Discuss Finding transformer VA rating in the UK Electrical Forum area at ElectriciansForums.net

Carolina

DIY
Reaction score
21
Hello everyone. I'm in training but we haven't seen transformers or how they work yet.

I have a transformer here I'm trying to figure out. There are no labels or inscriptions on it.
Primary side has 3 wires: black, blue (AC in), yellow (AC out?) and Sec has red and blue. Labeled USA 18AWG so a 0.8 mm2 (make it 0.75) cross-sectional area if the interwebs conversion sites are to be trusted.

12.5 Ohm between black and blue, 13.5 between black and yellow.

Feeding it AC (200V, should be 240) via black and blue wires makes the sec output around 6.5V, but if I probe neutral and primary yellow it measures 240V.

I wired a 60W bulb to N and the yellow wire and it lit up fine.
My question is: could I use this transformer as a step-up wiring only the primary side? how do I know how much power I could pull through it?

I'm thinking it of using to perhaps brighten up some lights, my mains can go as low as 170V sometimes, you can imagine how sad the output of a 240V bulb would look if you dropped the voltage that much.

Thank you!!
 
You don't mention the physical size of your transformer, but from the figures you gave, it sounds quite small / low power.
If you take typical current rating of the wire on your 6V secondary, that seems to give 30 to 40 Watts, unless I've got that wrong.

You can do as you suggest, and use the primary as an autotransformer to step up 200 to 240V, but the maximum power you have available should be limited to that figure above for safety.
 
The danger here with intermittent voltage supply is that it can go UP, as well as down. Plus, you'll still see a 30v drop from 200 to 170, it'll just be 240 to 210 instead. A sudden inrush from 170 to 240 could do any amount of damage as you'd see a spike of 270v.

Unless I'm misunderstanding your post?
 
I'm thinking it of using to perhaps brighten up some lights, my mains can go as low as 170V sometimes, you can imagine how sad the output of a 240V bulb would look if you dropped the voltage that much.
LED bulbs driven from constant current or constant voltage SMPS would give you full light output over a wide range of mains voltages, which would be a lot safer way of achieving that objective!
 
To understand the significance of using this transformer in the way you want, we need to look at how an autotransformer is designed. But first let's recap what you know about this one.

The primary is almost certainly intended for two options of supply voltage that would typically be selected by a concealed switch on the equipment. The high voltage option would use the ends of the winding, black and yellow, The lower voltage would use black and the blue tap. Most of the primary turns are between black and blue, with a smaller number between blue and yellow. The turns ratio is in proportion to the voltage ratio: If 200V on blue gives 250V on yellow, then the blue tap is at 4/5 of the total number of turns. This is an unusual position for the tap, I would expect to see nearer 220/240 for typical supply voltage options. There is a possible alternative explanation for the function of the tap but it's not important to go into that here.

Regarding the resistance measurements; obviously the resistance between the ends of a winding is the sum of all the resistances from each end or tap to the next. Resistance measurements are useful to find the order of the taps and identify their likely functions, but will not tell you the voltage ratios accurately because not all turns have the same length of wire. If the black end is near the middle of the winding each turn between black and blue will be shorter than between blue and yellow so the resistance ratio will be different to the turns ratio that governs the voltages.

It is not normal to mark the wire gauge on a transformer. If you are reading the 18AWG off the lead-out wire, it only relates to the lead-out itself, not to the transformer winding and tells you nothing about the transformer's rating. The best way to assess the VA rating is to compare the size and weight to transformers of similar design and function. There are limits to which the iron and copper can be worked, and in all commercial power transformers these are adhered to quite closely. Therefore the weight of material is closely linked to the VA rating. I mention comparing similar designs because special types of transformer with extreme voltage or currents, or transformers other than normal AC power types, might not have comparable size and weight.

What you want to do is to operate the primary as an autotransformer (input and output on the same winding) with the input on the blue tap and output at the yellow end of the winding, to increase the voltage by the turns ratio. You are probably aware of the basic relationships with any transformer: Power out = power in. Vout / Vin = Iin / Iout, ignoring losses. You want to step up with Vout = 5/4 x Vin and therefore Iin = 5/4 Iout, and discover what load the transformer can safely handle.

I will spoil the plot here and say that for this ratio, the safe load is in the same ballpark as the transformer's official VA rating, so if you have a transformer comparable in size to a commercial 100VA transformer, you could connect 100VA load to it. But the reason for this is more a coincidence than because of any relationship between the VA rating and the load. It would not apply if the voltage ratio were over 1:2; you might be limited to a lower load VA than the transformer rating. It's interesting to explore the reason behind this in an autotransformer.

If you were drawing the output from a secondary winding you would need a transformer equal in VA rating to the load. The primary would be wound for Vin and Iin, and the secondary for Vout and Iout. The winding wire size will be matched to the current. In the case of a step-up the primary will be wound with larger wire because Iin > Iout. If the voltage (and hence current) ratio is large, the wires will be very different sizes.

In an autotransformer, different currents flow through different parts of the winding. In your step-up application, the current through the blue lead will be Iin, that through the yellow Iout, and that through the black the difference between the two. Now we come to the important bit. In your auto connection, only the 1/5 extra voltage and hence 1/5 of the load VA is being transformed. The other 4/5 comes directly from the supply. So for an auto stepping up 4:5 the transformer only needs to be a fraction of the size of a comparable double-wound transformer. This is why auto configuration is much more economical when only a small voltage ratio is needed. But your transformer will not handle a load of 5x its VA rating because the wire of the section of winding carrying Iout is only of a size rated for rated VA at Vin. In a purpose-made autotransformer, that part of the winding would be rated 5x higher. Your transformer will however in theory handle a load slightly greater than its VA rating, because there is no heat dissipation from the unused secondary and the current in the main 200V part of the primary is much lower than designed (only Iin-Iout) so the heat dissipation in the 50V part could be allowed to increase a little. Therefore Iout could be higher than the designed Iin.

The take-away from this is that when a double-wound transformer is re-purposed as an autotransformer, the limiting factor might be the winding current rating, not the overall VA rating. But you can make your own autotransformer that does use all its VA capability. A boosting or bucking connection takes a double-wound transformer with a low-voltage secondary and connects that in series with the primary. Now you have the necessary difference in wire gauge to allow for the full Iout and in your case a transformer with a 50V secondary stacked on top of the primary will power a load VA of Isec x Vout or around 5x the transformer VA rating.

But note the point made by @Rockingit: If your mains supply goes up to 'normal' volts the output will be very high and might damage your equipment. This needs serious consideration.
 
Last edited:
Some pics. Heavy lines indicate larger conductors.
 

Attachments

  • 16580555265173323642443540388265.jpg
    334 KB · Views: 10
  • 16580555563416920921954747727178.jpg
    353.3 KB · Views: 11
  • 16580555846503933881776691798758.jpg
    251.2 KB · Views: 11
As always, thank you for your erudite explanation Lucien.

PS I accept your comment about the secondary 'wire gauge' - that was a mistaken path to follow!
 
You don't mention the physical size of your transformer, but from the figures you gave, it sounds quite small / low power.
Hi, thanks for your reply, sorry I forgot about the size. Please excuse the crudeness of my test bench.
Here's how it looks next to my clamp meter, dimensions of the heatsink are 7.5x5.0x6.5 cm. Weight is 1.73 kg.
DSC_5531.jpg


The danger here with intermittent voltage supply is that it can go UP, as well as down. Plus, you'll still see a 30v drop from 200 to 170, it'll just be 240 to 210 instead. A sudden inrush from 170 to 240 could do any amount of damage as you'd see a spike of 270v.

Unless I'm misunderstanding your post?
But note the point made by @Rockingit: If your mains supply goes up to 'normal' volts the output will be very high and might damage your equipment. This needs serious consideration.
You're right, no matter what the input V is there will be always a 40V difference between the transformer L and any N. Though I yet have to see full 240V on my mains, I live in a rural area so 200 is already as high as it goes in a good day.

Something I could do is take apart a cheap "fridge protector", this tiny AVS:
fg.jpg

that automatically cuts off the load whenever Vin goes over 250 and wire it to the transformer Vout, and perhaps add a selector switch to override it in case of failure.

LED bulbs driven from constant current or constant voltage SMPS would give you full light output over a wide range of mains voltages, which would be a lot safer way of achieving that objective!
I did this already, in fact I've asked here in the forum about what power supply, circuit and wiring would be better to power some 12V lights although incandescent (I have plenty of them, it's a long story), I've installed a few LED ones in a different room using a smaller power supply and they're also working fine.
Problem with regular AC LED bulbs is that all of them are rated for a 220-240V input and, well, I'm short on voltage for them, below 190 some start flickering, others (the filament kind) dim too much and others don't work at all. Same for CFLs, though tubes seem to be a bit more tolerant to the dips. So that's that.


@Lucien Nunes thanks for all the clarifications. I've bookmarked your comment to re-read it later on, as for the transformer itself I spent some more time playing with it, used a strings of lights that made up to 360W, tbh I went for resistive loads because they're simple to work with, and the transformer got a bit warm after 30 minutes, there was no audible hum or buzzing coming from it and Vout (241) remained stable at all times.
I'm not as advanced enough to create my own transformers yet but I do have a pending project that's making my own variac, that's simply a variable autotransformer. Seems like transformers are a whole different beast I'm not ready yet to tame so to speak.
 

Reply to Finding transformer VA rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi all, No electronic knowledge here. The plug/transformer of a led lightstring is fried. Now I am trying to find a replacement on Aliexpress...
Replies
9
Views
2K
I never did like transformer theory in my degree course and that was 40 years ago. I'm a boat builder now and we tend to have big battery banks...
Replies
3
Views
1K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
789
Hi, I'm replacing an old AT88A with the AT175F for my hydronic heating, which is connected to my 2-wire mercury t-stats and Honeywell V8043F zone...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock