Discuss Getting rid of economy 7 tariff and Smart Meter in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Buying a house that has a mechanical meter with rotating dials that then branches into two modernish digital meters (not Smart), one for economy 7 and the other for the rest of the electrics. I only want a single tariff so if I have a Smart Meter fitted for free I assume they will take all three meters away and just connect the two separate fuse boxes on to the Smart Meter but looking at online pics I only ever see two wires shown as coming out of the Smart Meter to the domestic fuse box. I wont have the funds to upgrade the electrics to a single trip consumer unit until later. BTW anyone know the maximum ampage that a Smart meter is rated for as I will want two electric showers and cooker in the future (but the economy 7 heaters will be removed for gas).
 
If you are installing gas heating you would be better having this for the showers too.

Electric showers are not a s good as mains. (generally.)

As for the meter rating it's more to do with the fuse the DNO installs.

Here the fuses are generally 100A but in some areas they are 80A or even 60A.

As for smart meters and E7 I have no idea as they have not made it to my area yet.
 
Welcome to the forum wrf12345.
If you could upload a quality photo of the gear that is there now we could advise on what would be expectedly done and also your future thoughts for your install - a good crisp photo will allow us to zoom in and read the ratings.
Cheers
 
a good crisp photo

Here you go mate.

upload_2019-3-30_13-13-18.png
 
"If you are installing gas heating you would be better having this for the showers too." May just have one electric shower, I don't use hot water or CH for eight months of the year to save on gas costs, find the small Triton 8kw showers are fine. Have not yet moved in so photo will have to wait.
 
WPD standard domestic supply is 15kW. The nearest fuse size to this is 80A (15,000/230). Even if your existing is 100A it is quite possible that this could be swapped for an 80A one if they attend your property. The old type of meters are generally rated at 80 or 100A, no idea re smart? meters
 
Calculating the maximum demand for an installation is not just a matter of adding up all the individual potential loads. A diversity factor can be applied to many loads, but not instantaneous water heaters, which, as far as design is concerned , are assumed to be constantly on.
At 8kW each, two alone exceed the maximum load for a standard UK domestic supply (15kVA), with no allowance for anything else, so no reputable electrician will fit and certify these, unless an additional controller is fitted that only allows one shower to be used at a time.
 
"If you are installing gas heating you would be better having this for the showers too." May just have one electric shower, I don't use hot water or CH for eight months of the year to save on gas costs, find the small Triton 8kw showers are fine. Have not yet moved in so photo will have to wait.

With the assumption that you're having gas central heating and a combi boiler installed, I reckon that what you save on gas costs with an electric shower will be more than spent on the cost of the shower and the electricity to run it.
 

Reply to Getting rid of economy 7 tariff and Smart Meter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
405
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
576
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
439
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock