Discuss Fire Alarm system Categorization in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

spud1

-
Arms
Reaction score
55
Hi all,

For those of you who have experience in fire alarms (comp to BS5839 -1);
I am having a disagreement with a client about the categorization of a fire alarm in their HMO which I recently inspected & tested.
They insist it is cat LD1 which is the case all apart from the absence of a detector in the under stairs cupboard where the meter and CU is located.
I say there should be one in there for it to be cat LD1 but they say the installer of the system carried out a risk assessment and deemed it unnecessary because the CU is Amend 3 compliant!? Never heard of this before. Also no detectors in crawl space roof voids either side of the loft conversion?

Cheers
 
Hmo come under part 6 not part 1 and therefore category LD1 and L1 have different coverage. Unless the cupboard is greater than 1m sq it is not a requirement to cover, unless it poses a risk area. Loft spaces are not required under part 6, unless a again the area poses a risk, such a solar panel invertors, or central heating boilers-heat recirculation units
 
Hmo come under part 6 not part 1 and therefore category LD1 and L1 have different coverage. Unless the cupboard is greater than 1m sq it is not a requirement to cover, unless it poses a risk area. Loft spaces are not required under part 6, unless a again the area poses a risk, such a solar panel invertors, or central heating boilers-heat recirculation units
Thanks Tazz,
Good point about it coming under part 6.
The meter and consumer unit (amend 3 compliant) are in the cupboard, would that not be classed as an increased risk area? The cupboard is around 1m3.
 
Its really down to the local council to state their risk asessment under the HMO licence, so this should be available to you. Although we can only give advice to HMO customers....the original HMO licence stands, to cover the property.
 

Reply to Fire Alarm system Categorization in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
307
The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Replies
19
Views
950
I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Replies
5
Views
1K
Hello, I applied for a retrospective completion certificate for kitchen relocation. The work was done about 7 years ago. The building standard...
Replies
26
Views
6K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock