Discuss Garden lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
92
hello guys

I have a garden lighting install coming up,
Everything is decided apart from the type of cable to use.
We have bedding lighting on a 30ma RCD so I assume I can do away with SWA or if anyone has any suggestions?
 
Is any of the cable buried.

Yes sorry I should add a little more detail.
So we have a control box that will have the supply from the house in SWA run surface.
However my concern is that we will have flexible cable running from the control box the the final lighting positions.
I will be leaving the flexible cables on the flower bed not buried.
 
Flex trailed over a flower bed sounds like an absolute lash up. I wouldn't be trying to lessen the risk of impact on these cables through enhanced or additional protection, but thinking about redesigning the install so that trailing surface cables can be avoided. Section 714 also applies.
 
Just looked online at garden lighting kits. Appear to be plug and play kits that let you highlight what you want round the garden by plugging directly into a mains socket. No mention of cable fixing or protection.
 
Installing lighting on a flower beds will always be tricky. Bury the cables, even if protected there is a high chance of damage. Leave them trailing surface, unprotected, over time they may become concealed leaving a bigger hazard after all people become forgetful that they are there.
 
Flex trailed over a flower bed sounds like an absolute lash up. I wouldn't be trying to lessen the risk of impact on these cables through enhanced or additional protection, but thinking about redesigning the install so that trailing surface cables can be avoided. Section 714 also applies.

Lash up job... I think you miss understood the system I am using.

The control box has an swa supply, from this box are 2-5 meter hard wired pond flexes that are fixed solid into the ip 65 fittings so the only alternative I have would be flexible conduit which someone has suggested.

The term lash up is a little bit strong in my opinion.
 
just bury some pvc conduit where they trail off into the beds, or place the lights in a location where you could clip them to something? It suggest NYY as its UV resistant and fairly tough against minor impacts, you will need a blowtorch to strip it though in this winter weather.
 
Flex trailed over a flower bed sounds like an absolute lash up. I wouldn't be trying to lessen the risk of impact on these cables through enhanced or additional protection, but thinking about redesigning the install so that trailing surface cables can be avoided. Section 714 also applies.
I agree, garden lighting is always a pain in the proverbial. Can't you drop the job and do a nice Couple of CU changes instead? Oops that sounded a bit sarcy, honestly, they are usually more trouble than they are worth.
 

Reply to Garden lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
543
Hello all, I think I might have done gone and ducked things up. We got a timer frame single story extension put on( 35sqm) For the Lighting...
Replies
4
Views
577
A
the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3...
Replies
4
Views
470
Hi all, I am planning to install wall lights such as these ones (LAP Bronx Outdoor Up & Down Wall Light Black - Screwfix -...
Replies
5
Views
718
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock