Discuss Hager SFT240 Changeover Switch in the UK Electrical Forum area at ElectriciansForums.net

harrism

DIY
Reaction score
0
hello guys, hope you’re all well.

We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric hookup and a generator on board.

We were looking for a bit of advice if possible please? (We’ve actually asked several independent sparkies to come aboard, which we get either no response or a big NO :) )

There are consumer units on the three boats, each has a caravan type / 32A hook up plug to the boat. However, the past few weeks has been awful weather and the electricity kept going off with the storms. We all have on board generators, so we’d like to be able to easily switch between mains electric and on board electric.

The Hager SFT240 din rail changeover switches have arrived, lovely and small instead of big bulky pieces of equipment. The question is the wiring (and I’ve spoken to Hager support who say that there is no tech notes on them 🤔)

Would the wiring be the following:

Good afternoon, we have purchased Hager SFT240 as a changeover switch. This will be used on live aboard boats with a mains incoming connection, or if out at sea on a generator. Please can you confirm the correct wiring for these switches. Are we correct in saying:

1: Line to main fuse board
5: Neutral to main fuse board

2: Mains Line in
4: on board generator Line in

6: Mains Neutral in
8: on board generator neutral


Many thanks in advance
 

Attachments

  • IMG_8057.jpeg
    766.4 KB · Views: 11
You will probably need more isolators- the changeover switches also need DP switches on each side

What I mean is
1 DP switch for OFF grid > changeover switch
and
1 DP switch for ON grid > changeover switch

I have a second DB at home and I have a Hager SF363 DP changeover switch

The switch I have has a bottom common point- this works well in my consumer unit as the mains comes out of the bottom and feeds the MCB's as well as the neutral bar

I also have an earth rod when working in Island mode
 
You will probably need more isolators- the changeover switches also need DP switches on each side

What I mean is
1 DP switch for OFF grid > changeover switch
and
1 DP switch for ON grid > changeover switch

I have a second DB at home and I have a Hager SF363 DP changeover switch

The switch I have has a bottom common point- this works well in my consumer unit as the mains comes out of the bottom and feeds the MCB's as well as the neutral bar

I also have an earth rod when working in Island mode
in this case, is the dp isolator required?

assuming the changeover sw is 3 position i.e. grid-off-gen then the board can be isolated if required.
if the changeover sw needs maintenance then turn off the generator and unplug the shore supply.

or am i missing something??
 
in this case, is the dp isolator required?

assuming the changeover sw is 3 position i.e. grid-off-gen then the board can be isolated if required.
if the changeover sw needs maintenance then turn off the generator and unplug the shore supply.

or am i missing something??
Yes
Can that isolator be locked in the off position?
 

Reply to Hager SFT240 Changeover Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
FYI --- This is a U.S. installation. I'm replacing a three way switch (the UK might more sensibly call it a two way switch??) with a Kasa Smart...
Replies
4
Views
777
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
811
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
856
Hi - On our small vessel we have a 12v failry powerful motor to run the autopilot, where the power is supplied by the boat's battery bank. On an...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock