Discuss Emergency Lighting Central battery system design in the UK Electrical Forum area at ElectriciansForums.net

S

stescott1

Hi All,
I am new to this site so be gentle please....

My question is this... I have been to an existing job which has 55 slave EMLs throughout the building. We are experiencing volt drop on the longer routes with the LED fitting, approx 40 lights. The LED fittings start to strobe as they hit below about 22vdc. The batteries in the unit are 2x 100Ah batteries and the load of the existing lights is approx 14.5A.
I was wondering how I can ramp the voltage up to 30vdc when on load. I was thinking say 6vdc batteries but not sure how to work out the Ah rating etc.
My question is, is it ok to mix the sizes of the batteries inside the unit i.e. 2x 100Ah and 1x 15Ah or do I have to replace them all for alike?

If there is anyone with this type of knowledge or experience please point me in the right direction is possible.

Many thanks
Stescott1
 
I would start by contacting the manufacturer to ensure you're within the limit for the number of luminaires for the charger/batteries.

If that is ok, you then need to calculate the required cable sizes which should then be compared to those that have been installed.
 
I don't think that adding an additional battery in series with the others is the answer, particularly one of a lower capacity. The lower capacity battery will be dead when the others are only partly discharged. You might also exceed the maximum permissible voltage for the lighs.

What's the voltage at the batteries when the lights are getting 22V?
 
As previous, you need to do some testing.....check voltage of batteries off load, Should be 27.6 volts. Then check batteries on load, should be aprox the same. If 22v then batteries require load testing. Batteries will only last between 5-7 years with constant charging. And voltage decrease will occur when battery capacity is low, on load.
 
Thanks for the answers.
The batteries are new and are about 27v on and off load. I have a circuit which is not too long and lights work fine. It seems to be that they flicker around or below 22v. I have load tested the batteries and they pass. I have contacted the manufacturer of the fittings and he has done a batt calculation, the result was the existing batteries are over sufficient for the 3 hour duration. The fittings also should work up to 30vdc, I have been told.

My only other idea was to have 5 6vdc batteries all at 15Ah capacity which will work but I'm not sure for how long. Any ideas??

Thanks again for the posts.

Steve
 
If you are getting 27v off load and 27v on load....then you have a big problem if your stating 22v at the light fittings, thats a 5v loss in cable run
 
I know its a big drop...
I am not sure of the cable run lengths of 4 of the circuits.
I may have to run new cables for the additional fittings we installed! maybe this might help if I run them in 2.5mm FP.
Cant think of any other ways around it....
 
I would start breaking up the circuits, and continue testing. You need to prove the cables and their terminations in each fitting. Incase there is a manufacturing fault with the fittings....so one step at a time, if you can link the fittings out, even better. You can conduct a full insulation and r1 + r2 test.
 
Normally when doing central battery system emergencies 2.5mm2 FP200 is used throughout due to volt drop issues. (The luminaires are likely 24Vd.c.) 1.5mm2 may be used to tee off for a fitting, but certainly I wouldn't be wiring multiple fittings in 1.5mm2.
 
Out of curiosity, were the original fittings 8w fluorescent's? I've known the old type too work happily on long runs with voltages down to less than 20v. It maybe the LED type are much more voltage critical?
 
Never seen a central emergency battery system with just two batteries...
The central battery systems we have, require substantial storage racking in an Ex Zone room to house the batteries!!
 
The type you have E54 is to supply essential db boards at inverted 230v. Boards will possible supply em lighting, fire alarm, va, firemans lift etc. Usually large inverter cabinets, with stacked batteries, dotted around the building, or lined up in on large vented room.
These 2 battery em packs, are basic power supplies solo for 24v em lighting, good enough for aprox 100 x 8w bulkhead for 3 hours
 
This is something I haven't checked. Although The existing fittings are 8w fluorescents which is why we haven't seen any problems until fitting LED.
Thanks Ill try this tho.
 
This is something I haven't checked. Although The existing fittings are 8w fluorescents which is why we haven't seen any problems until fitting LED.
Thanks Ill try this tho.

You are using 24v led bulkheads ...? if yes, then check all cable runs, as I suggested, then we can look at compatibility of led
 
Do the LEDs work if you connect them directly to the batteries eliminating any volt drop on the cabling?

Yes they do there doesn't seem to be a problem with the fittings themselves. I think like Bossian said the LEDs may be more sensitive to voltage drop. Some of the 8w existing fittings are further down the line than the LEDs and seem to work fine.

Im starting to think Ive F'd this job up putting the LEDs in instead of 8w bulkheads.
 
You are using 24v led bulkheads ...? if yes, then check all cable runs, as I suggested, then we can look at compatibility of led
Yes they are 24v LEDs. I will try splitting them up and then if that works I can wire the LEDs on a dedicated line.

Wish me luck....
 

Reply to Emergency Lighting Central battery system design in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey, with regards to DALI Emergency Lighting Automated testing via a control system, does anyone know how best to overcome a fitting that is...
Replies
1
Views
886
Have dealt with central battery systems in the past, fire rated cable that either loops in and out of the luminaire using ceramic terminal blocks...
Replies
0
Views
799
I am looking for a product to convert an existing lighting circuit in a communal stairwell to be emergency battery backed up. There are 6x 7W LED...
Replies
9
Views
2K
Hi Guys & Girls, It's been a while, hope everything is good. I have an issue that's proving to be a bit of a head scratcher. Please bear with...
Replies
11
Views
2K
Good afternoon - apologies if I'm overthinking this, but I was hoping I could put this out there for consideration. Scenario is as thus. Picture...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock