Flashing LEDs when fan and lights off

Discuss Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
Good afternoon everyone.
I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on. I have wired the feed to the fan via an adjustable overrun timer and DP isolator with the SL for the fan timer coming from the light switch.

The issue is with lights and fan off the LEDs are flickering dimly - this stops when the DP switch is opened. I assume there is a small leakage to N from somewhere in the timer causing the sensitive LEDs to flicker, which when the DP switch is opened cannot occur hence the flicker stops.

I have bought and fitted a 47nF 100r capacitor and connected it to all possible combos in the timer - no change. The only thing that stops it is if I disconnect the SL from light switch yo timer - but obviously the fan wont run now.
I have spoken to a qualified sparky who's only suggestion was the capacity action as a snubbed - he doesn't know what to do now!

I am stumped and would appreciate any advice please.
 
Good morning everyone. As mike suggested I disconnected the SL at fan - no change.
I have fitted a different timer - no change.
Cables are not particularly close or bunched - so I think unlikely it's inductive from an adjacent cable.
Showing between 7v - 11v between L/N at one of the LEDs.

I have wired a pendant with 100w lamp across one of the LEDs L/N and problem gone, but obviously I can't keep that there!

I'm using .47uf 100r capacitor as snubber, but are these large enough (or whatever), as the 100w lamp appears to be able to dissipate the stray voltage.

Yet again I appreciate all the help.
Thanks for all the info. It doesn't get any clearer!
Have you tried disconnecting S/L from the timer and measuring the voltage on the 'Manrose' S/L terminal (if any).

I'm presuming all the lamps (by which I mean the bulbs themselves) on this circuit are mains voltage, there's no led driver or electronic transformer on this circuit, no shaver socket or charger, or anything we're missing?
 
Last edited:
It would help me if you could disconnect the entire LED string (complete with the shower light) from its supply, eg at the terminal block or whatever it is that you show in your diagram, and measure the resistance of the lamp chain between L and N. I would expect it to be very low, eg 10 or so ohms with the shower halogen bulb in circuit.
 
Thanks for all the info. It doesn't get any clearer!
Have you tried disconnecting S/L from the timer and measuring the voltage on the 'Manrose' S/L terminal (if any).

I'm presuming all the lamps (by which I mean the bulbs themselves) on this circuit are mains voltage, there's no led driver or electronic transformer on this circuit, no shaver socket or charger, or anything we're missing?
I will measure the V at the SL at the timer.
The spots are 240v ovio inceptor nano5.
The Halogen is not mains voltage, it's 12v from a Tx just before the light that is set into the extractor inlet over the shower.
I might disconnect the Tx and see if that does anything.
 
It would help me if you could disconnect the entire LED string (complete with the shower light) from its supply, eg at the terminal block or whatever it is that you show in your diagram, and measure the resistance of the lamp chain between L and N. I would expect it to be very low, eg 10 or so ohms with the shower halogen bulb in circuit.
I'll go and do that now - back shortly.
 
I'll go and do that now - back shortly.
Sorry, sent you on a wild goose chase!
I had the feeling the shower light couldn't be mains halogen with what we've seen, as it's not acting as a snubber!

If you put a mains halogen somewhere in that chain, that would be one way of solving the problem.
I think Mike is right, it just needs more snubbers until the effect goes away.
 
The voltage at SL is 11.4v.
All LEDs and halogen, 2 snubbers and 100w lamp - approx 100M ohms
All LEDs and halogen, 2 snubbers- 90M ohms
All LEDs and halogen, 1 snumber- 100M ohms
All LEDs and halogen, - 120 - 150M ohms.
I have taken a picture of the 2 snubbers I have - are these suitable or can you recommend something else please.
 

Attachments

  • Screenshot_20230806-121336_Gallery.jpg
    706 KB · Views: 17
I have taken a picture of the 2 snubbers I have - are these suitable or can you recommend something else please.
The 47nf is maybe a little low. I think 100nF (0.1uF) or more with say 120 ohms in series is the usual sort of thing.
There have been threads on this forum before about this.

This has been a suggestion before:
You may still need more than one!
 
@clanky boy notwithstanding any of the last four pages, somewhere you have a Ghost voltage on your supply to these lights, this can be caused by many different reasons, but usually its a two way switch somewhere on the loop with an induced voltage between the two switch's, a clean supply or snubber/snubbers are the only way to cure the problem IMO.
 
The 47nf is maybe a little low. I think 100nF (0.1uF) or more with say 120 ohms in series is the usual sort of thing.
There have been threads on this forum before about this.

This has been a suggestion before:
You may still need more than one!
I have ordered a few 150nF and I'll try that - if no joy I'm off to tie a noose!!!
Thank you everyone for the help and advice - if the new snubbers don't work I'll pick this up again.
 
Mike, apologies for delayed reply, but I finally got round to fitting the snubbers today. I got 8 x .1uF 120ohm and fitted all of them, one more each time. It has vastly improved but problem still there - that equates to .8uF and 960ohms! I disconnected them again and tried my 100w bulb again - problem goes instantly yet it equate to 500ohms and .41A, if my maths serves me correctly. Am I missing something or do I need much bigger snubber(s) say .22uF (220nF),470ohm snubbers- your thoughts please, kind regards, Mark.
 
The snubbers need to be on each individual light not all bunched together, see post No 39 that is just one light connected at the lower end of the junction box.

Its the bulb that is picking up the Ghost voltage not the circuit.
 
Last edited:
The snubbers need to be on each individual light not all bunched together, see post No 39 that is just one light connected at the lower end of the junction box.

Its the bulb that is picking up the Ghost voltage not the circuit.
I had 8 spread across 4 lights at each Jb, but you said put them as close to the first light, hence all 7 on a short tail off yhebjb for the first light - I'll put them back on each light on then.
 
The snubbers should be across each bulb, not the junction box starting at the closest bulb to the main junction.
i don't get why it matters where you put the snubbers.

I'm assuming our hypothesis is that the flashing of LED's is being caused by an 'induced' /capacitively coupled voltage arising from the circuits switched live conductor(s) close proximity to permanently live conductors.

If you consider the equivalent circuit of what's happening, you have the capacitance (and inductance?) of the coupling between the cables (no resistive component unless there's a fault!) , and the capacitance/resistance of the snubber, acting as a potential divider, with the lamps across the snubber side. The resistance of the copper wire is absolutely negligible in relation to the capacitances in play, so it can't matter where you put the snubbers - they are on the equivalent of a bus-bar whether you put them distributed along or all at one end. It's not as if there can be a gradient of induced voltage along the cable!

With 8 x 0.1uF not completely solving the problem, that implies the impedance of the coupling between L and SL is at least equivalent, which I find hard to believe.
The only thing I can think of is that somehow this ghost voltage is partly or mainly dc, the capacitors only dealing with the ac bit of course.
Is there any way the timer could be responsible for a dc component?

I would like to suggest that, if possible, an insulation resistance test is done on this circuit.
And I think it would be useful to map out the path of permanent live and switched live, in terms of where those conductors run parallel to each other in the cables, and see if an alternative source of the power, or an alternative way of wiring, removing most of those parallel paths, could reduce the impedance of the ghost voltage, if that's what it is!
 
Are you using PMR209 snubbers? Your picture on the post above does not look like them.
They are not pmr 209, but are equivalent rating. I'll get some mr209s ordered and try them - trouble is there are 30 odd types in RS and they don't have any with sh1 on them, like the ones in your picture Mike - does this matter - will any pmr209 do the job. .47uf, 1uf .22uf what rating do you suggest please?
 
I can't see how that would matter in this case. As long as the values are the same. It's only 2 components bundled together in one package.
 
Hi Clanky
TBH I'm not sure spending more on snubbers is necessarily the way to go.
Keep trying with them if you like, but I feel there is something else going on here.
Is it the case that disconnecting the SL from the Manrose timer stops the LED's flashing?
Could you confirm that?
 
Just to follow on from my previous post - things to try.
You originally said that turning off the DP switch to the fan stopped the led's flashing. Presumably that is still the case?
If so, can you try disconnecting the SL from the Manrose and see if that stops the flashing.
If it does, one way of solving the issue would be to install a DP light switch, which looks do-able from your sketch.

e.g. https://www.electricaldirect.co.uk/...-1-way-double-pole-light-switch-white-919713?

IMG_0236.jpeg

Otherwise could you, as a separate experiment, disconnect the halogen driver (mains side) and see if that makes any difference?
Sorry about all the questions/suggestions. This is an usual situation that snubbers are not easily resolving, and I'm concerned that 'fixing' it with snubbers would be just hiding an underlying cause that could be a fault or a 'feature' of one of the accessories.
 

Reply to Flashing LEDs when fan and lights off in the UK Electrical Forum area at ElectriciansForums.net