Discuss Garage Sockets Regulations in the The Welcome Forum area at ElectriciansForums.net

Steina

-
Reaction score
0
Hi everyone
I've been out the business a long time and am rusty on regs. Perhaps someone can assist?

My son has an armoured cable fed from his house CU via a dedicated mcb to his detached garage.

This cable is connected to a 'Lewden' 'garage' CU consisting of a 6A mcb feeding two small flourescent light fittings and a 16A mcb feeding one double switched socket.

He uses several rechargeable drills/tools etc in his job and currently uses two 4-way extension leads to recharge everything.

I'm proposing installing four additional double switched sockets and returning to his garage CU to change the feed to a ring. I appreciate this means I need to change his 16A mcb to a 32 A mcb.

To save changing the 16A for a 32A, is it within the regs to simple add four more sockets i.e. have five in total on a single cable?
 
So what you're saying is you've never been in the business you're a DIYer that wishes for some advice.

Yes, you can add four more sockets. I'm sure those who do domestic work will correct me if I'm wrong here, but this work will be notifiable to building control, and will need a minor works certificate producing.

- Corrected by others, not notifiable if it stays as a radial circuit and is already RCD protected.
 
Last edited by a moderator:
The additional sockets would need RCD protection (take it's a domestic garage). If the circuit remains as a radial, it would not need a compliance cert.

As Rob said, what level of competence, expertise and test equipment do you have?
 
Yes you can add extra sockets to the 16A circuit, however the sockets require RCD protection.
No there is no requirement to notify.
Easiest way to provide RCD protection, would be to swap the 16A MCB for either a 16A or 20A RCBO.
 
To clarify:
I'm a timed served electrician who then qualified as an engineer. I've worked in the Merchant Navy as an Electrical Engineer and Nuclear Power Stations. This experience removes me from the DIYer status but have not worked in domestic situations since I was in my early twenties (50 years ago!) and am therefore not familiar with current IEE Regs.

My original question is to ascertain whether I'm acting within regulations (whether building or IEE) in simply adding four more sockets to his existing radial circuit or do I have to make the radial a ring circuit and change the 16A mcb to a 32A mcb.

Much appreciate any help.
 
To clarify:
I'm a timed served electrician who then qualified as an engineer. I've worked in the Merchant Navy as an Electrical Engineer and Nuclear Power Stations. This experience removes me from the DIYer status but have not worked in domestic situations since I was in my early twenties (50 years ago!) and am therefore not familiar with current IEE Regs.

My original question is to ascertain whether I'm acting within regulations (whether building or IEE) in simply adding four more sockets to his existing radial circuit or do I have to make the radial a ring circuit and change the 16A mcb to a 32A mcb.

Much appreciate any help.
You do not have to change from radial to ring.
You do not have to change the MCB from 16A to 32A.
What you do have to do, is provide RCD protection for the new sockets.
This can be by using RCD sockets, swapping the 16A MCB for an RCBO, installing an RCD before the garage CU or by providing RCD protection at the house.
 
To make any changes means that the changes you make must comply with current regulations Spinlondon has summarised this effectively.
It should be clarified that this RCD protection should be 30mA and that if there is already such protection further protection is not required.
You would also need to provide a minor electrical installation works certificate detailing the compliant results of your testing.
All this is assuming that the basic factors of the existing circuit are currently safely and compliantly installed.
Under building regulations in England, almost no matter what you do, if it is described in the above posts, it would not be notifiable work.
 

Reply to Garage Sockets Regulations in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
198
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
443
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
628

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock