plus when the customer changes the appliance they dont need to call an electricin in or try and do tge plug themselves. Whats your position on 3amp fuses in fans that require them in theor MI HT.?
 
Well reg - 134.1.1 - If you choose to not follow that reg you blatently ignoring bs7671 & MI, i dont think that would look good in a court room.

In the BYB it states under 134.1.1 that "The installation of electrical equipment shall TAKE ACCOUNT of manufacturers' instructions", where as it used to say that they must be followed. The reason they probably changed it is because people would blindly follow incorrect advice just because it looked all official like from the manufacturer. It's perfectly legitimate to TAKE ACCOUNT of MI but disregard them all the same if you feel (as a trained professional) the need.

As for 3A fuses, I'd have nothing to add to what Richard has already said at the top of the page.
 

Reply to EICR, opinions please... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
533
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
I trained as a electrician in the 70s but have long since retired. Just had an EICR test done on my property in advance of selling. I have a 60s...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock