Raptor0014
Esteemed
- Reaction score
- 1,261
Evening all.
I did an EICR recently and then changed a consumer unit.
As part of the EICR process I take off around 25% of all accessories to check terminations etc.
Property was well maintained and EICR was satisfactory with a few C3s. Board was a split load single RCD board. Light and smoke detector circuits being the ones not RCD protected. Owner requested a CU upgrade as I was also installing a EV charge point and they wanted everything in one board.
So I replaced it with a full DP RCBO surge protected board.
After the install and doing all the tests etc I did a final go around to check everything worked and nothing was causing any issues.
Turned the landing light on at the bottom of the stairs and both down and up light RCBOs tripped.
When I removed the switches at the bottom and top of the stairs I noticed a single core red conductor in with the rest of the conductors.
So realised then that the previous installers had borrowed a neutral somewhere, probably in the loft which is fully insulated, boarded and had a load of storage items in there.
At the moment I’ve put the lights on one RCBO. There is still some of the lights on another RCBO as they had an extension built around 10yrs ago. So kitchen, utility and garage are on one RCBO and rest of lights on another. I’ve also labelled the board to say there’s a borrowed neutral on the offending circuit as I need to go back and rewire the circuit properly.
I was just wondering if there was something I was missing in my testing that would give me an idea that a neutral is borrowed? I’ve asked a couple of sparks I know and even my yearly assessor for the CPS. But no one seems to have any sure fire way to tell.
I’ve made a mental note to always take hallway and landing light switches off now as part of the 25%.
But was just wondering if the hive mind of the forum and experience of the members could tell me a way to pick it up so I don’t get a repeat occurrence in the future.
I did an EICR recently and then changed a consumer unit.
As part of the EICR process I take off around 25% of all accessories to check terminations etc.
Property was well maintained and EICR was satisfactory with a few C3s. Board was a split load single RCD board. Light and smoke detector circuits being the ones not RCD protected. Owner requested a CU upgrade as I was also installing a EV charge point and they wanted everything in one board.
So I replaced it with a full DP RCBO surge protected board.
After the install and doing all the tests etc I did a final go around to check everything worked and nothing was causing any issues.
Turned the landing light on at the bottom of the stairs and both down and up light RCBOs tripped.
When I removed the switches at the bottom and top of the stairs I noticed a single core red conductor in with the rest of the conductors.
So realised then that the previous installers had borrowed a neutral somewhere, probably in the loft which is fully insulated, boarded and had a load of storage items in there.
At the moment I’ve put the lights on one RCBO. There is still some of the lights on another RCBO as they had an extension built around 10yrs ago. So kitchen, utility and garage are on one RCBO and rest of lights on another. I’ve also labelled the board to say there’s a borrowed neutral on the offending circuit as I need to go back and rewire the circuit properly.
I was just wondering if there was something I was missing in my testing that would give me an idea that a neutral is borrowed? I’ve asked a couple of sparks I know and even my yearly assessor for the CPS. But no one seems to have any sure fire way to tell.
I’ve made a mental note to always take hallway and landing light switches off now as part of the 25%.
But was just wondering if the hive mind of the forum and experience of the members could tell me a way to pick it up so I don’t get a repeat occurrence in the future.