I don't think any of this British Gas slating is helping the OP with his problem when the boiler probably has nothing to do with it.
Discuss Flickering light, tripping rcd in the UK Electrical Forum area at ElectriciansForums.net
Nuisance tripping is always a pain to find.
It does sound like a loose connection somewhere to me.
Could you divide the circuits (temporarily) onto other RCDs or RCBOs to identify the problem circuit.
Also, just a thought but what lamps are we talking about? ...Some LED lamps in standard SELV lights (i.e. without a dedicated LED Driver) can flicker.
All type of lamps some led some filament. Thinking of putting boiler on a rcbo in case it's a build up of earth leakage. Lights flickering has got me. Think a look at tails main switch is in order. But everything was tight 3 weeks ago.Nuisance tripping is always a pain to find.
It does sound like a loose connection somewhere to me.
Could you divide the circuits (temporarily) onto other RCDs or RCBOs to identify the problem circuit.
Also, just a thought but what lamps are we talking about? ...Some LED lamps in standard SELV lights (i.e. without a dedicated LED Driver) can flicker.
Fair point, the technical staff probably have the range of competence you'd find in any 8000 souls but the experience of friends and family suggests the business model is 'sell a boiler no matter what'.I don't think any of this British Gas slating is helping the OP with his problem when the boiler probably has nothing to do with it.