- Reaction score
- 25,489
You are doing well to have that Ze and exceed the max Zs for a type B, 32A breaker in a domestic property.
Discuss Exceeding max adjusted Zs on a board change. in the UK Electrical Forum area at ElectriciansForums.net
Depends if the spur, if it exists is fused at a FCU.I'm missing something, am I wrong with my view on the Zs ?
Testing during a board change, a RFC on a 32A 60898, with rcd protection, you find that the max Zs is exceeded by 0.1 ohms using the no trip setting on your mf tester
QUOTE]
QUOTE]
What was the result for Zs as recorded by the MFT, as a matter of interest, or have I missed that?