Discuss First eicr and low iR readings in the UK Electrical Forum area at ElectriciansForums.net

I'm sure you know that such a low reading is a definite C2, therefore an unsatisfactory outcome on the EICR. Best way to find it is to split ring into sections, and narrow down the location. I recently had a similar result caused by damp affecting several newish sockets and fcus on one particular wall.
 
Hi - the heating system (with its pumps and motorised valves) is always suspect to me and easily removed from play with the DP FCU. Try testing at 250V (L+N to E) as there may be surge suppressors somewhere getting lively. If you’ve time and out of interest I’d whip the fronts off all the outlets and see if that changes anything. If this is the place from the other post, I recall from the cutout pic it had heat affected tails, so there might be further carbonised insulation...
 
Hi - the heating system (with its pumps and motorised valves) is always suspect to me and easily removed from play with the DP FCU. Try testing at 250V (L+N to E) as there may be surge suppressors somewhere getting lively. If you’ve time and out of interest I’d whip the fronts off all the outlets and see if that changes anything. If this is the place from the other post, I recall from the cutout pic it had heat affected tails, so there might be further carbonised insulation...
Thanks wilko, gave my self plenty of time,all day in fact, and took off every to the best of my knowledge socket front, yes same place as the other thread and the cpcs on the older (pre 2005) wiring are all blackened/carbonised
 
Last edited:
the cpcs on the older (pre 2005) wiring are all blackened/carbonised

Blackened?! Any pics? Not familar with that at all. Is the whole place full of oily soot from wok fires or what? That could be a significant factor in low insulation.
 
Blackened?! Any pics? Not familar with that at all. Is the whole place full of oily soot from wok fires or what? That could be a significant factor in low insulation.
Hi - this visual info could explain the low IR and would suggest those cables need to be replaced.
Sorry for the delay chaps.....
729870C6-28C2-49E1-900F-534BF7C592F0.jpeg

You can make out the blackened cpc, it’s the length of what exposed/visible but only on the older cable
 
The terminal screws are the same. This is normally caused by atmospheric conditions. Are the line and neutrals the same.
 

Reply to First eicr and low iR readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
421
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
699
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
767
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
640
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
675

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock