Hi all

Just a quick one.

For a fire alarm loop addressable system. Fp200 1.5mm cpc 1.5mm

To obtain R1+R2 would you treat the "loop" as a radial in effect and link brown and earth in connector then tester on other leg.

Or would you treat it as a ring and figure of eight and can be tested at any point.?

Thankyou
 
It can be handy if trying to calculate length of loop to prove to manufacturer support you haven't gone mad.
In general IR testing is far more pertinent before comissioning.
 
It can be handy if trying to calculate length of loop to prove to manufacturer support you haven't gone mad.
In general IR testing is far more pertinent before comissioning.
As you say IR is more pertinent / important to identify any shorts or cable faults
A check of the resistance of each conductor loop will verify that all the connections good and will give a resistance to calculate the loop length don't see the point of the R1 + R2 it's not likely to carry any fault current
 

Reply to Fire alarm loop testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock