Discuss Global Insulation resistance testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Gazthesparky

-
Arms
Reaction score
128
I was doing a fuse board update the other day and normally I use duel RCD boards with mcb s but instead I used separate Rcbos due to the customer specifying these. I prefer fitting Rcbos due to just that one circuit is disrupted when there is a fault.

when quoting for the job I carry out a quick few tests which include a global L,N to earth to check for faults

then as I'm terminating the circuits on the day of the upgrade I carry out the insulation Resistance test on each circuit.

it then got me thinking can you carry out a global insulation test on the incoming tails like you use to be able to on Bs3036 boards

I haven't got my BGB with me at the moment it's at work but I'm sure that in there it states that RCDs should not be IR tested (plus they are sensitive to the test voltages) hence you can no longer carry out a global IR Test.


Im sure that you carnt carry out a global test anymore due to the RCDs /RCBOs but I just thought I would throw it out there and see if anyone has other ideas quicker ways to carry out insulation tests without having to do every circuit individually
 
I'm sure that most of the people doing cheap EICR's simply guess the IR for the report!

As far as I'm concerned the only way to IR a board with RCD's or RCBO's is to disconnect them!

Unless anyone can advise otherwise??
 
I've seen people test on 230v when RCD or RCBOs are used,
That will explain why they can do 3 Semi detached houses in a day full EICR and paperwork
 
How do you record the IR's for each circuit on your schedule of test results?
Global is fine for a "quick test", but I'd never use it as standard test procedure following a CU change.
IR test RCBO's at your own peril....
 
When I sat my 2391, our tutor taught that if you were wishing conducting a global I/R, then you would record the minimum values obtained and hence record this value on your schedule of test results. Obviously if any really low values were discovered then these would want further investigation.

Chris
 
If you wanted to do a global IR when you have RCDs and RCBOs, then just link all the lines from the top of the breakers (etc) together (out of the connections) and then test to the neutral bar and earth bar (and E-N).

Not quite as quick as a turn the MCBs on test but quicker than individual testing.
Global IR is a suitable method for testing, so long as you get good results, it is the bad results that then take the time.
 
You cant IR RCD's/RCBO's, read the manufacturers instructions.

IR test of the full installation, if you do this, then as long as the reading is above the minimum allowed, then you record that result in all the appropriate boxes. I agree, and i also prefer one test one circuit, but that doesn't mean the other way is wrong, bad practice or whatever, it is in GN3 so it is good practice and we have to live with it. I dare say that in time this practice will die off, due to RCD's etc.

Cheers........Howard
 
Last edited by a moderator:

Reply to Global Insulation resistance testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
618
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
678
Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just...
Replies
11
Views
3K
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Replies
9
Views
2K
Evening chaps, I've been asked to do a visual inspection, and an insulation resistance test on a fishing boat, which is working off 24v, this is...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock