Discuss Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net

@clanky boy notwithstanding any of the last four pages, somewhere you have a Ghost voltage on your supply to these lights, this can be caused by many different reasons, but usually its a two way switch somewhere on the loop with an induced voltage between the two switch's, a clean supply or snubber/snubbers are the only way to cure the problem IMO.
 
The 47nf is maybe a little low. I think 100nF (0.1uF) or more with say 120 ohms in series is the usual sort of thing.
There have been threads on this forum before about this.

This has been a suggestion before:
You may still need more than one!
I have ordered a few 150nF and I'll try that - if no joy I'm off to tie a noose!!!
Thank you everyone for the help and advice - if the new snubbers don't work I'll pick this up again.
 
Mike, apologies for delayed reply, but I finally got round to fitting the snubbers today. I got 8 x .1uF 120ohm and fitted all of them, one more each time. It has vastly improved but problem still there - that equates to .8uF and 960ohms! I disconnected them again and tried my 100w bulb again - problem goes instantly yet it equate to 500ohms and .41A, if my maths serves me correctly. Am I missing something or do I need much bigger snubber(s) say .22uF (220nF),470ohm snubbers- your thoughts please, kind regards, Mark.
 
If you know where the main power for the downlighter runs, put the snubbers as close to the first lamp as you can.
I have put 7 snubber s into the first light JB. Flickers and then peters out over 30 seconds.
 

Attachments

  • Screenshot_20230815-152850_Gallery.jpg
    935.2 KB · Views: 28
There's got to be more to this than just needing more and more snubbers chucking at it surely?

Not sure what though I must admit.
 
The snubbers need to be on each individual light not all bunched together, see post No 39 that is just one light connected at the lower end of the junction box.

Its the bulb that is picking up the Ghost voltage not the circuit.
 
Last edited:

Reply to Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
700
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
635
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
317

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock