Discuss EICR question, OLD AC RCD- code 3 or no code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

So a Landlord could have had a brand new CU fitted in August 2022 to bring him up to regs and 6 months later which would be March 2023 has a change of tenant and has a Condition report done only to be told his 6 month old RCD is a C3...........NO
Now if he has extra sockets or a new circuit fitted then that's a different matter and code
 
So a Landlord could have had a brand new CU fitted in August 2022 to bring him up to regs and 6 months later which would be March 2023 has a change of tenant and has a Condition report done only to be told his 6 month old RCD is a C3...........NO
Now if he has extra sockets or a new circuit fitted then that's a different matter and code

Improvement recommended, due to regulatory changes. No work needs to be carried out and nothing is potentially dangerous.

Provided the inspector provides an explanation, I can't see a problem.

I'd expect more annoyance if additional work was required for the installation of a new circuit, if CU was changed last August, but coding wouldn't be a factor there.

I'd also add that, while we can not be held responsible for changes to regulations, it would have been remiss of any installer to be fitting type AC RCD protection in August 2022.
 
Last edited:
So a Landlord could have had a brand new CU fitted in August 2022 to bring him up to regs and 6 months later which would be March 2023 has a change of tenant and has a Condition report done only to be told his 6 month old RCD is a C3...........NO
Now if he has extra sockets or a new circuit fitted then that's a different matter and code
As I have stated already, coding it as a C3 gives the client the option of improving the safety of the installation. Many landlords would want this to be made clear so that they can take responsible action.
And if they decide not to act at this time, C3 can still result in a satisfactory EICR. There has to be a point where we start to look forward in terms of keeping up to date with safety improvements, and not give in to inertia just because it might cost money.
 
Improvement recommended, due to regulatory changes. No work needs to be carried out and nothing is potentially dangerous.

Provided the inspector provides an explanation, I can't see a problem.

I'd expect more annoyance if additional work was required for the installation of a new circuit, if CU was changed last August, but coding wouldn't be a factor there.

I'd also add that, while we can not be held responsible for changes to regulations, it would have been remiss of any installer to be fitting type AC RCD protection in August 2022.
Yes i agree it would be remiss....but i see this a lot because the wholesalers were knocking them out cheap to get rid of stock
 
Improvement recommended, due to regulatory changes. No work needs to be carried out and nothing is potentially dangerous.
...

Absolutely - in just the same way when we find an installation that has the old black and red colours - due to regulatory changes we also must highlight this as a C3 - Improvement Recommended.

After all if the regulations do change making previously acceptable aspects no longer compliant, then it has to be across the board, if we must highlight one particular thing as C3 because it's non-complient we must apply this globally applying C3s on everything that is no longer completely compliant with the latest version of the regs.

Of course the customer doesn't have to address the 10-20 C3s or whatever results from the automatic C3 for anything not completely in line with the most recent regs.

OR

Should we apply engineering judgements based on the current version of the regs?

So red & black wiring, although not in line with current regs, wouldn't actually be an issue whatsoever, - changing to the new colours wouldn't really improve anything from a safety, usability, or end user point of view - so why Recommend an improvement when there actually isn't any real improvement.

Similarly, if the RCD type isn't an issue in this application again if changing it wouldn't really improve anything from a safety, usability, or end user point of view - why Recommend an improvement when there actually isn't any real improvement.

On the other hand if the RCD is on circuits that would benefit from changing the type this would be an improvement, anything from a safety, usability, or end user point of view, so deserves a C3.

On the other, other hand (?) If the RCD is actually being blocked by dc, (or clearly almost certainly will be blocked - say on a circuit where the customer uses a silly "granny charger") - then it becomes a C2


This is my problem btw with many questions about "I have x, what code?" - the answer is C1, C2, C3 or nothing for the same "issue" even on the same site depending upon the circumstances.

An easy example is "premature wiring collapse" - a drooping cable across an entrance is C1, a cable affixed, but which would drop across an exit in the event of a fire, would be C2, a cable affixed, but which would drop along a wall - out of the way in the event of a fire, would be C3, or a cable affixed, but which would drop down just a few inches - well out of harms way in the event of a fire, wouldn't attract anything.
 
@Julie.

My thinking, the capacity of which is limited, is that potential for issue exists due to the way in which this protective device operates and the fact that one new appliance has the potential to change that operation.

I take the above points, but believe old wiring colours aren't a good comparison as they will have no impact on a householder who doesn't tinker with fixed wiring in their home. Replacement of an old or failed appliance doesn't generally require consultation. Given that a significant number of domestic EICRs are carried out for the sole reason of complying with rental legislation, I feel this adds another layer to the issue as no one can look around the property and assume risk on the basis of appliances present at time of inspection.

Similarly, the issue of premature collapse doesn't generally involve variables - risk exists or it does not and remedial work is quite simple.

Furthermore, most inspectors who carry out EICRs won't have any means of detecting DC leakage, much less any interest in attempting to do so.

What I have taken away from this discussion is that a number of opinions in favour of not coding type AC RCDs are based on customer reaction. While I understand that position, I don't consider customer sensibilities to be a factor of testing and inspecting. It's an interesting discussion about what, on the surface, appears to be a simple issue.
 
Another way to look at this might be that if we do not code an item as C3 because it complied at the time of installation, we are taking away the client's choice to make a significant improvement to the safety of the installation. They would be unaware of the improvements made to the wiring regulations, and of changes that are happening in the world of technology that can both contribute to safety, but also to introduce new potential hazards (in this case the DC blinding of older RCDs).
Coding it C3 at least makes the client aware that an improvement to the safety of the installation is actually an option.
That's an interesting way of saying 'covering my arse' :)
 
But that would be at the inspector's discretion?

Now that you raise this point, I can't help wondering if it is possible to issue a satisfactory report containing a C2?
I think the point is C2 is an immediate "unsatisfactory" due to a clearly identified danger following a single fault, whereas C3 are not that dangerous in themselves.

But if you found an installation where practically everything was so rubbish it merited C3 you might come to the conclusion that overall it is not to a satisfactory degree of safety.
 
I think the point is C2 is an immediate "unsatisfactory" due to a clearly identified danger following a single fault, whereas C3 are not that dangerous in themselves.

But if you found an installation where practically everything was so rubbish it merited C3 you might come to the conclusion that overall it is not to a satisfactory degree of safety.

I read more on this last night and it makes perfect sense when viewed in black and white.
 
My interpretation is that anything that is not to the current version of the regs merits at least a C3. Every reg change should hopefully be an improvement, so anything which hasn't incorporated that improvement should be coded 'improvement recommended'.
There are many things I've installed in complete compliance with the regs that a few months later would attract a C3 on an EICR.
The plastic cased CUs in all my properties except one is an example that comes to mind, and now the type AC RCDs in those CUs.
 
I then said - in that instance how would you code a voltage operated ELCB- it complied with the regs at the time of the install and you can test it with an RCD tester and the test button works so....
Going back to this point...
In almost all cases I consider this a legitimate C2, as:
...the chances are there'll be a lower impedance fault path via any metal services than via the earth rod, and the VOELCB needs current to flow via the earth rod to operate
...it will do nothing at all about a human caught between live and real earth

So we are only one step away from live parts and no ADS unless the Ra is exceptionally good.
As they were removed for safety reasons about 37 years ago I doubt I'd get as far as coding it - I'd just replace it.

Have you ever got one to trip with an RCD tester btw? I'd assume it would need more than 30ma to do anything as it's basically a solenoid.
 
Last edited:
It's been decades since I came across a VOELCB, but I changed them on sight back then, so it's definitely a C2 if I found one now. They are not residual current devices, so I believe C2 is entirely justified.
Might be entirely wrong, but I have a recollection that the voltage operated devices had a resistance of around 60 ohms, so about 1.8V on the earth wire to trip it off.
 
Might be entirely wrong, but I have a recollection that the voltage operated devices had a resistance of around 60 ohms, so about 1.8V on the earth wire to trip it off.
Completely academic now, I know....one of my very old books says the requirement was based on the Ze, if 200 ohms then tripping at <=24v was required and if 500 ohms it had to trip at <=40v.
The 14th Edition says the correct test is a test voltage not exceeding 45v applied to N and E on the installation side and it must trip instantaneously.
It may be that manufacturers did a lot better than the minimum requirement though!
 
C3 for me & in all case’s regarding now & then situations…it covers your opinion/competence & is a recommendation for improvement in so many “grey” areas the Regs present to us those situations
 

Reply to EICR question, OLD AC RCD- code 3 or no code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. What are your thoughts on coding type AC RCDs when doing EICR's? I understand the issue on DC currents preventing RCd's from functioning...
Replies
10
Views
9K
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K
Hello sparkly people Im a total beginner around how electricity really works. Ive recently been made redundant from ground works in construction...
Replies
2
Views
786
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
748
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock