Discuss Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net

Lintay

-
Reaction score
4
I'm working in a warehouse and replacing the old fuse boards with a new 3 phase board.
The board will be sitting directly above the buzz bar im not sure if I need to put in an isolator in between them to isolate the 3 phase board?
Thx
 
Depends on the rating of the dist-board switch disconnector, the tails you use and what fuses protect the busbar (buzz bar?).

You could always upgrade the dist' board to have a front end MCCB switch/fuse as oppose to a disconnector.
 
I take it your not usually doing this kid of work given the questions?, you have 2 options here, fit an mccb rated at the tails you wish to use or upgrade the tails so that they are rated to the busbar O/L protection (200amps), the latter been the cheaper but you need to check it will fit on your switchgear, if not you can parallel 2 smaller tails up.

Why do you have a 250amp disconnector in the board costing a lot more than a standed 100amp 4 pole disconnector if you only intend to use 25mm tails, what is the designed demand on the dist board?
 
I'm usually doing domestic work but now work for a new employer. He's gave me a 100 amp isolator to feed from the bus bar to then feed the dist-board,my boss has supplied all the materials.
So if the dis-board main switch was 100amp I could connect tails direct to busbar?
Thx guys
 
The isolator load tails will route back through the bus bar into dust-board

No you won't be doing this, the bussbar chamber is not a through route for circuits be they submains or final circuits, you do not need this isolator anyway there are other options I have mentioned already, it does seem your are quite inexperienced in this area, I would suggest and judging from your questions that you bring someone in who has the experience here and work alongside so your can get the valuable experience yourself, the design is totally wrong, your unaware of the relevant regulations which will limit your options here, please take this as constructive advice, errors in this kind of work can be very costly and good, compliant design is crucial here.
 
I'm usually doing domestic work but now work for a new employer. He's gave me a 100 amp isolator to feed from the bus bar to then feed the dist-board,my boss has supplied all the materials.
So if the dis-board main switch was 100amp I could connect tails direct to busbar?
Thx guys
When you say isolator is it fused at 100A. If so you need at least 35.0 conductors to and from it. Have you got additional busbar clamps, I hope you are not going to pair up from existing clamps.
 
I'm usually doing domestic work but now work for a new employer. He's gave me a 100 amp isolator to feed from the bus bar to then feed the dist-board,my boss has supplied all the materials.
So if the dis-board main switch was 100amp I could connect tails direct to busbar?
Thx guys

Im sorry to say this but seems your boss has designed this wrong too, I cannot understand why with a modern distribution board that he hasn't fitted a 100amp mccb front end device in the dist board to allow for reduced tails, all the isolator etc is extra work and wasted space, either this or we don't have the full story here, I'm still lost with the design.

PS - you will need to protect your tails for overcurrent if your not fitting 200amp rated (as stated protects the busbar) tails direct to the 250amp disconnector.
 
Thx for constructive advise darkwood hence why I'm querieing the design.
So could I come straight off the bus bar into dist-board and double up the tails?or will I need to replace the main switchwith a fused switch aswell? Thx
 

Reply to Feeding 250 amp 3 phase board direct from buzz bar need isolatir in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
742
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock