Search for tools and product advice,

Discuss EV Charger Earth Rod in the UK Electrical Forum area at ElectriciansForums.net

If the Consequences caused by overvoltage for a single dwelling unit where an assessment shows the total value of electrical installation and connected equipment is found to necessitate the cost of SPD protection then you install one, you don’t fob it off as the assessment will have been done with the client.
If it’s found it’s not required then yes don’t install one.
 
View attachment 56887

Then you recommend one......ta da

It does not say that.
It says that where a risk assessment is not performed an SPD must be installed. With one exception, a single dwelling where the cost of installation outweighs the benefit.

So:
1: If a risk assessment is carried out then you follow whatever the conclusion of the risk assessment is. This does not constitute a recommendation, this is a clear yes or no decision based on calculated risk.
2:if a risk assessment is not carried out you fit an SPD (no mention of recommendation)

The exception to 2 is that IF it is a single

dwelling AND the total value of the equipment that would be protected does not justify the cost of installation then SPD protection may be omitted.
Again a clear yes/no decision based on calculation. This is not a recommendation.

Nothing in the regulations mentions recommendations for SPDs, the requirements are clear-cut yes/no decisions.
[automerge]1585819738[/automerge]
Not if the client says that they don't want one.....it's only a recommendation

If the client says they don't want one, then don't do the job and walk away.
As far as the regulations are concerned you do the job to the regulations or not at all, theres no picking and choosing which bits you want to comply with.
 
i dont agree with that? Your suppost to eliminate the car shell becoming live should a open PEN conductor occur not wait for someone to have a shock and hope the rcd trips which it wouldnt with the loss of neutral conductor!

Why do we have RCD at all then?

RCD are fitted so there is no single point of failure that leads to a dangerous situation. They are not a substitute for proper insulation of conductors or earth bonding of metalwork, but are there to deal with cases when something unlikely but possible results in a dangerous situation (e.g. open PEN conductor, garden tool cuts extension lead, etc).

True if you lost the majority of L-N voltage it would not be able to trip but I suspect you would see a fair portion of 230V remaining due to the other phases' loads. If designing something like this from scratch you would probably have something like the Matt:e box contactor that would zero-volt release under such circumstances, and possibly only close fafter doing a self-test cycle.
 
Had a call out yesterday to a Car Charger not working Power supply on to unit.
When car plugged in went to fault straight away.
On investigation found the earth rod on the house supply had a sheared nut in the earth pit leaving a very high earth loop.

If the car Charger had not picked up this issue the people in the house would of never known the nut was sheared.

Just my Thoughts
 

Attachments

  • IMG_3781.JPG
    261.9 KB · Views: 20
If the Consequences caused by overvoltage for a single dwelling unit where an assessment shows the total value of electrical installation and connected equipment is found to necessitate the cost of SPD protection then you install one, you don’t fob it off as the assessment will have been done with the client.
If it’s found it’s not required then yes don’t install one.

Given that separate Type 2 SP+N SPD can be bought for under £100 and you can get whole CU with them already included for around £100-£150, why both with the risk assessment at all?

I suspect doing it properly and documenting it for the client is going to cost more than £100 of your time!
 
Given that separate Type 2 SP+N SPD can be bought for under £100 and you can get whole CU with them already included for around £100-£150, why both with the risk assessment at all?

I suspect doing it properly and documenting it for the client is going to cost more than £100 of your time!
I install them as standard in domestic
 
No spd required.......it's only a recommendation to have one and I believe you have to do a course to get a qualification to fit car chargers

i believe you only have to have the qualification and manufacturer ev charger approved if you want to be olev registered. If not a EIC will suffice.
[automerge]1585859854[/automerge]
Why do we have RCD at all then?

RCD are fitted so there is no single point of failure that leads to a dangerous situation. They are not a substitute for proper insulation of conductors or earth bonding of metalwork, but are there to deal with cases when something unlikely but possible results in a dangerous situation (e.g. open PEN conductor, garden tool cuts extension lead, etc).

True if you lost the majority of L-N voltage it would not be able to trip but I suspect you would see a fair portion of 230V remaining due to the other phases' loads. If designing something like this from scratch you would probably have something like the Matt:e box contactor that would zero-volt release under such circumstances, and possibly only close fafter doing a self-test cycle.

no this is does not mean fitting an rcd will cover the open PEN fault. You contradicting yourself in your post, yes a contactor will satisfy this requirement hencr the 1st amendment.
have you fitted an ev charger on a pme relying on this two rcds in series theory??
 
Earth rod bolt shearing is very common when they are overtightened. I've done it myself a few times when I was learning but soon learned that brass bolts don't need anywhere near the same torque as steel
 
I try not to use the bolt, but pack the clamp with brass wedges and just nip up the bolt at the end, using 25mm bare copper conductor there is not a lot of space to pack.
 

Reply to EV Charger Earth Rod in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
4K
  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
171
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
Guidance please - C&G L3 electrical installation - Hotel extension project Hi folks, I am fairly new to this forum but it looks like the...
Replies
6
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock