Testing during a board change, a RFC on a 32A 60898, with rcd protection, you find that the max Zs is exceeded by 0.1 ohms using the no trip setting on your mf tester
On the EIC do you -
A) simply record the actual measured value
B) record the actual measured value and note the position under comments on the installation
C) retest, bypassing the rcd, on the Hi setting of the tester and record the revised value
D) change the ocpd to a lower value to achieve compliance with max Zs
E) do something different?
There's a round of drinks riding on this, so think carefully!