Search the forum,

Discuss Fuse size? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nicsin02

Today my job was to change fuses in switched fused spurs from 13a to 3a. It was for boilers and the electrician beforehand didn't change them. The circuit is protected by a 6a mcb and fed using 1mm twin and earth cable. Surely if the cable is protected by a 6a mcb then there is now risk of the cable burning out because it would obviously trip rendering the 13a fuse pointless? So my question is would it have been safe if it was left as a 13a in the spur? Thanks
 
hi there . my answer would be yes , it is safe as the 6a fuse protects all of the circuit , but bad practise to do so. At the end of the day , if you test a ring circuit do you check every plug unplugged to see if the fuse rating is correct . probably not. the heating engineer should ideally be the one to check the fuse rating at the spur.
 
Not fitting the appropriate value of fuse in the fuse connection is dam lazy and a sign of poor workmanship.

You did the right thing changing them as its good practice.
 
Speed of operation between a 6A mcb and a 3A fuse would be (without looking it up) negligible. So in my opinion,theoretically, the fuse did not need to be changed. Regulations probably say it should be changed. Good practice ? that,s only a viewpoint.
 
The cable is protected upstream, so it still protects the cable even with the 13 amp fuse, bit pointless really :/
 
The fuse is the FCU would be to protect the equipment. And the cb to protect the cable.
Also it should provide discrimination so The local device operates before the entire circuit.
You definitely done the right thing.
:)
 
The fuse is the FCU would be to protect the equipment. And the cb to protect the cable.
Also it should provide discrimination so The local device operates before the entire circuit.
You definitely done the right thing.
:)

Would the local device operate before the entire circuit protection ? (3A fuse V 6A mcb) Don,t think anybody could say or prove that. I know you are quoting regs, and rightly so, but the originator was posting a theoretical question and is theoretically right.
 
In the event of a fault I tend to see the local fuse to bs 1362 operate first in TN installations.
If TT, then it will not protect against an earth fault. Like any device. Apart from a Rcd/RCBO.

In theory the max zs Is less than half for a 3 amp 1362 so it should operate first.
 
I've seen PCBs burnt out because they were protected by 13A fuses instead of 3A, even on circuits protected by 5A 3036s.

In the event of a short circuit within an appliance it's anyones guess which of either a 3A 1362 or a 6A B type would trip/blow first. However, in the case of an overload which can be caused by something as simple as a loose connection within the FCU (as experienced first hand), if the FCU is fitted with a 13A 1362 the 13A won't blow, and by the time the 6A B type trips (if it ever does), the PCB is already fried. Also, as most boilers are fed via FCUs on 32A/20A circuits, if protected by a 13A 1362, there ain't no chance on this earth that it's gonna blow in time to save anything should a fault occur within the boiler. The only way to protect a boiler in the event of an overload is to fit a 3A 1362.

I believe it's also a requirement in the Gas Safe regs to protect a boiler with a 3A overcurrent protective device. As I was told once before, it ain't just our regs we have to work to!
 
it,s usually the manufacturer that specifies a 3A fuse in the spur and if not fitted they can invalidate a warranty claim.When I was wiring heatings for B G a few years ago I used to pick up a box of fused spurs and change the fuses in them all to 3A it only took five minutes and was one less thing to do when you got to site.
 
Not sure where your all getting your information from, as to plug top/FCU fuse protection. Fuses within these accessories are there purely to protect the flexible cable connected to them. Protecting the equipment in any way is purely coincidental!!

If the manufacturer of an appliance requires a form of OL device to protect components within an appliance, then it should be provided by the manufacture. So in essence, the installation circuit wiring is protected by a suitable rated MCB, Fuse etc, located in the CU/DB. Appliances with a manufactures factory fitted lead/flex with a fusible plug top or is connected to the power source via a fusible connection unit, the fuse is protecting the lead flex, ...Not the appliance!!
 
Not sure where your all getting your information from, as to plug top/FCU fuse protection. Fuses within these accessories are there purely to protect the flexible cable connected to them. Protecting the equipment in any way is purely coincidental!!

If the manufacturer of an appliance requires a form of OL device to protect components within an appliance, then it should be provided by the manufacture. So in essence, the installation circuit wiring is protected by a suitable rated MCB, Fuse etc, located in the CU/DB. Appliances with a manufactures factory fitted lead/flex with a fusible plug top or is connected to the power source via a fusible connection unit, the fuse is protecting the lead flex, ...Not the appliance!!
Normally in the installation manual for the boiler it states that the appliance must be fed via a 3A fuse and a double pole isolator with a minimum contact separation of 3mm.
 
You did the right thing. The MCB is there to protect the cable, and the fuse in the spur is there to protect the appliance flex, but by default is will also protect the appliance.

I agree, the 6a MCB would most likely trip before the 13a fuse, but by fitting the correct fuse you have it all covered.

And as an earlier post stated, you will maintain any warranty.

Cheers.......Howard
 
Agree with Engineer54, in my particular boiler the PCB,relays,etc (24V circuit) are protected with a 100mA fuse and the pump,fan,solenoids,etc (240V circuit) are protected by a 2A fuse. (both boiler manufacturer,s fuses). This surely puts to bed the idea that the 3A/13A fuse, & 6A mcb protective devices forementioned are not intended to protect the appliance, only the circuit cabling. Nicsin02 posted a worthwhile topic, though don,t think anyone would disagree that the 3A fuse is more appropriate.
Congrats to lively and knowledgeable participants in this forum,as an ex leccie, I love to browse it.
 
in my particular boiler
This surely puts to bed the idea that the 3A/13A fuse, & 6A mcb protective devices forementioned are not intended to protect the appliance
In your particular boiler no, you're probably right, however some of the cheaper boilers come with only the 3A fuse in the plug to protect them. As do most appliances.If fuses weren't meant to protect appliances as well as the cable, then every appliance utilising flex with a csa of 1mm or over would automatically come with 13A fuses?? But they don't do they? In fact, if I'm not mistaken, most boilers are fed with 1mm flex so surely a 13A fuse would be ok as it protects the cable feeding it??Somehow I think the legal requirement to protect boilers with 3A fuses has got more to do with protecting the boiler than the cable.
 
In your particular boiler no, you're probably right, however some of the cheaper boilers come with only the 3A fuse in the plug to protect them. As do most appliances.If fuses weren't meant to protect appliances as well as the cable, then every appliance utilising flex with a csa of 1mm or over would automatically come with 13A fuses?? But they don't do they? In fact, if I'm not mistaken, most boilers are fed with 1mm flex so surely a 13A fuse would be ok as it protects the cable feeding it??Somehow I think the legal requirement to protect boilers with 3A fuses has got more to do with protecting the boiler than the cable.

It may be of interest that The Code of Practice for In-service Inspection and Testing of Electrical Equipment:3rd Ed, Table 15.6 lists 1.25mm[SUP]2[/SUP] as the minimum CSA for an appliance cord or flex protected by a 13A BS1362 fuse and 0.5mm[SUP]2[/SUP] minimum for a cord or flex protected by a similar 3A fuse.
 
Comparing data for a 6A BS 60898 Type B MCB or BS 61009 RCBO from BS7671:2008+A1:2011 Fig 3A4 with a 3A BS1362 Fuse from the Bussman catalogue datasheet:
6A MCB requires a prospective overload current of 30A to trip in the conventional time.
3A Fuse requires a prospective overload current of between 12 and 18A in the conventional time.
[FONT=&amp]Therefore discrimination is likely to be achieved in this case.[/FONT]
 
In your particular boiler no, you're probably right, however some of the cheaper boilers come with only the 3A fuse in the plug to protect them. As do most appliances.If fuses weren't meant to protect appliances as well as the cable, then every appliance utilising flex with a csa of 1mm or over would automatically come with 13A fuses?? But they don't do they? In fact, if I'm not mistaken, most boilers are fed with 1mm flex so surely a 13A fuse would be ok as it protects the cable feeding it??Somehow I think the legal requirement to protect boilers with 3A fuses has got more to do with protecting the boiler than the cable.

"Some of the cheaper boilers come with only the 3A fuse in the plug to protect them" ??
I find this hard to believe, and if so, the manufacturer of that boiler would surely be negligent in their protection of the boiler components, PCB in particular.
 
It may be of interest that The Code of Practice for In-service Inspection and Testing of Electrical Equipment:3rd Ed, Table 15.6 lists 1.25mm[SUP]2[/SUP] as the minimum CSA for an appliance cord or flex protected by a 13A BS1362 fuse and 0.5mm[SUP]2[/SUP] minimum for a cord or flex protected by a similar 3A fuse.

Very true, it also says it in the regs. Oh well 1mm/1.25mm, both the same thing really :D
 
"Some of the cheaper boilers come with only the 3A fuse in the plug to protect them" ??
I find this hard to believe, and if so, the manufacturer of that boiler would surely be negligent in their protection of the boiler components, PCB in particular.

Not if the PCB is built to handle 3A. Like I said in my first post in this thread, I've seen PCBs fried because the boiler was protected by a 13A fuse instead of a 3A fuse.
 
Irrespective of what a manufacturer states on the appliance or boiler or what have you, the 1362 fuse in a plug-top or FCU is there purely to protect the flexible lead/cable and NOT the appliance itself. As i have stated earlier any protection to the appliance by a 1362 fuse rating, is purely coincidental.... Any appliance protection requirements are down to the manufactures themselves. Obviously it is down to the end user to fit an appropriate sized 1362 fuse to the plug-top or FCU...
 
Not if the PCB is built to handle 3A. Like I said in my first post in this thread, I've seen PCBs fried because the boiler was protected by a 13A fuse instead of a 3A fuse.

PCB,s are not built to be protected by a CIRCUIT fuse of 3A or any other size. Leave that to their designers to protect it. A short circuit in a PCB will "fry it" normally anyway whatever the protection. I have also seen PCB,s fried, and with lower than 3A protective devices.
 
So if boilers are to have their own protection fitted internally by the manufacturer, why is it that the last boiler I took apart had no fuse apart from the 3A in the plug it came with? I'm not doubting what any of you are saying, but I find it hard to understand how the componets would be protected if you say they are not built to handle 3A and yet the only protection they have is 3A?
 
I find it hard to understand how the componets would be protected if you say they are not built to handle 3A and yet the only protection they have is 3A?

That question is best asked to the boiler manufacturer, rather than to the forum.... It'll be interesting to see what they have say too!! ...lol!!
 
So if boilers are to have their own protection fitted internally by the manufacturer, why is it that the last boiler I took apart had no fuse apart from the 3A in the plug it came with? I'm not doubting what any of you are saying, but I find it hard to understand how the componets would be protected if you say they are not built to handle 3A and yet the only protection they have is 3A?

You make a pertinent point regarding protection, (or lack of protection in some cases) of boiler PCB,s. The 3A fuse that is required in the FCU or plug top, in my opinion, WILL protect boiler components, if there is no manufacturer,s protective device, but probably not the PCB. I don,t understand why a boiler manufacturer would not include a say, 100mA fuse to help protect the PCB(would cost them little) Could it be that they make a lot of money from replacement PCB,s Gosh, shouldn,t be thinking that.
 
That question is best asked to the boiler manufacturer, rather than to the forum.... It'll be interesting to see what they have say too!! ...lol!!

Haha, I'd love to, but I do have a life. Last thing on my mind of an evening is getting into an over the phone debate with a boiler manufacturer! :D
 

Reply to Fuse size? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
306
Hi, my friend is having a floating shelf with a electric fire, and I’m between minds where to put the socket, I was gonna put the socket behind...
Replies
3
Views
721
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
939
Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
Replies
1
Views
653

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top