james king

hi all i was wondering what all do when u come across a fault on a cct. eg a ring final!!

what ways do u do it?

what test do u do?

split rings?

im just asking what u do i know this may sound funy and prob not make sense lol
 
depends on the fault. could be low IR or high continuity, or crossed polarity, and many more. you'll have to be more specific.
 
or some scroats JB nailed under a laminate floor
 
think you need to do a bit of reading. the higher the IR, the better.
 
low IR could be : damaged insulation e.g. nail in cable. damp in a fitting. faulty appliance. faulty fitting.

high continuity could be poor connections
 
I just love Fault finding , tripping lighting MCB , RCD tripping , open circuit on ring mains , low insulation , High Zs reading, motors humming 3 phase , machines inoperative ,

one of the most common is a lighting mcb tripping , normally this is caused by posh lights with burnt out wiring shorting , other faults i have found low IR tripping RCD , fault was caused by young lad peeing over socket , tripping RCD , extension lead in garden powering pond pump had got wet , tripping RCD , out side light full of water , Fire alarms continuosly sounding even after reset , cause burst pipe flooding detector ( shop totally flooded £250,000 worth of damage ouch) tripping MCB , fault located to Rodent attack Dead squirrel found across cables , Tripping MCB fault due to burnt out connector (originally a posted thread ) open circuit on ring main ,cause cable chopped in half then plastered ove

just a few ive come across over the years best one was a call out to no power , this was caused initially by a power cut , but when the power came on still no power , main fuse blown fault traced to a light in an elderly gentlmans lounge , it kept blowing fuses so he wrapped the fuse with 30 amp fuse wire , which in turn blew the 30 amp rewirable fuse which he then wrapped in 30 ap fuse wire which then blem the main fuse , fault was a faulty light fitting testing revealed a low IR reading on the ring circuits , cable was melted probably caused by incorrect fuse wire in fuse , and one reason to reccomend replacing rewirable boards to MCB's
 
Last edited by a moderator:
thats what i thought... so how can u just take the skt plates off to look for low IR??? doesnt make sense.....

say u have high continuity eg 274Kohms u will more than likly have a low IR reading correct?

so what steps would u take in order to track down the high cont reading?
 
okay...im really knackered (because I work now!!?)...but these are the tests you need to complete for a ring main....

Insulation resistance of the ring...

* make sure all switches are ON.
* All loads are removed.
* Remove sensitive equiptment (or link between L and N and test at 250v DC). (if not then use 500v DC).

* Use an Insulation resistance tester.
* Check the testers calibration, be sure its not damaged, check the batteries.

* Test between L-N, L-E, N-E (or link L-N and test to E).
* Minimum reading 1 Megohm, if below 2 Megohm then investigate.




Continuity of ring conductors....

* Step 1. End to end continuity...L-L (r1) N-N (rn) E-E (r2). Record results.
* Step 2. Cross connect L + N. Measure resistance at each outlet between L + N (r1 +rn / 4). Record results.
* Step 3. Cross conect L + E. Measure resistance at each outlet between L + E. (r1 + r2 /4 = R1 +R2). This is your result.


Good luck.


Im going to bed.


Zzzzz. Snore.
 
Last edited by a moderator:
thats what i thought... so how can u just take the skt plates off to look for low IR??? doesnt make sense.....

say u have high continuity eg 274Kohms u will more than likly have a low IR reading correct?

so what steps would u take in order to track down the high cont reading?

I think you realy do need to do a LOT more reading .......
 
fault finding is an art on its own. you can't learn it from books. it's experience. basically, it boils down to logic and breraking down the circuit , ist in half to identify the faulty half, then thatn half in half again, and a gain, till you've found the fault , say between point 6 and point 7 on the circuit. then its time to get the crowbars and hammers out.
 
hers one jigga open circuit on a ring main say live , how to locate the fault you could open every socket and inspect the wirng for disconnected conductors or do as i do , i carry out an R1R2 test or R1Rn , Rn or R2 depending on what the fault is say for instance an open circuit on the Neutral , then i would carry out an R2Rn test so from the board disconnect the tails of that circuit join the CPC and the Neutral to gether and then test the circuit at every socket and check the readings untill i get an open circuit then ill open that socket and retest then ill test from the other leg or the ring and carry out tha same tests untill i fing a sockets that has a disconnected wire , i have had this fault and traced the fault to an open circuit on a section of wire so it was replace that leg lifting the floors we traced the cable and the fault was located to a socket that was behind a radiator cut the socket out JB retested spot on all ok
 

Reply to fault finding in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
842
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
823
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
969

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock