Raptor0014

Esteemed
Reaction score
1,261
Having a discussion the other day with a kitchen fitter who “also does electrics” and he is adamant that a NIC contractor told him that a meter isolation switch has to have the supply go in the bottom and the load out the top, same as a MCB. This convo came about as he said the property we were both at was wired wrong as the supply went in the top of the EMIS.

I tried to explain that unless the manufacturer instructions stipulate it only goes one way (like a KMF) then it won’t really matter, if there is any ambiguity it should be labelled which way it is wired and any sane electrician would test it was dead before working on it. Plus it would usually have the larger of the two covers over the supply side.

However he was adamant I was wrong. 🙄 So I opened up the CU I was working on and asked him to look at the 100A switch and pointed out the supply for that goes in the top and the same 100A type switch is usually found in the EMIS.

I‘ve installed various make EMIS and don‘t ever recall one stipulating which way the supply side must be. But he is adamant that they can only go one way.

Am I being thick?
 
If that were the case, you would only be able to assemble the case in one way to facilitate that. The Line/Neutral orientation is important because it could be opening/closing the line before/after the neutral.

If it was a switch fuse it's obviously different because you don't want the fuse terminals to be live with the switch in the off position, but for a standard (is it 60947-3 compliant) isolator, unless stated on the device itself, it shouldn't matter which side is the load and which is the supply.

Ask him to explain why it matters. And ask him what qualifies him to be providing such 'guidance' :D
 
If that were the case, you would only be able to assemble the case in one way to facilitate that. The Line/Neutral orientation is important because it could be opening/closing the line before/after the neutral.

If it was a switch fuse it's obviously different because you don't want the fuse terminals to be live with the switch in the off position, but for a standard (is it 60947-3 compliant) isolator, unless stated on the device itself, it shouldn't matter which side is the load and which is the supply.

Ask him to explain why it matters. And ask him what qualifies him to be providing such 'guidance' :D
I did ask him to explain and I did mention about the line and neutral being right. I explained about KMFs etc for the very reason about the fuse terminals being live.

But he was so insistent that it was wrong and should be bottom in top out that I actually started to doubt myself hence running a sanity check on here. I normally have a couple on the van but didn’t have one to show him.
 
I did ask him to explain and I did mention about the line and neutral being right. I explained about KMFs etc for the very reason about the fuse terminals being live.

But he was so insistent that it was wrong and should be bottom in top out that I actually started to doubt myself hence running a sanity check on here. I normally have a couple on the van but didn’t have one to show him.

Don't buy into his delusion. Unless I'm messed in the head, what he's saying is complete rubbish. As you pointed out... if it required a specific way, it would be labelled as such or there would be a wiring diagram on them and the cases would only go together one way.
 
Don't buy into his delusion. Unless I'm messed in the head, what he's saying is complete rubbish. As you pointed out... if it required a specific way, it would be labelled as such or there would be a wiring diagram on them and the cases would only go together one way.
I am not able to tell from here if you are “messed in the head” 😄

however I would put my vote in for it really makes no difference, an isolator is just that, it isolates one set of terminals from another.

It might be more “normal” for it to be one way round rather than another but either way is just fine, after all it is able to do its job as an isolator.
 
Last edited:
Might be Chinese whispers:

DNO person says 'Our standard configuration is to put the feed in the bottom.'
NIC spark says 'DNO person says they put the feed in the bottom.'
Kitchen/spark says 'NIC spark says the feed has to go in the bottom'

By the time you get to the 20th person, the remark still refers to bottoms but not in the context of wiring isolators.
 
It is possible this comes from something like the wylex REC2 isolators where the enclosure is designed so that the incoming supply goes in the bottom and then the lid goes on and gets sealed, the top outgoing terminals have a smaller seperate lid. This allows the DNO side to remain enclosed when the electrician is connecting to the outgoing side.

However I think you can just swap it around so the enclosure is up the other way to feed in the top.

Also an MCB doesn't have to have the feed in the bottom, it can go tbe other way. Some DBs have the MCB's fed from the top such as single phase schneider/Merlin Gerin boards.
 
Most if not all European double pole MCB's and RCD's are fed from the top, the terminals are staggered to allow bus bars to be used on both line and neutral.
 
with the KMf type switch fused units,s. 1 way isolates the fuse when turned off, the other leaves it live. choice allcomes down to where you can dress the cables in neatly. can't leave something that looks like a ktchen fitter has done it.
 
Hopefully no-one calling themselves an electrician is trying to claim that it won't work the other way, rather that there is some regulation requiring it to be installed a particular way.
 
Hopefully no-one calling themselves an electrician is trying to claim that it won't work the other way, rather that there is some regulation requiring it to be installed a particular way.
Having seen and had to rectify this guys work previously. It’s clear he’s no electrician. At a stretch he’s done a part P course at some point.

I’m far from perfect by any stretch of the imagination. But I do have some idea of what I’m doing. 😂 And if I’m ever in doubt, even in cases like this, I’m not afraid to ask more knowledgeable people and/or consult the BBB.
 
Having a discussion the other day with a kitchen fitter who “also does electrics” and he is adamant that a NIC contractor told him that a meter isolation switch has to have the supply go in the bottom and the load out the top, same as a MCB. This convo came about as he said the property we were both at was wired wrong as the supply went in the top of the EMIS.

I tried to explain that unless the manufacturer instructions stipulate it only goes one way (like a KMF) then it won’t really matter, if there is any ambiguity it should be labelled which way it is wired and any sane electrician would test it was dead before working on it. Plus it would usually have the larger of the two covers over the supply side.

However he was adamant I was wrong. 🙄 So I opened up the CU I was working on and asked him to look at the 100A switch and pointed out the supply for that goes in the top and the same 100A type switch is usually found in the EMIS.

I‘ve installed various make EMIS and don‘t ever recall one stipulating which way the supply side must be. But he is adamant that they can only go one way.

Am I being thick?

Facility to seal the enclosure cover and incoming ‘bottom’ connections, allowing the outgoing ‘top’ connections to be
made at a later stage



https://www.NoLinkingToThis/p/wylex...Tab=qaTT#product_additional_details_container


Load /Supply either way.
 
Last edited:
I've come across some "interesting" "facts" from supposedly competent electricians in teh past. One of my favourites was the one who told me that data had to be in the top section of the dado trunking - because if the power went in the top and data in the middle then they wouldn't be insulated*. Had to re-route some of the cables on that job as the top section wasn't big enough for all the cables.
* No this wasn't about open-back mounting frames, he genuinely believed the PVC divider only insulated one-way.
 
I was once told by an ex navy Electrician that if common and L1 were swapped over in a one way switch it would then operate upside down ?! :)
 
I'm sure it doesn't matter if the supply goes in the top or bottom of the isolator, we've had this debate at work. It's a switch which disconnects and reconnects a conductor. Yet we still put supply in the top and load in the bottom out of habit, as it is in a CU main switch. The tiny diagram on the front of a RE2 isolator shows the top as main and the bottom attached to the switching poles, see pic, still sure electrically it doesn't matter
 

Attachments

  • rec2 isolator label.jpg
    11 KB · Views: 7
It doesn't matter. The electrons don't care which contact they arrive at and find an air gap. But then. 1/100th of a second later, other electrons will arrive at the other contact and find the same air gap.
 
The problem is there are muppets in this world who don't know to test what side of the switch is live, just assume that the covered terminals are the live side, which is not unreasonable, but only make that mistake once.
 
I did ask him to explain and I did mention about the line and neutral being right. I explained about KMFs etc for the very reason about the fuse terminals being live.

But he was so insistent that it was wrong and should be bottom in top out that I actually started to doubt myself hence running a sanity check on here. I normally have a couple on the van but didn’t have one to show him.
When I was in infant school, he would be the one standing in the corner with the hat on.
 
Came across a stand alone RCD once that had been wired N - S on one pole and S - N on the other. Still worked perfectly as an RCD, of course, and the layout of things around it made it obvious why it had been done, but the problem was the test button circuit. These are normally wired to take the neutral from one end and the live feed from the other, so that the power to the test circuit is disconnected as soon as it trips. Unfortunately, in this case, the neutral and the live were both taken from the 'in' side, so the test resistor had been fried by the button being held in too long.
 
Came across a stand alone RCD once that had been wired N - S on one pole and S - N on the other. Still worked perfectly as an RCD, of course ...
It shouldn't have worked - should have tripped under any load as the sense coil would read the sum of the currents rather than the difference.
 
It shouldn't have worked - should have tripped under any load as the sense coil would read the sum of the currents rather than the difference.
You could well be right. It was back in the day when RCDs were still pretty much a novelty and this one had been added in front of an old MEM rewireable fuse board. I only got as far as testing it by the inbuilt button, which it failed and then started emitting smoke (which was when I realised how it had been connected.)
Board and RCD were replaced by DIN rail type CU, with a RCD main switch and MCBs and a couple of extra ways for the new circuits that I was there to install.
 
I really like the Hager VC02SW REC isolators
The cover can be rotated to allow the supply at either side

218556_41.jpg


They are also slimmer than others on the market, as well as having terminals that tighten to 3.6 Nm and cord clamps for the meter tails
All in a decent bit or kit.
 
I really like the Hager VC02SW REC isolators
The cover can be rotated to allow the supply at either side

218556_41.jpg


They are also slimmer than others on the market, as well as having terminals that tighten to 3.6 Nm and cord clamps for the meter tails
All in a decent bit or kit.
Is it much slimmer than wylex RECSW2S?

I like the twin screws provided by wylex and wonder if Hager provide the same?


Edit: Can't find info on terminals, but note that it's 15mm narrower than the slim wylex enclosure. Seems a touch expensive, but smaller profile would be invaluable in many homes where incoming supply is afforded a ridiculously small
amount of space.
 
Last edited:
Is it much slimmer than wylex RECSW2S?

I like the twin screws provided by wylex and wonder if Hager provide the same?


Edit: Can't find info on terminals, but note that it's 15mm narrower than the slim wylex enclosure. Seems a touch expensive, but smaller profile would be invaluable in many homes where incoming supply is afforded a ridiculously small
amount of space.
REC2S 150mm 63mm 79mm (H W D)
VC02SW 145mm 50mm 78.5mm
 

Reply to Electric Meter Switch Isolator wiring orientation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
441
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock