Discuss Eicr in the UK Electrical Forum area at ElectriciansForums.net

J

joehat

Sub mains to 2 x outbuildings.

Is the only way for this to pass an eicr is for the cables to be dug up and redone, I am going to make safe and add rcds by main fuse??

No armour or protection??
8e29dce8603da19561b01b3794b40481.jpg
7a1381191aa1c939a355aa8a83225f0e.jpg
49b2e033147b8669e6134db6b500718b.jpg
 
So its an EICR - a few C2's, and unsatisfactory report, submit your invoice with report and walk away, when paid, discuss remedial works with client.
 
They looked like 16 mm t/e
I would put a c2 but if they wasn't gonna have it dug up Ect would you say an rcd would make it a lot safer and that's what I'm suggesting,
 
Last edited by a moderator:
You cannot pass or fail an EICR, it is a report not an exam. You are giving a report on the condition of the installation in its current condition including an overall assessment of either satisfactory or unsatisfactory.

As for suggestions to rectify that problem: disconnecting it would be the cheapest soloution. Without inspecting that lot I can't really give an opinion on whether it is salvageable of not.
 
You cannot pass or fail an EICR, it is a report not an exam. You are giving a report on the condition of the installation in its current condition including an overall assessment of either satisfactory or unsatisfactory.

As for suggestions to rectify that problem: disconnecting it would be the cheapest soloution. Without inspecting that lot I can't really give an opinion on whether it is salvageable of not.

Thank you. I know it's satisfactory or unsatisfactory.

As you have no valid opinion apart from picking at my wordings, then I'd appreciate no more comments from you.

Thanks
 
What's on the other end of these submains?

An office to one and an outbuilding/bedsit in another.

I would class it as unsatisfactory in a report but as the client will not want to disconnect, I would feel the best option is to recommend rcd protection at the points in then picture as a minimum. Obviously ideally I would recommend armoured cable or equivalent, but the cost i feel unless it's compulsory eg selling of a house then, It won't be a consideration to them.
 
An office to one and an outbuilding/bedsit in another.

I would class it as unsatisfactory in a report but as the client will not want to disconnect, I would feel the best option is to recommend rcd protection at the points in then picture as a minimum. Obviously ideally I would recommend armoured cable or equivalent, but the cost i feel unless it's compulsory eg selling of a house then, It won't be a consideration to them.

As I previously stated you are there to do a report, if it's unsatisfactory with c2's and the customer ignores the report, there is nothing you can do.

Move on to the next job.....
 
An office to one and an outbuilding/bedsit in another.

I would class it as unsatisfactory in a report but as the client will not want to disconnect, I would feel the best option is to recommend rcd protection at the points in then picture as a minimum. Obviously ideally I would recommend armoured cable or equivalent, but the cost i feel unless it's compulsory eg selling of a house then, It won't be a consideration to them.

wouldnt recommend a upfront rcd- if that meter cupboard is remote from the office and bedsit- then any nuisence tripping in those outbuildings would knock that rcd out and they would loose all power
 
Thank you. I know it's satisfactory or unsatisfactory.

As you have no valid opinion apart from picking at my wordings, then I'd appreciate no more comments from you.

Thanks

To be honest I couldn't give two hoots what you appreciate.

If that black cable is NYYJ/hi tuff or similar then depending on installation method it may be salvageable. I doubt very much that the T&E is.

As I have already said, the cheapest soloution is disconnection of the whole rotten mess.
If you have us all of the information then maybe a more useful opinion could be put forward
 
An office to one and an outbuilding/bedsit in another.

I would class it as unsatisfactory in a report but as the client will not want to disconnect, I would feel the best option is to recommend rcd protection at the points in then picture as a minimum. Obviously ideally I would recommend armoured cable or equivalent, but the cost i feel unless it's compulsory eg selling of a house then, It won't be a consideration to them.

Then issue the report and make your recommendations. Fitting RCDs will not provide the necessary protection for those cables, and you will then have carried out work which does not comply making you liable.
 
To be honest I couldn't give two hoots what you appreciate.

If that black cable is NYYJ/hi tuff or similar then depending on installation method it may be salvageable. I doubt very much that the T&E is.

As I have already said, the cheapest soloution is disconnection of the whole rotten mess.
If you have us all of the information then maybe a more useful opinion could be put forward

How about you get lost, I asked politely not to comment on my posts anymore, that's all my future posts
 
Last edited by a moderator:
Joe and Dave please keep it civil to avoid the thread derailing, if you don't feel you can get on well enough to engage in the same threads may I suggest you use the ignore feature and at least that way the thread can stay open, cheers lads.
 
How about you get lost, I asked politely not to comment on my posts any more, that's all my future posts

A bit unnecessary if you ask me. Dave is a very experienced sparky and if you discount his input as not being valid, you will not learn from him.

Learning from others is what you need and nobody knows everything!
 
Joe and Dave please keep it civil to avoid the thread derailing, if you don't feel you can get on well enough to engage in the same threads may I suggest you use the ignore feature and at least that way the thread can stay open, cheers lads.

Surly as its my thread , if I ask for him not to comment further then that should be respected. I was not rude in. Asking him only when he ignored me just because he likes to be sarcastic ???
 
Maybe get someone who is experienced at carrying out EICRs to come and do a few with you, that way you will start to learn the process involved. You are there to report only, the install is not your problem. You're not there to do the customer any favours in terms of trying to achieve a 'Satisfactory' overall report. If something is wrong, which in this case it is. List it and code it in the EICR and then set out in your estimate for remedial works how you intend to rectify the issue and apportion a price to it. Simples. In this case I would get customer to contact a ground worker to lay some flexible 100mm ducting from A to B at a depth of not less than 700mm, make sure a draw rope is left in the duct, then you can quote for pulling in SWA (CSA determined via your cable calcs), terminating, testing etc etc. If they don't like the price then that's probably why it was bodged in the first place. Take your money for the EICR and walk away from the sorry situation. Don't become 2nd Lieutenant Bodge....
Also it may have been a good idea not to start stating who can and who cannot comment on your post. It is a forum after all, if you wanted specific answers to you query why not ask a couple of local sparks who you work with face to face, that would avoid all the nonsense stirred up on this thread?
 

Reply to Eicr in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
792
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock