Discuss fluke 1652 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

H

holte end74

alright lads , when i do a R1/R2 test on a ring main do i use the lead with a plug? if yes how do i plug this into the tester do i just use the red and green or do i also plug in the blue one ?
 
You only need the green and red test leads for an R1+R2 measurement, usually made easier with a socket adaptor.
 
Last edited by a moderator:
Kewtech socket adaptor all the way. saves having to null leads between tests :D Also get the lighting set too.........Cant remember the last time I used the socket lead or the push button test lead.
 

Reply to fluke 1652 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
693
I saw the sponsored post on this forum for magnetic leads to avoid removing conductors when doing an R1+R2 test, here...
Replies
2
Views
487
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi, just hoping for a bit of advice. When I travel abroad (Europe, predominantly Spain/Cyprus) I usually take a single travel adaptor and a UK 4...
Replies
2
Views
441

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock