Here goes.....Im doing the 2357 C&G course. For one question I have to do a cable calculation for power and lighting circuits.
I am having issue with the ground floor lighting circuit, in a domestic dwelling, as in I am way off the 3% tolerance for volts drop.
Details as follows:
Plan view of ground floor provided.
x2 Fluorescent fittings. 2x100wx1.8/230v = 1.57A
x5 Ceiling pendants. 5x100w/230v = 2.17A
x6 Internal Wall fittings. 6x100w/230v = 2.6A
x4 External wall fittings. 4x100w/230v = 1.74A
x8 50W 12v downlighters. 8x50w/230v = 1.74A ( as I have assumed a transformer at each fitting)
I have calculated length of run at 102mtrs from dist board through the whole ground floor (as I am assuming that switch drops, and strappers are included?)
So here I am so far.... Assumed 100w for all light fittings except the downlighters.
Total current demand is @ 9.82A, allow for diversity of 66% = 6.5A. After correction factors...Table 4D2A = 1mm.
Volts drop @ 44. mv/a/m x IB x length/1000 = 44 x 6.5 x 102/1000 = 29.2V!!!!
Firstly Have I made a mistake so far? Have I missed something obvious?
I do have an idea on how this can be changed....I'm sure somewhere I read rule of thumb x10 100w fittings per circuit?
If so shall I break this down into 2 circuits? Please point me in the right direction!
I am having issue with the ground floor lighting circuit, in a domestic dwelling, as in I am way off the 3% tolerance for volts drop.
Details as follows:
Plan view of ground floor provided.
x2 Fluorescent fittings. 2x100wx1.8/230v = 1.57A
x5 Ceiling pendants. 5x100w/230v = 2.17A
x6 Internal Wall fittings. 6x100w/230v = 2.6A
x4 External wall fittings. 4x100w/230v = 1.74A
x8 50W 12v downlighters. 8x50w/230v = 1.74A ( as I have assumed a transformer at each fitting)
I have calculated length of run at 102mtrs from dist board through the whole ground floor (as I am assuming that switch drops, and strappers are included?)
So here I am so far.... Assumed 100w for all light fittings except the downlighters.
Total current demand is @ 9.82A, allow for diversity of 66% = 6.5A. After correction factors...Table 4D2A = 1mm.
Volts drop @ 44. mv/a/m x IB x length/1000 = 44 x 6.5 x 102/1000 = 29.2V!!!!
Firstly Have I made a mistake so far? Have I missed something obvious?
I do have an idea on how this can be changed....I'm sure somewhere I read rule of thumb x10 100w fittings per circuit?
If so shall I break this down into 2 circuits? Please point me in the right direction!