Hi folks, new DIY member here. Currently (no pun intended ...) working on my new (old!) house; I've replaced a few sockets (in existing locations), but I've recently experienced a problem on a circuit (16A radial - this is the only socket on the radial directly from the CU, via a 30 A junction box).

When I plug an appliance in (anything, extension lead, charger), and flick the 'on' switch at the socket, power is lost to the circuit, right back to the CU. The RCD doesn't trip. If I turn the socket to the 'off' position, power is restored to the circuit. This has only just happened - been using the socket in question since I bought the house.

Any suggestions?!

Cheers!
 
i'd guess at a poor connection maybe at the socket or the JB, even at the consumer unit MCB. putting it in layman's terms,you have power with no load, but as soon as you load the cicuit, the poor connection will not allow current to flow.
 
How are you testing for power?

If it is a neon screwdriver then that is your first problem! They are very unreliable at testing if something is live (or much worse) is dead.

As already said, probably there is an open at the CU or the related breaker is faulty.
[automerge]1588430275[/automerge]
These are the sort of thing you should use for checking for voltage being present:


Also remember it is vitally important that you check the tester is working if you are trying to prove a circuit is dead. You can buy battery powered "proving units" for that, but for most DIY use then checking it on a known live circuit first (or showing the power goes from on to off by flicking the switch) is your minimum alternative.
[automerge]1588430595[/automerge]
Another if the first not in stock:

The idea is they are simple so you can't really go wrong, and they draw a small current so a "floating" cable won't pick up enough stay voltage to show anything (as non-contact and neon screwdriver ones need very little current so can show live on an open cable near other live wires)
 
Last edited:
Thanks both - I've been testing with a 'dedicated pen' (not ideal, I appreciate) - I'm certainly not picking anything up from anywhere else (nothing in the vicinity), and the connections in the socket / JB are A OK (I did these, and have subsequently checked).

In terms of the idea of a poor connection somewhere, I suspect this could also result from damage to T+E within its sheath? The embedded cable might have had a lump hammer over it last week, with hindsight (I'm re-plastering the house). I've chased the cable out of the wall and can't see any damage.

Of course I haven't had the face away from the CU to check the connections are sound here - but could well be a problem with the breaker. Will consult a spark to take a look!

Cheers!

Dan
 
Thanks both - I've been testing with a 'dedicated pen' (not ideal, I appreciate) - I'm certainly not picking anything up from anywhere else (nothing in the vicinity), and the connections in the socket / JB are A OK (I did these, and have subsequently checked).

In terms of the idea of a poor connection somewhere, I suspect this could also result from damage to T+E within its sheath? The embedded cable might have had a lump hammer over it last week, with hindsight (I'm re-plastering the house). I've chased the cable out of the wall and can't see any damage.

Of course I haven't had the face away from the CU to check the connections are sound here - but could well be a problem with the breaker. Will consult a spark to take a look!

Cheers!

Dan
Salford is just on the limit of my area. after covid has calmed down , I could sort it for you if you can't find anyone closer.
 
Thanks both - I've been testing with a 'dedicated pen' (not ideal, I appreciate) - I'm certainly not picking anything up from anywhere else (nothing in the vicinity), and the connections in the socket / JB are A OK (I did these, and have subsequently checked).

Is it a non-contact voltage detector type?

If it is then you are almost certainly detecting a capacitively coupled voltage (aka ghost voltage) on the cable. This occurs when an unconnected cable is in closeproximity to another cable which is live.
When you plug an appliance in it connects the live conductor to the neutral which eliminates the ghost voltage.

If this is occurring at the MCB as well as the end of the circuit then it may be that the MCB has tripped without the toggle moving, or the MCB may be incorrectly fitted to the busbar.
 

Reply to Faulty Socket?! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
751
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
628
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
963
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
845

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock