Discuss Garage Board - achieving discrimination? in the UK Electrical Forum area at ElectriciansForums.net

Michael, you have missed some essential points.

1. The new tails (heading towards the garage) MUST pass through a current limiting device. RCDs do not limit the current.
So a switch/fuse is needed at that point (I think I detailed this in this thread about 6 months ago. I CBA to read all the way back).
The fuse needs to be appropriate for the SWA.

2. A time delay RCD (or any RCD) is NOT necessary at the house end.
 
Michael, you have missed some essential points.

1. The new tails (heading towards the garage) MUST pass through a current limiting device. RCDs do not limit the current.
So a switch/fuse is needed at that point (I think I detailed this in this thread about 6 months ago. I CBA to read all the way back).
The fuse needs to be appropriate for the SWA.

2. A time delay RCD (or any RCD) is NOT necessary at the house end.

Absolutely agree about switch fuse, schoolboy error.

I agree time delay "might" not be necessary, but it gives another level of protection I think is worth the extra small cost.
 
Dave, unsurprisingly you are correct. Had time to check my understanding this morning. Obvious when you take time to think about it.

So best solution would be pull tails from house CU into service block. Then new tails into house CU and new RCD enclosure with time delay RCD. Then SWA to garage CU with RCD.
Cheap simples and best soloution. Any fault in garage will only trip garage RCD, with SWA cable also protected by time delay RCD.

Why the time delay RCD?
 
No, please do start as this thread has improved my knowledge which has got to be a good thing. And hopefully for others.

Agreed time delay RCD does not provide shock protection, but it does still provide earth leakage protection. So I'm still thinking it's a good thing ?
 
No, please do start as this thread has improved my knowledge which has got to be a good thing. And hopefully for others.

Agreed time delay RCD does not provide shock protection, but it does still provide earth leakage protection. So I'm still thinking it's a good thing ?

Why does it need earth leakage protection?
 
So that begs the question; what use does a time delayed RCD have?
We know it must be used for RCD's in series.

Time delayed RCDs are used to achieve discrimination where the upstream device is providing fault protection because the required EFLI for the mcb or fuse cannot be met. For example TT systems where you can rarely achieve a low enough Ra to allow mcbs or fuses to operate in the required time.
 
As a s type max allowed tripping time is 500ms and 130ms min tripping time then I wouldn't particularly use it where you need a disconnect time of 0.2 seconds for final circuits upto 32 amps(depending on rcd tripping time when tested) 100ma standard device would be used for fault protection only.
Where a s type is useful is protecting tails entering a metal enclosure and distribution/circuits above 32amps which have generally a 1 second disconnect time and discrimination against downstream rcds.
For a TT system
 

Reply to Garage Board - achieving discrimination? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
791
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
889
Hi this may be a simple answer to my question but I can't find the answer in the regs If im fitting a garage board from a consumer unit with RCD...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock