Discuss EV charger issue - Garo PME trips in the UK Electrical Forum area at ElectriciansForums.net

Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used inaccurately.


I had an EV charger installed in December on my detached garage by a local electrician. The charger is one that doesn't have a PEN fault detection device (Tesla), hence we agreed I'd get it separately (Search Results - Detail - https://www.garo.co.uk/product-details/All/G6EV40PME).


Armoured 10mm^2 cable (from main circuit board to garage - approximately 32 meters) has been used to the garage where a smaller consumer board and the PME fault device was fitted. From there there's around 4-5m of 4mm cable to the actual charger.


After awhile I've noticed that the PME fault device trips every now and again - always late in the evening or at night, although that's mostly when I charge. It is quite sporadic, although in reality probably happens every 5-6 charges, which can be annoying in the morning if I miss the message on the car's phone app.


Interestingly the Tesla charger integrates with my Home assistant, so I can see the voltage at the charger, which seems to significantly drop on some evenings/nights (expected under load?), although never below the PME device's 207-253V range.


I have raised this with the electrician several times and he's not sure why this is happening. Also everything seemed fine on the 2 occasions he's tested it - once after installing and later when I raised the problem with him. However the test was never done by him at the time when voltage significantly dropped.

I did measure the voltage myself once when the voltage seemed low, soon after the PME device tripped and I reset it. In the house - ~232V, in the garage's consumer unit - ~230V, meanwhile Tesla charger in Home Assistant reported approx 222V while charging.



Question - where would I go from here ? Is there anything obvious another electrician would perhaps notice.. ?

Some photos attached.

Thank you
Apologies for the late response.. I am exceptionally busy these days with solar pv installs galore. not so much EV charging but approaching teh wider renewable sector with same determiantion to consumer the mundane through to interesting knowledge. Dont fit anything I do not fully understand. Not been on the forum as much the last few months. not had time. Business has tripled in size.
I am not a fan of Garo RCBOS, went through a spell using them but found them too prone to nusinace tripping - oddly enough normally a tesla involved.. i had one install with a similar issue albeit in the end we got the dno out who fitted a bit of kit to measure the supply voltage and we could show that as he was fed from an overhead line - with pole 2 metres from his garden fence that as he was end of the line his voltage would drop to just over 200V in some cases. long story short they replaced transformer on the pole and now everything is fine.
I have been told by some planners for the dno that as so many people are now on octopus go and similar tariffs for evs that kick in at 00:30 every night they can actually see the effect on ev chargers kicking in at this time on the local parts of grid and the voltage level drops. It is in some areas causing some headaches in balancing the grid supply.

Had another customer with similar issue of car stopping charging due to detection of low voltage (sub 220V), flashed up on esla central dash. this could happen day or night and occur majoirty of time. it was only when he took it to the Tesla rangers over by Avonmouth and showed them on a 7kw charger that they then relented from saying it is your supply. they replaced the charging port and a wiring loom even thought there was supposedly nothing wrong with it. so read into that what you will
 
ElectricallyRandom: Questions, questions, questions!

1. Is you leccy supply from overhead cables?

2. Where are you along the line of poles between the transformer and your tap off?

3. In the voltage plot was it your EV starting to charge that caused the very significant voltage drops at 8pm and 10pm? I have assumed it was which is why I am checking. Or something else?
 
ElectricallyRandom - good morning Sir.

Just wondering if you have resolved the problem and how? We like to learn from what advice was useful or otherwise.
 
ElectricallyRandom - good morning Sir.

Just wondering if you have resolved the problem and how? We like to learn from what advice was useful or otherwise.
Been really busy, so no, I didn't yet. In the mean time it has happened at least twice again. Garo tripped in the evening, I've reset it and the charging completed by early morning. I'm very tempted to just swap the garo for a matt:e as per several similar stories online.
 
Did you lower maximum charge current?
Only just. Need to charge today - dropped the current from 32A to 26A. Will see how it goes.

To answer your questions a few posts above:

1. No overhead cables around here - all underground.
2. Not sure I understood the question, but I have no idea whereabouts the main transformer is in this neighbourhood (new development, dozens of new houses). It's definitely not in the vicinity if it makes a difference.
3. Yes, voltage drops quite noticeably when I start charging.
 

Reply to EV charger issue - Garo PME trips in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
834
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
1K
Hi all, I've installed a Tesla Gen 3 wall charger supplied by my client. For your information, the place that I installed is in a block of flat...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock