Discuss Glass washer tripping RCD in the Electrical Appliances Forum area at ElectriciansForums.net

S

Simmo79

Hi there. I was wondering if someone could help me... Glass washers are not my usual 'thing'.. The Lambrr glass washer in my girlfriends work is tripping the RCD. It was tripping every time she tried to turn it on and start a wash cycle, so I opened it up, fixed a small leak, dried it out etc.... Now it does a full cycle, it washes well with hot water. But it trips the RCD still a few seconds after the wash is completed, making it annoying for the bar staff. Anyone have any experience with this kind of thing know what's next.
 
As above. You need to be conducting tests on the circuit to find where your fault is.

After confirming the circuit is alright, you could conduct a ramp test if you suspect the washer to be faulty. For example a 30mA RCD may trip at 12mA by conducting a ramp test with the suspect appliance connected and then at 27mA with the glass washer removed.....
 
If it always trips at one point in the cycle, you could try to identify what is being energised at that point. After washing, maybe rinse-agent dispenser or water softener regeneration valve, or the element is ? If it has an electronic programmer, it might be difficult to identify by running the appliance as the act of energising the faulty load will kill the supply and reset the program. A camswitch programmer will obviously stop with the faulty load energised. This is where a trained service agent will have the advantage as he will know / have data on what happens when. It might be necessary to isolate the loads from the controller and IR test them - elements are frequent suspects as mentioned above.
 

Reply to Glass washer tripping RCD in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
479
I have Curry's Essential tabletop dishwasher model CDWTT115 for nearly five years. Earlier this year my machine have stopped running during a wash...
Replies
0
Views
499
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock