Electromagnetic effects upon cables both single and three phase cables upon entering a metal distribution board. this was picked up on a periodic test and inspection on a small block of flats. This has caught me out and i cant think of what causes this or the implications, any ideas ????
 
Keep all the lines together with the neutrals going through the same metallic enclosure.
ie.. Don't take lines through one metal coupler neutrals through another and earths through another.
 
How to identify the problem and what to look for, that should enable me to sort it. and then for future ref refresh my memory on eddy currents. cheers
 
As the others have said, you need all your supply cables going through the same aperture, and if that is not possible then a workaround is to cut a slot between all the holes and make sure you use brass glands, nut's and banjo's if fitted.

Another possibility is to use a suitable plastic gland plate, the brass fittings above also apply here.
 
If the gland plate that the singles pass through is steel (IE magnetic) you will get eddy currents. The eddy current will equal the current in the conductor.

There’s two ways around this:
Make the gland plate out of aluminium.
Cut a slot between the gland holes to break the circuit.

A word of warning, don’t use steel lock nuts for the glands.

This plate was for a 1MVA transformer. I usually fill the slots with epoxy resin to keep creepy crawlies out.

View attachment 13602
 
There’s two ways around this:
Make the gland plate out of aluminium.
Cut a slot between the gland holes to break the circuit.

Even aluminum.plates can allow circulating currents over a certain level/magnitude. I always use brass sealing glands in 10mm Paxoline (for want of a better name) board for multi entry single cables into Switchboards/TX's and the like. The slotting of standard steel gland plates is as good a method as any, for stopping circulating currents forming, but the finished installation can look a real pigs ear, if care isn't taken on sealing the slotted sections...
 

Reply to electromagnetic effects in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
3K
So Allianz insurance inspector has pulled up a C3 ( I know it’s not mandatory) about magnetic effects from a circuit. so we have a small 9-way...
Replies
7
Views
1K
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock