Discuss Fluke tester in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
229
Hi guys, for those of you into testing a lot, using a Fluke 1652C all in one tester. What does EER 5 mean when testing? I'm told it could mean noise. Could someone explain please?
The test are mainly carried out on larger size distribution cables (longer runs etc) as opposed to domestic installations. Would you say that the flukes are aimed at the domestic market? Thanks
 
Error 5 does indeed indicate noise, however a work around (provided the circuit isn't rcd protected) is to select the L-N option.
Null the leads, then connect the L to phase and N to earth.
This will give you a fast Zs reading that's proven very accurate on a properly calibrated fluke when comparing those readings with other makes of tester.
 
Error 5 does indeed indicate noise, however a work around (provided the circuit isn't rcd protected) is to select the L-N option.
Null the leads, then connect the L to phase and N to earth.
This will give you a fast Zs reading that's proven very accurate on a properly calibrated fluke when comparing those readings with other makes of tester.

The anti trip low current test should not be used for non RCD circuits, the high current test should always be used as the first option.
 
The anti trip low current test should not be used for non RCD circuits, the high current test should always be used as the first option.

Agreed Dave,
My post relates to those models in the flook range that don't have the high current option ie the 1651 without b or c prefix.
With those models, if you connect the way I describe, your effectively performing a high current test.
Of course high current is not an option with rcd's in circuit for obvious reasons.

To the OP your Flook 1652C DOES have high current option.
 
Last edited by a moderator:
Agreed Dave,
My post relates to those models in the flook range that don't have the high current option ie the 1651 without b or c prefix.
With those models, if you connect the way I describe, your effectively performing a high current test.
Of course high current is not an option with rcd's in circuit for obvious reasons.

To the OP your Flook 1652C DOES have high current option.

Then those testers are not fit for purpose!

High current testing is possible with RCDs in the circuit using the alternative Zs test method. The only time it's not really possible is with ring circuits.
 

Reply to Fluke tester in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Replies
12
Views
1K
Could someone tell me if it is possible in fluke 1663/1664 to activate the option to carry out an insulation test without having the finger fixed...
Replies
4
Views
892
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
653

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock