Hi all
Im a Sole trader electrician and i have about 7 years of experience. I would consider myself competent at testing and I regularly test my own jobs but ive only really subbed to firms that have Part P and are members of NICEIC or the other electrical bodies, i dont personally hold Part P qual and Im not a member myself of NICEIC. I do not do enough of my own jobs to warrant joining NICEIC or getting the part P qual.
My problem comes as my friend has asked me to test his house (as part of him selling it) which I can physically do but Im confused if I can self certify the house and produce a condition report for the letting agency and inform building control as a one off. Or do I need turn down the work and get another electrician to come test?
Any information to clear this up for me would be great
Many thanks
 
you can do an EICR for your mate. complete the certificate. part pee and LABC are irrelevant here as they only apply to installation works. you will not be certifying installation work, but completing a condition report. any faults that require remedial work come under the umbrella of maintenance and, as such, part pee and notification to LABC do not apply. however, any remedial work that you may do must comply with BS7671.
 
I guess the issue is do you believe you are competent in carrying out EICRs? There is a difference between inspecting & testing work you have done and an EICR (I'm assuming it's an EICR that's required!).
If you believe you have better than average knowledge of BS7671, go for it.
 

Reply to Electrical Condition Report and Part P in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am going to fully rewire my house. What do I HAVE to do once I’ve rewired it? I am an approved spark, but do not have part P. Do I need...
Replies
11
Views
2K
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
921
Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
631
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
793
Hi all, New to the forum! Quick background on me: I have a degree in electrical engineering and spent many years working with qualified...
Replies
76
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock