Discuss EV chargers and TN-C-S supply earthing general hassle in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor gets broken in a TN-C-S or thesedays most TN-S supplies.

1) If the PEN gets disconnected in the street, N and CPC become live making the car >70v. Won't everything in the house be just as dangerous? Radiators, dishwashers etc, Why are they so ----y about EV chargers especially?

2) Why is TN-C-S becoming most common if it's dangerous? There were 500 incidents a year reported

3) Electric cars are almost all plastic on the outside, can the mfrs just make them as class II appliances with no external earthing? Like arden equipment
 
Here's an interesting video from John Ward if you've not already seen it.
That's where I started, great explanation of how and why, but I'm still missing the part where EV chargers need specialist courses and earth rods but a lawnmower socket circuit just needs an rcd and earth.

If the PEN fault is just as rare and dangerous for everything else, the seem to be picking on EV's. Maybe it's DC related?
 
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor gets broken in a TN-C-S or thesedays most TN-S supplies.

1) If the PEN gets disconnected in the street, N and CPC become live making the car >70v. Won't everything in the house be just as dangerous? Radiators, dishwashers etc, Why are they so ----y about EV chargers especially?

2) Why is TN-C-S becoming most common if it's dangerous? There were 500 incidents a year reported

3) Electric cars are almost all plastic on the outside, can the mfrs just make them as class II appliances with no external earthing? Like arden equipment

When you touch the car you are stood on the ground which makes it more hazardous.

There are many electric cars which have metal bodies.
 
1) If the PEN gets disconnected in the street, N and CPC become live making the car >70v. Won't everything in the house be just as dangerous? Radiators, dishwashers etc, Why are they so ----y about EV chargers especially?
Yes, but inside a house you are in an equipotential environment and anything metalic bringing in true earth from outside is bonded so will rise in potential along with the radiator and dishwasher etc, There is a risk for things like outside lights (although not often touched) but definitely outside taps which also add water to the situation in my opinion are as much if not more of a risk than EVs

2) Why is TN-C-S becoming most common if it's dangerous? There were 500 incidents a year reported
Because its cheaper, when you need to run that much cable one less conductor probably gives a sizeable cost saving, Some would also argue for the very low Ze (high fault current) but this could also be achieved with true TN-S if all conductors are equally sized

3) Electric cars are almost all plastic on the outside, can the mfrs just make them as class II appliances with no external earthing? Like arden equipment
Really? A few friends of mine have electric cars and they seem to have metal body panels.
I wonder if the metal body of the car could be connected to the DC battery ground (like a standard car) and the charging circuit inside the car is housed in a double insulated enclosure and had suitable isolation transformers from the AC to DC side therefore removing any risk if the CPC has a high voltage on it, perhaps there is a reason not!?
But this would make the car class 2 as you say but allow manufacturers to use any construction materials
 
That's where I started, great explanation of how and why, but I'm still missing the part where EV chargers need specialist courses and earth rods but a lawnmower socket circuit just needs an rcd and earth.

If the PEN fault is just as rare and dangerous for everything else, the seem to be picking on EV's. Maybe it's DC related?
If you are aware of the potential dangers, after additional training if necessary, then thats fine to go ahead and install it for people. Some people just seem to plough ahead regardless.

It might be just rare and dangerous, but it will only take just one instance, which might prove fatal. After all, its a large metal box connected to electricity, but isolated on 4 rubber tyres, just waiting for someone to come along and touch it.

Most electric lawnmowers I know of, are Class 2.
 
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor gets broken in a TN-C-S or thesedays most TN-S supplies.

You raise a reasonable point.Electric gates ,heat pumps etc ( plus all outside metalwork) all carry the same risk under open PEN circumstances.Perhaps it is the fact that people clean their cars far more often than they clean their gates or heat pumps is what finally caused the regulators to decide that " we need to take steps to mitigate danger " should a broken neutral occur in a TNCS system.
 

Reply to EV chargers and TN-C-S supply earthing general hassle in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
819
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
As the title says, does a three-pin socket (external) used as charging point need an earth electrode or open PEN fault? Are mode 1 and mode 2...
Replies
17
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock