Discuss Fault finding questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

L

Leepato

1. I carried out a x1 rcd test on a 30ma rcd and the time came in at 44ms with doesn't comply with the circuit disconnecting by 0.4ms. What is the problem? Old/faulty rcd? X5 was 13ms.


2. Done my continuity test on a ring and all continuity was proved. However my neutrals end to end was 0.61, live end to end was 1.45 and earth was 0.97. Why different on my conductors?
 
1. I carried out a x1 rcd test on a 30ma rcd and the time came in at 44ms with doesn't comply with the circuit disconnecting by 0.4ms. What is the problem? Old/faulty rcd? X5 was 13ms.


2. Done my continuity test on a ring and all continuity was proved. However my neutrals end to end was 0.61, live end to end was 1.45 and earth was 0.97. Why different on my conductors?

1 1x within 300ms
5x within 40ms
2 loose connection on line conductor
 
Last edited by a moderator:
Thats a low reading on 0.28 foe the L-E.

Did you omit everything in circuit that could give false readings?

I mean things like Neons on accessories. With the neon being such a high resistance, it can throw the reading of the IR test.

Looks like a potential earth fault, which is the most common problem, l find. You wouldnt have a neon connected in circuit on the L-E reading as it would be connected in things like fused connection units (between L&N).

What is the circuit under test?
 
Just read that its a ring final sorry for asking.

Look for a line conductor that isnt connected properly and is almost touching the metallic casing. That might explain why youre getting a higher resistance on end to end on the L-L and why youre getting only 0.28Mohms on the IR test.

Just a hunch but l think that you may find that its a possibility..
 
This is the trouble, without stripping the circuit back and inspecting it thoroughly its hard to see where the fault is. It's possibly the only way and the customer will have to pay an hourly rate.
 
0.28 on L-E is obviously a failure as should be much more than 2 Meg, split the cicuit into two radials then retest and the side that has bad reading split down further until fault found.
I personaly wouldn't bother testing rcd on load with those readings.
 
I think leepato should call an electrician in!!!! Basic tests asking some ridiculous ????? Why are the end results different ????? Hello!!!!! A second year apprentice would know why!!!!!!!!!
 
I say the op has not only asked for help with one fault finding test but three no less! You only need EFLI and PFC and you have a full house.

To the king I am: is that paid work? If not i could pimp you out for free EICR all day long :p
 
Did you perform the IR test after you secured your second fix (screwed all accessories such as socket fronts in place)?

The reason l asked is that l once did my IR test first with all wires connected but left the socket fronts hanging, so that the plasterer could do his bit.

When l secured the accessories, the RCD kept activating, over and over. When l performed the IR test once more, my N-E readings had plummeted to lower than 1Mohm.

The reason: When l pushed once of the socket fronts on, l had nicked the neutral wire and it was resting against the metal casing, of the backbox.

Im thinking that its a possibility that youve done the same with a line conductor somewhere.

I would follow thekinglam's advice on this one.

To locate the fault, break the ring into two radials. The bad side will have a higher resistance on the line conductor and you can identify the exact location of the fault by splitting it up further eliminating each leg until you find it.

Do you understand what we mean Leepato?

This was meant for the bottom of page 1. Didnt see page 2 (sorry)...
 
Last edited by a moderator:

Reply to Fault finding questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I saw a Fluke 1653B on Gumtree local to me being sold as faulty. Fault was stated as no continuity between 'N' and 'PE' ports on the resistance...
Replies
3
Views
441
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
627
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock