Discuss fault on N&L to CPC in the UK Electrical Forum area at ElectriciansForums.net

J

jimmy

It's been a few years since college and I'm stuck on understanding this,

I'm getting an intermittent fault on kitchen sockets. Causing some tripping.

Broken it down and when I IR test the circuit. L to E is 200+
N to E is 200+
But when I test N&L to E thruster fluctuates between 120Mohnm to 160Mohm

I don't understand why it's over 200 M when I test separately.

Can anyone explain to my stupid brain please. TA
 
Assuming both N-E and L-E have an IR of 220Mohm then the combined IR would be much lower:
1/(1/220+1/220)= 110Mohm

This would explain your situation but whether it's the actual cause or not I don't know!
 
a reading of 120 Meg is good enough to be ignored. your fault is more likely to be an appliance.
 
fault on N&L to CPC

Definitely not an appliance. Thanks big cheese that explains the reading. It's now dropping down to 30Mohm now and again.

So how can I trace intermittent faults without rewiring everything?
 
if the circuit is a ring. guesstimate the mid point and split it. then you may well find a low reading on 1 leg. then split that leg again.... and so on till you narrow it down. even so, 30Meg. will not trip a RCD.
 
fault on N&L to CPC

Spent hours doing that. I get 200+ on leg L&N to E then 10mins later back to below 100Mohm.

I'm worried about the fault to other causing problems to the ladies appliances.
 
Have you taken the sockets off the wall? Is anything damp / newly plastered / decorated? How old is the install? 30M should be findable and I personally would look for it because it could direct you to the site of cable damage etc; a short length of T+E and a few fittings should be able to get over 30M. But 100M... a few years ago your tester wouldn't have been able to read that high. I wouldn't exactly call it a fault and it wouldn't cause any other problems.
 
fault on N&L to CPC

Well I've put all sockets back on and it's reading 200M+ L&N combined. Don't know why. Maybe fiddling with sockets?? Who cares I'm walking away now :)
 
Re: fault on N&L to CPC

Well I've put all sockets back on and it's reading 200M+ L&N combined. Don't know why. Maybe fiddling with sockets?? Who cares I'm walking away now :)

That's that one sorted then! Ermmm....... Daz
 
could have been a cable caught up by a screw or squashed against the back box. by pulling the faceplate off and refitting, you could have cleared the fault.
 
Damp maybe a prime suspect on this one, or the old bottle sterilizer right next to socket or kettle etc . U could remove all sockets and connector block the ring and test cable only. Just s thought!
 

Reply to fault on N&L to CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
383
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
476
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
621
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
464
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock