Discuss Fluke 1653b Tester Faulty? in the Lighting Forum area at ElectriciansForums.net

Ross1

-
Reaction score
16
Hi guys,

Lately, when testing Ze and Zdb on PME and TNS my tester has been reading 0.00 and PSCC is alwats 10kA
Has anybody else experienced this.

It was calibrated in june. Ive had it for 6 years.

When testing Zs on any circuit (which is the same setting as Ze it is giving me a reading.

Any help would be appreciated
 
Hi mate I have the same tester and when I first bought it I had the exact same issue!

I sent it off to fluke and they returned it stating that it was fine and nothing wrong with it however it's work fine ever since.

Unfortunately I never found out what was wrong with it.
 
This might sound daft but is it possible that you have nulled the leads with bad contact at the probes or nulled one set of leads and are now using another, so that the stored offset is too high? The 1653 saves the null and uses it on continuity and loop impedance tests until you change it. Then when you take a reading it will subtract too much and possibly hit zero every time on low Zs and low continuity readings.

I don't know what it does if measurement minus null is less than zero - one would hope it would show a negative figure to indicate an invalid null but I know at least one old model of tester that didn't, so it still gave a sensible-looking zero with the probes held together leading you to assume that the null is correct,
 

Reply to Fluke 1653b Tester Faulty? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I...
Replies
27
Views
7K
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
I forgot I had a Di-Log 9803P so called '17th Edition Tester!?', it was a rash ebay purchase a long while ago intended as a spare, and I discarded...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock