Discuss EICR recommendations in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
12
Just a quick one. Testing a house that's install is about 20 year old. Obviously hasn't got a metal clad DB, earthing is only 10mm. Would you put these down in the reccomendations? Even though these items were perfectly fine when it was installed?
Lee
 
Non metal fuseboard I personally wouldn't comment on but the 10.0 earthing conductor I would.
 
Just a quick one. Testing a house that's install is about 20 year old. Obviously hasn't got a metal clad DB, earthing is only 10mm. Would you put these down in the reccomendations? Even though these items were perfectly fine when it was installed?
Lee
What size are the L/N tails?
 
I'm with Murdoch - TNS or TT and that 10mm is probably more than adequate. I recently installed a 10mm on a rewire because it was a tricky run and 16mm would have made it much harder to pull. Adiabatic only needed a 4mm, so 10mm more than enough.
 

Reply to EICR recommendations in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
707
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
273

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock