Search the forum,

Discuss External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net

I think this is one of the best, difference of opinion debates Ive seen for ages!!! Its what this forum has been lacking lately.
I dont have much to do with TT systems (since college) and there arent that many around here, or Ive just been lucky enough not come accross one but Im enjoying reading all the points raised by E54, wirepuller and D Skelton and its giving me a greater understanding of TT systems.

Jay

I second that. It's all good stuff from these knowledgeable gentlemen. :)
 
I'm with E54 on this. As he says, getting a low value in the first instance, will only lead to lower Ra values later on.
i understand Wirepullers points too, but I would prefer to have a system in which even if the RCD failed, there was a chance of another device operating, rather than not even worry about it.
I installed a rod (single rod, not needed, but was told to install anyway) on a job a year ago, it was 50 ohms.
i tested it the other week, whilst on the same site for another job and it was 2 ohms.
This is on top of a hill too.
I reckon another rod would see one ohm ish.

its nice to see a decent debate with decent technical discussion.
 
It was very dry when I installed the rod. Like E54 has mentioned, the ground around the rod consolidates, lowering the contact resistance.
the idea of installing multiple rods (on top of each other) is to get below the level where seasonal changes will have too much of an effect.
 
Engineer54;719568[B said:
]Using your argument, One could easily ask WHY would you be giving a dam about Zs values on a TN system, if your both so confident that an RCD will ''Always'' fulfill your Zs requirement to trip the OCPD?? That argument (which i also disagree with) is just as valid as you blindly accepting a 200 ohm Ra on a TT system because a Reg vaguely say so ...
[/B]
As i've stated many times here, if i had installed a rod position that gave me a 10 ohms value, another rod would ''always/automatically'' be added, you have would to be a bloody fool not too!! And yes, it is more than possible in many instances to achieve near TN values, but that takes a bit of time and effort and knowing what your doing. But again, that's something else that has been lost in time and space!! lol!!

Yes you can get over situations with the use of RCD devices, but at the end of the day, it is just a substitute, it's not really a valid TT system, even more so if you haven't even tried!!! I've been involved with far, far too many TT systems of every type and description, in various countries and locations, that you'll ever convince me in the slightest, that a rod with a 200 ohm Ra sitting on it, is any sort of a TT system. What it is, is a bloody joke!!

Encouraging these younger sparks and untrained so-called DI's, to not even bother installing a decent TT system and just bung an RCD in, isn't the message we should be portraying either!!

Firstly not all TN circuits will have RCD protection,and secondly there are maximum Ze values for TN systems,therefore if a Zs reading was considerably higher than the maximum for a standard OCPD something is clearly not right.That said I would have no problem relying on an RCD to meet disconnection times wher a type B needed to be changed for a type C/D and Zs slightly exceeded the max permitted value.

As I've already stated...if you achieve a TN value of Ra I'm with you all the way......but thinking 10...20...30 ohms is any better than 100-200 ohms ,I'm not.
 
I'm with E54 on this. As he says, getting a low value in the first instance, will only lead to lower Ra values later on.
i understand Wirepullers points too, but I would prefer to have a system in which even if the RCD failed, there was a chance of another device operating, rather than not even worry about it.
I installed a rod (single rod, not needed, but was told to install anyway) on a job a year ago, it was 50 ohms.
i tested it the other week, whilst on the same site for another job and it was 2 ohms.
This is on top of a hill too.
I reckon another rod would see one ohm ish.

its nice to see a decent debate with decent technical discussion.

Just to make it clear....If you get a TN value it was worth the effort....my issue is ONLY with those who scoff at the Bs 7671 value of 200 ohms,and seem to think (for example) 20 ohms is the dogs danglies. It isnt. Do the calculations and you will find 20 ohms does the same job as 200....or 500 for that matter.
 
The most important factor is a stability, some soil/ground types won't allow a low Ra, that's just how it is. The tx arrangement plays a role too, you could have 21 ohms at the tx.

The key is a stable system for the soil type, if you have a favorable soil type and a combined HV/LV tx then yes a good low loop impedance is possible.
 
It was very dry when I installed the rod. Like E54 has mentioned, the ground around the rod consolidates, lowering the contact resistance.
the idea of installing multiple rods (on top of each other) is to get below the level where seasonal changes will have too much of an effect.

I don't agree with the statement that the ground consolidates especially when (very rarely) we have a long dry spell and the ground starts to crack and gaps appear. I realise the rod is 1200 mm long and the ground won;t dry out for the full depth but it could go down about 300mm thus reducing the contact with the rod.
 
I don't agree with the statement that the ground consolidates especially when (very rarely) we have a long dry spell and the ground starts to crack and gaps appear. I realise the rod is 1200 mm long and the ground won;t dry out for the full depth but it could go down about 300mm thus reducing the contact with the rod.

This is fundamentally the problem, where most of you sparks go wrong right from the word go. You will never achieve any form of stability with a single 1.2m rod of any size, and that's a fact!! I have no idea why in fact earth rods were ever reduced from what they used to be, (8 and 10 foot X 5/8'' /3/4'') to these tiny 1.2m lengths you have now. You Need a good 8' of rod in the ground whenever possible, or there isn't going to be any stability in the system!! Fortunately depth also reduces a rod positions Ra value too, so it's the way to go!! So don't use a single 1.2m rod for a TT system, always use at least 2 X 5/8'' rods coupled together with a coupler as an absolute minimum....

So you don't believe that the ground/soil consolidates around an earth rod over time?? Perhaps you don't believe in ground settlement either?? It's a fact i'm afraid!!
 
This is where we disagree. I think they're perfectly suitable and defines the needs of a TT system quite clearly. The only bit I'm not quite sure on is the 200 ohms? Seems like a randomly generated value and in my opinion should be replaced with a calculation.

Really?? We must be looking at completely different versions then ...lol!!



And this type of remark helps no one. If I didn't like you and respect your knowledge I would be calling you an arrogant twit right about now :D


Really?? We must be looking at completely different versions then ...lol!!

Nothing arrogant in that statement at all, the whole section on TT systems is helpful to no-one, and why we get so many queries about TT systems on the Forum!! But i'll agree with you on the 200 ohms, it can only be a random figure pulled out of the air for what good it will ever do!! By the way, i may be many things, but what i'm NOT, is anybodies fool. I've been involved in the constructing of TT systems most of my working life, so i don't need a Reg book to tell me anything about what's needed and why. Now if that's being arrogant, then so be it!! lol!!
 
This is fundamentally the problem, where most of you sparks go wrong right from the word go. You will never achieve any form of stability with a single 1.2m rod of any size, and that's a fact!! I have no idea why in fact earth rods were ever reduced from what they used to be, (8 and 10 foot X 5/8'' /3/4'') to these tiny 1.2m lengths you have now. You Need a good 8' of rod in the ground whenever possible, or there isn't going to be any stability in the system!! Fortunately depth also reduces a rod positions Ra value too, so it's the way to go!! So don't use a single 1.2m rod for a TT system, always use at least 2 X 5/8'' rods coupled together with a coupler as an absolute minimum....

So you don't believe that the ground/soil consolidates around an earth rod over time?? Perhaps you don't believe in ground settlement either?? It's a fact i'm afraid!!

I 've installed a few of these in my early days didn't put many 8ft ones in though about 3 I think.
they used to be terrible if you hit a bit of stubborn ground. the steel cap that was screwed on to help not deform the top of the rod didn't always work,
We were putting these in when voltage operated trips were the norm. That was because there was a higher current in the main earth when a fault occurred. Not long after they were outlawed(Voltage trips) it was decided the rods did'nt need to be that big because of the smaller current needed and the speed of the R.C.D.
As for the ground consolidating I've been on some rewires where I 've pulled the old rod out of the ground with little or no resistance. So I stand by what I say.
One thought though is why the pulled out easy in the first place. Could this have been the installers fault?
 
I installed a rod a few weeks ago at a sewage plant serving a pub...(following on from an EICR). The reading from the existing spike was 700 odd ohms,no idea what the rod was as it was completely buried. Replaced it with a coupled rod beloved of E54 and got something like 15 ohms....happy days. But let me state now I'd have been just as happy with 115.
Why everyone keeps banging on about the importance of stability is another thing that defeats me.....yes,if you are going to rely on a low enough Ra to operate an OCPD the stability is vital....if your Ra means one or more RCD's are needed for earth fault protection why does stability matter?....it can be 10 ohms or 500....the RCD will still trip the same.
I think this is where the 'plucked out of the air' 200 ohms figure has been arrived at.....Ra values below that are not likely to exceed the 500/1667 value required for safe operation of RCD's even if ground conditions change.
 
Nothing arrogant in that statement at all

What's arrogant is this notion that just because you've got loads of experience dealing with TT systems you are right and everybody else is inexperienced, misguided and wrong lol (I don't mind so much coz I know you know I'm not a complete ignoramus). I however see things differently, I see your knowledge as good and I don't see your opinion as being wrong. I also think you'll find that when it comes to TT systems we actually agree on more than we disagree on, in the same way that some scientists are convinced by quantum theory and some are convinced by string theory. Both groups have an excellent fundamental understanding of the universe but both choose to describe it's minute operation in slightly different ways. Neither is right, and neither is wrong, and by the same token, I believe that people who understand TT systems the way you do add just as much valuable knowledge to the pool as people who understand TT systems like myself and wirepuller.

I love a good debate but the minute anyone starts to try and devalue an opponents viewpoint instead of continuing to bolster their own, in my eyes their opinion starts to lose credibility. Now I'm not saying this is the case here, I've known for a long time how strongly you feel on some matters regarding the installation of TT systems. My point is, you can't accuse someone of being outright wrong when you can clearly see that they too have a fundamental understanding of what a TT system is and how it operates but just chooses to disagree on one or two points :)
 
I installed a rod a few weeks ago at a sewage plant serving a pub...(following on from an EICR). The reading from the existing spike was 700 odd ohms,no idea what the rod was as it was completely buried. Replaced it with a coupled rod beloved of E54 and got something like 15 ohms....happy days. But let me state now I'd have been just as happy with 115.
Why everyone keeps banging on about the importance of stability is another thing that defeats me.....yes,if you are going to rely on a low enough Ra to operate an OCPD the stability is vital....if your Ra means one or more RCD's are needed for earth fault protection why does stability matter?....it can be 10 ohms or 500....the RCD will still trip the same.
I think this is where the 'plucked out of the air' 200 ohms figure has been arrived at.....Ra values below that are not likely to exceed the 500/1667 value required for safe operation of RCD's even if ground conditions change.​




You see that's where we completely differ, your all too willing to put your faith in RCD's instead of making the effort to have a TT system work as it should!! You may well install an S type up-front, to cover any down stream RCD's, but lets be honest now, ...how many UK electricians, let alone so-called DI's would even think about installing one?? Most of them are convinced that RCD's are as reliable as MCB's so why would they bother!! Again, having so easily obtained a 15 ohm reading, means that your ground conditions are pretty good, (and that the existing rod is probably a twig that hasn't been installed properly) so i'd of put a little more effort into the system. Who knows, that TN value could well have easily been realised!! lol!!

To be totally honest, i don't really know why you bother installing a TT system if that's your honest view. If your not bothered about Ra values and the importance of stability, why not just add your RCD's and let any bonding to the installation be your reference earthing. Using your argument the 700 ohm Ra from the existing rod is as good as any, it's under your magic 1667 ohms ...lol!! All in all, it's a sad day, when other international earthing standards can teach the UK a thing or two, especially when in many cases, their standards are actually based or taken on/from past British standards!!

On all the projects i've ever been involved on, i can't think of a single one where the specifications didn't call for any earthing system to be higher than 1 ohm. That value covered TX installations, as well as other made earthing systems... and your trying to defend your Reg's and it's 200 ohms!!!! ....Quite amazing!!

As the old saying goes, ...you can lead a horse to water but..... lol!!
 
I 've installed a few of these in my early days didn't put many 8ft ones in though about 3 I think.
they used to be terrible if you hit a bit of stubborn ground. the steel cap that was screwed on to help not deform the top of the rod didn't always work,
We were putting these in when voltage operated trips were the norm. That was because there was a higher current in the main earth when a fault occurred. Not long after they were outlawed(Voltage trips) it was decided the rods did'nt need to be that big because of the smaller current needed and the speed of the R.C.D.
As for the ground consolidating I've been on some rewires where I 've pulled the old rod out of the ground with little or no resistance. So I stand by what I say.
One thought though is why the pulled out easy in the first place. Could this have been the installers fault?​





A few of what?? I can't imagine those thin twigs were about in the day's of VOELB's. I've personally still never seen one, ...until recently i'd never seen a 1.2m 5/8'' rod either!! lol!! That was in a wholesalers in Cyprus, who told me they are only used as an extension to their standard 2.4m rods!!


If you could pull an earth rod out, then it was never installed properly in the first place and/or more likely installed close to the building external wall, where all the builders rubble would have been dumped!! Sorry, but ground consolidation is a known fact of life whether you believe it or not!! lol!!
 
Firstly not all TN circuits will have RCD protection,and secondly there are maximum Ze values for TN systems,therefore if a Zs reading was considerably higher than the maximum for a standard OCPD something is clearly not right.That said I would have no problem relying on an RCD to meet disconnection times wher a type B needed to be changed for a type C/D and Zs slightly exceeded the max permitted value.

As I've already stated...if you achieve a TN value of Ra I'm with you all the way......but thinking 10...20...30 ohms is any better than 100-200 ohms ,I'm not.


I must have missed this post!!

Most, if not ALL will be, on a domestic installation if i'm not mistaken!!

Clearly not right, but still protected by a RCD with it's magic 1667 ohm Zs, so complies completely with your analogy!!

All depends what you mean by ''slightly exceeded'' replacing a type B with a type D MCB and the difference can be substantial!! And if Zs values don't comply, then disconnections times will be extended!! But again, no problem we have a RCD to cover it!! lol!!
 
much more of this thread and i will be tempted to bang a scaffold pole in the garden, hopefully will miss the incoming cable, gas main, water main , and drains. aiming for a Ra comparable to the Ze i've already got from a 951 on the lead sheath. :ack2:
 
engineer 54, from day 1 of my apprenticeship it was drummed into me that the regs are the electricians bible and even though they are not a legal document they can be used in a court of law.
So if the regs recommend that a circuit be installed in a certain way, then it is probably advisable to follow them.
We have been treat like sheep from day 1 and to deviate from this path would be a tad risky, in thatif something went wrong through no fault of your own you could find yourself up s...t creek without a paddle
 
engineer 54, from day 1 of my apprenticeship it was drummed into me that the regs are the electricians bible and even though they are not a legal document they can be used in a court of law.
So if the regs recommend that a circuit be installed in a certain way, then it is probably advisable to follow them.
We have been treat like sheep from day 1 and to deviate from this path would be a tad risky, in thatif something went wrong through no fault of your own you could find yourself up s...t creek without a paddle


It doesn't take much to improve on anything it states in BS7671!! As far as the section on TT systems, you would be hard pressed to actually NOT conform! In fact, i would go as far as saying you would have to go out of your way to do so!! lol!!


BS 7671 is basically minimal requirements to be met, there is nothing wrong in deviating from the path, as you put it, if you can substantiate or improve on what is being called for!! There are for example many non-standard circuits that have no mention or reference in either the Reg's or it's various OSG's but conform to all aspects of basic circuit requirements...
 
I have no idea why in fact earth rods were ever reduced from what they used to be, (8 and 10 foot X 5/8'' /3/4'') to these tiny 1.2m lengths you have now.
Rumour has it that the rod length was shortened so all those DI's could get the shorter rods into their ex-company cars :)
 
I reckon TT systems should be outlawed and everything made TN.

To me it seems archaic and unreliable expecting something as important as fault current to somehow dribble its way through soil, rock, sand, concrete, and whatever other crap lies between an installation and its transformer, when there is a perfectly good neutral connection going back to it anyway, which doesn't get worse or disappear in hot weather.
 
Last edited by a moderator:
much more of this thread and i will be tempted to bang a scaffold pole in the garden, hopefully will miss the incoming cable, gas main, water main , and drains. aiming for a Ra comparable to the Ze i've already got from a 951 on the lead sheath. :ack2:

I'd have to be careful banging a rod in at my house.
The Manchester Water Ring Main runs alongside it.
It'd be fun puncturing that! :)
 
You see that's where we completely differ, your all too willing to put your faith in RCD's instead of making the effort to have a TT system work as it should!! You may well install an S type up-front, to cover any down stream RCD's, but lets be honest now, ...how many UK electricians, let alone so-called DI's would even think about installing one?? Most of them are convinced that RCD's are as reliable as MCB's so why would they bother!! Again, having so easily obtained a 15 ohm reading, means that your ground conditions are pretty good, (and that the existing rod is probably a twig that hasn't been installed properly) so i'd of put a little more effort into the system. Who knows, that TN value could well have easily been realised!! lol!!

To be totally honest, i don't really know why you bother installing a TT system if that's your honest view. If your not bothered about Ra values and the importance of stability, why not just add your RCD's and let any bonding to the installation be your reference earthing. Using your argument the 700 ohm Ra from the existing rod is as good as any, it's under your magic 1667 ohms ...lol!! All in all, it's a sad day, when other international earthing standards can teach the UK a thing or two, especially when in many cases, their standards are actually based or taken on/from past British standards!! Personally I'm happy to install to Bs 7671 regardless of whether or not you agree with it.The reason for upgrading the 700 ohm reading was it was picked up on an EICR by myself as not complying with the recommendation in Bs7671,and coded 3. With a functioning RCD it was perfectly safe and did not represent a dangerous situation,improvement only needed to bring it within the 7671 spec. That is the only purpose of an EICR,picking up things which do not comply with 7671....not the regs according to E54.

On all the projects i've ever been involved on, i can't think of a single one where the specifications didn't call for any earthing system to be higher than 1 ohm. That value covered TX installations, as well as other made earthing systems... and your trying to defend your Reg's and it's 200 ohms!!!! ....Quite amazing!! I think most of the projects you are involved in are much,much larger than the TT systems commonly discussed on here....which are very small scale,such as sheds,single dwellings,garages etc.

As the old saying goes, ...you can lead a horse to water but..... lol!!

I must have missed this post!!

Most, if not ALL will be, on a domestic installation if i'm not mistaken!! not correct...only since 2008 has it become the norm for blanket RCD protection,the majority of UK installations are pre-2008.

Clearly not right, but still protected by a RCD with it's magic 1667 ohm Zs, so complies completely with your analogy!!

All depends what you mean by ''slightly exceeded'' replacing a type B with a type D MCB and the difference can be substantial!! And if Zs values don't comply, then disconnections times will be extended!! But again, no problem we have a RCD to cover it!! lol!!Bang on the money mate.....glad you are finally beginning to see the light.

Re-the highlighted.
I'll use an example I have used on here before.
A school computer room...bench trunking with a ring circuit feeding multiple sockets,on a 32a type C and RCD in an enclosure at the CU. The teachers use a master switch on the trunking to shut down at night,and then switch it back on in the morning.Trouble is more computers have been added and now the starting surge trips the MCB fairly regularly. We changed the type C for a type D...Zs exceeded by about 0.2 ohms if memory serves...but it's on an RCD so according to 411.4.9 we can rely on the RCD to meet disconnection times.
Quick fix at minimal cost.
Would you have not accepted the RCD as an earth fault device and insisted rewiring/alteration at considerable expense to the school?...and if so how would you justify that based on a quick and cheap solution in full compliance with the UK regs being available?
 
TT systems cannot be outlawed, they are there as the suppliers cannot guarantee an earth. If they were to convert all the hundreds of thousands of TT systems in the UK to TN systems by PME (as it's impossible to run SWA to all these distributions) just think of the danger which will occur during storms, high winds or whatever causes the loss of the Neutral to the consumers supply systems. I think there would be a lot of live metalwork on a few farms lol
I reckon TT systems should be outlawed and everything made TN.

To me it seems archaic and unreliable expecting something as important as fault current to somehow dribble its way through soil, rock, sand, concrete, and whatever other crap lies between an installation and its transformer, when there is a perfectly good neutral connection going back to it anyway, which doesn't get worse or disappear in hot weather.
 
Haha, wonders never cease to amaze me!!

So what are you saying here, that a project's TT earthing system is different in importance to that of one of your domestic customers (and i'm not talking about sheds!!)?? No way on this earth would i ever see the type of light yor talking about!!

Of course your happy to conform to BS7671, it means you don't have to think about anything or come to that do much about anything either. So in your world an existing useless 700 ohms is worth changing to an equally usless 200 ohms because it says so in the Regs, and all because you have an RCD in place?? Which just about sums up your argument!! That and this existing 700 ohm being perfectly safe, yeah right!! Why even consider the fact that the all singing, cover all RCD is going to fail sooner, rather than later....

Can't really be arsed anymore, you'll only come up with another smart arsed reply that is just going to be, yet another compromise for a working TT system. I'm just wondering if you have ever installed any TT system with a sub 1 ohm or TN value, perhaps before RCDs became the norm?? Probably not, as you still wouldn't see the point and come up with some compromise or other!!
Come to that, Do you really install an S type up front on your TT installations?? Because from your posts on this thread, Frankly i can't really see you bothering, and just using them as an example, to get over the other argument, of totally relying on a single RCD sitting on a numbty Ra value!!
 
I reckon TT systems should be outlawed and everything made TN.

To me it seems archaic and unreliable expecting something as important as fault current to somehow dribble its way through soil, rock, sand, concrete, and whatever other crap lies between an installation and its transformer, when there is a perfectly good neutral connection going back to it anyway, which doesn't get worse or disappear in hot weather.


So tell me, what do you think gives a DNO Distribution Transformer it's earth and it's TN-S cables earth and PME / (TNC-S) neutral conductors it's multiple earthing then?? lol!!

A local stable TN value TT system is better to have, than a supplied TN earthing system. You are in control of that system not others!! Yet many of you scoff at the idea as not being possible, when in fact it's more than just possible!! Though you certainly wouldn't think so, going by this thread and the ''why bother'' attitude!!

The seemingly total lack of understanding towards TT systems in the UK these days, is just amazing!!
 
So tell me, what do you think gives a DNO Distribution Transformer it's earth and it's TN-S cables earth and PME / (TNC-S) neutral conductors it's multiple earthing then?? lol!!

A local stable TN value TT system is better to have, than a supplied TN earthing system. You are in control of that system not others!! Yet many of you scoff at the idea as not being possible, when in fact it's more than just possible!! Though you certainly wouldn't think so, going by this thread and the ''why bother'' attitude!!

The seemingly total lack of understanding towards TT systems in the UK these days, is just amazing!!

THAT is exactly what the lecturer at the college said when I was doing the 2391 course.

Then he spoiled it by saying if you're fitting an outside halogen floodlight which has to be earthed and there's no cpc in the cable, you can link the earth terminal to the neutral at the light ............
 
THAT is exactly what the lecturer at the college said when I was doing the 2391 course.

Then he spoiled it by saying if you're fitting an outside halogen floodlight which has to be earthed and there's no cpc in the cable, you can link the earth terminal to the neutral at the light ............

They always spoil things!! Why would you even think about installing a circuit without a CPC these day's!! lol!!
 
Haha, wonders never cease to amaze me!!

So what are you saying here, that a project's TT earthing system is different in importance to that of one of your domestic customers (and i'm not talking about sheds!!)?? No way on this earth would i ever see the type of light yor talking about!!

Of course your happy to conform to BS7671, it means you don't have to think about anything or come to that do much about anything either. So in your world an existing useless 700 ohms is worth changing to an equally usless 200 ohms because it says so in the Regs,yep and all because you have an RCD in place??yep Which just about sums up your argument!! That and this existing 700 ohm being perfectly safe, yeah right!! yep Why even consider the fact that the all singing, cover all RCD is going to fail sooner, rather than later....nope

Can't really be arsed anymore, you'll only come up with another smart arsed reply yep that is just going to be, yet another compromise for a working TT systemnope. I'm just wondering if you have ever installed any TT system with a sub 1 ohm or TN valuenope, perhaps before RCDs became the norm?? Probably not, definately not as you still wouldn't see the point and come up with some compromise or other!!yep
Come to that, Do you really install an S type up front on your TT installations??new ones...yep Because from your posts on this thread, Frankly i can't really see you bothering, and just using them as an example, to get over the other argument, of totally relying on a single RCD sitting on a numbty Ra value!!

lol..........
 
Well, we were talking about a domestic!! But then why would you install a cable(s) that didn't include a CPC??

One example would be where the distance would dictate a CPC being unreasonably enormous. We're talking miles, not meters lol.

There are many other situations where relying on ADS would not be the best option.
 
So tell me, what do you think gives a DNO Distribution Transformer it's earth and it's TN-S cables earth and PME / (TNC-S) neutral conductors it's multiple earthing then?? lol!!

A local stable TN value TT system is better to have, than a supplied TN earthing system. You are in control of that system not others!!
Good point, I hadn't thought that far ahead. Was just having a rant. I don't think we did distribution transformers on my 5 week course, although that may have been in the two weeks I was off having it large in Ibiza. Can't have missed that much. ;)

On a serious note, the DNO is responible for getting current to and from the installation (Line and Neutral) so why shouldn't they also be responsible for the fault current path as well?
 
Good point, I hadn't thought that far ahead. Was just having a rant. I don't think we did distribution transformers on my 5 week course, although that may have been in the two weeks I was off having it large in Ibiza. Can't have missed that much. ;)

On a serious note, the DNO is responible for getting current to and from the installation (Line and Neutral) so why shouldn't they also be responsible for the fault current path as well?


They are, where they provide an earthing point!! Sometimes the system just cant take any more end user PME connections. It's not always as simple as it first seems, and why you should always ask the DNO, if a PME connection is available. And more importantly, why you should never make your own PME connection, even if you know your next door neighbours on either side has been provided with a PME connection!!
 
Having worked for one of the RECs and got involved with supply and distribution the pme system is the preffered system used at all times by them , you will probably notice more and more overhead TT systems being converted with the new aerial buched conductor(ABC) network , you will also probably have noticed that every 4th pole as required by Distribution Supply regs that the neutral is bonded down to earth with a stake , this is for safety reasons in case the neutral breaks down , There are drawbacks of course firstly the need to test for polarity on the incomming supply and also the loss of the neutral on the incoming supply , and the consequences. But there is no difference whether there are 10 or 100 properties being supplied , as long as the Ze is below the 0.35 . The fault current that returns back to the transformer is no longer fault current from the cut out back to the Tx , only within the customers premises , Yes it is correct that the REC would need to be contacted if you want a PME conversion , you can not do it yourself , but as time goes by more and more of the old TT systems will be converted , Indeed many olde
 
Having worked for one of the RECs and got involved with supply and distribution the pme system is the preffered system used at all times by them , you will probably notice more and more overhead TT systems being converted with the new aerial buched conductor(ABC) network , you will also probably have noticed that every 4th pole as required by Distribution Supply regs that the neutral is bonded down to earth with a stake , this is for safety reasons in case the neutral breaks down , There are drawbacks of course firstly the need to test for polarity on the incomming supply and also the loss of the neutral on the incoming supply , and the consequences. But there is no difference whether there are 10 or 100 properties being supplied , as long as the Ze is below the 0.35 . The fault current that returns back to the transformer is no longer fault current from the cut out back to the Tx , only within the customers premises , Yes it is correct that the REC would need to be contacted if you want a PME conversion , you can not do it yourself , but as time goes by more and more of the old TT systems will be converted , Indeed many olde

Go and ask your Engineer if that is always correct or not!! You may be very surprised by the sound of it!! lol!! Think you must have been working on relatively all new PME installations, and not on existing converted cables that are in excess 60+ years old!! Most of the older TN-S cables that are now beginning to breakdown haven't been completely converted either, many being over the 0.35 ohm, and also carrying TN-S earthing on sections of the same cable!!

I can think of a few valid reasons for the DNO to refuse connection to a PME converted supply, as well as too converted overhead systems as well!!
 
TN-S systems mostly remain TN-S systems , what we are talking about here is a TT system!!
The older TT systems that are converted are allways assesed and Ze readings taken into account before conversion . Their are exceptions where even with a PME supply you would have to install your own earthing system of course!!
 
Got to agree with Eng that TT is by far the most reliable method of earthing. Disregarding the Ra value and the reliance on RCDs argument. The only thing you are relying on is the earthing arrangement at the sup tranny. No supply cable breakdown to worry about at all!
 
Last edited:
Yes your right of course you do have more control of your earth arrangements . It is not unknown for neutral faults to come about on PME systems , sometimes actually melting the bonding cables and taking out appliances in some instances , I have seen it a few times
 
TN-S systems mostly remain TN-S systems , what we are talking about here is a TT system!!
The older TT systems that are converted are allways assesed and Ze readings taken into account before conversion . Their are exceptions where even with a PME supply you would have to install your own earthing system of course!!


I think you should really go and talk to your Engineer if you are really being serious about older DNO TN-S supply distribution cables remaining TN-S!! So what do you think the DNO's do when the lead sheathing of these old cables starts breaking down, ....dig it all up and replace them?? I would confidently say there are more partially converted TN-S cables throughout the UK than fully converted!!


Yes the thread were on, is about TT systems. But you made a post statement that isn't correct, (as you have done again in this post too!!) so i've replied!! Actually, an overhead PME system either converted or purpose installed, will probably all be full blown PME supplies, as they are much easier and cheaper to PME!!
 
Last edited by a moderator:
Just read this thread from start to finish and IMO I think that it will be very useful to many people as an informative and well constructed debate........well done to 'most' involved
 

Reply to External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
As the title says, does a three-pin socket (external) used as charging point need an earth electrode or open PEN fault? Are mode 1 and mode 2...
Replies
17
Views
5K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Called to look at a job today for a previous client. Tumble Drier giving off 'funny smell' and tripped the RCD - Called out her appliance...
Replies
20
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top