Discuss Funny readings continuity of protective conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

Simon Hall

I'm doing an continuity test on a lighting circuit and I'm getting funny readings I'm putting on test lead on earth and one on switch live then I'm getting a reading of around 1.4 ohms but then when I'm checking the polarity it's shooting up to around 93 ohms but not breaking the circuit as you would expect yet when the power is on the light works fine I'm totally lost now any help would be much appreciated thanks
 
sounds like the 93ohms is the (cold) resistance of the load.
 
If you have the main switch is still closed and the earth and neutral are still in their respective bars, e.g when using a link wire from line to earth, then you can read the resistance of a piece of equipment via the neutral earth link when the switch is open. (it will also give a slightly lower R1+R2 than actual when switch closed)
R1+R2 odd reading.jpg
 

Reply to Funny readings continuity of protective conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I would like to get some information on what protection is on a multi meter when accidentally testing a live circuit while the meter is on the...
Replies
1
Views
483
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
429
OLDBOY
O
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi I am trying to do the 180 degree test on the aramature of a 240 volt electric motor, out of a blender. Youtube would sujest that the...
Replies
5
Views
671
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock