Discuss Heat mat fault, neutral earth reading... in the UK Electrical Forum area at ElectriciansForums.net

SSE

-
Reaction score
22
A neighbours underfloor bathroom heating mat stopped working a while back, she asked me to look at it today. Turns out when it was installed the joiner had accidentally burst the cable for it. It's a small thin blue cable that heats up that has two conductors & an earth. Someone has done a repair on it underneath floor which looks like they have used proper kit, crimps, heat shrink etc. I've just took a voltage reading at the programmer which is fine going in & out & Ive peeled off the heat shrink & took a reading between each of the conductors & earth & on one I'm getting 150v & the other I'm getting 90v. Any ideas? Mat just needing replaced I'm guessing.
 
A neighbours underfloor bathroom heating mat stopped working a while back, she asked me to look at it today. Turns out when it was installed the joiner had accidentally burst the cable for it. It's a small thin blue cable that heats up that has two conductors & an earth. Someone has done a repair on it underneath floor which looks like they have used proper kit, crimps, heat shrink etc. I've just took a voltage reading at the programmer which is fine going in & out & Ive peeled off the heat shrink & took a reading between each of the conductors & earth & on one I'm getting 150v & the other I'm getting 90v. Any ideas? Mat just needing replaced I'm guessing.
Have you carried out any other tests other than checking voltages at various points, IR as an example.
 
Yes. Checked the resistance & it was fine & so was the IR from conductors to earth. Strange.
Thanks SSE is the fault the heating not working, tripping the RCD or CB, or what, sorry to be blunt but without knowing the exact fault it's hard to suggest what the problem might be.
 
Thanks SSE is the fault the heating not working, tripping the RCD or CB, or what, sorry to be blunt but without knowing the exact fault it's hard to suggest what the problem might be.
Sorry Mte read the thread , no mention of exact fault, but title says Nto E fault, could the chippy have damaged the cable you mentioned elsewhere?
 
What was the resistance between L and N? If it's high, the heating cable may be damaged (but not a clean break) and not touching the earth, hence good IR readings
 
Hi,where were your voltages measured,and with what?
Has it got a temp sensor?
Has the joiner been water-boarded?
 
What was the resistance between L and N? If it's high, the heating cable may be damaged (but not a clean break) and not touching the earth, hence good IR readings

Resistance was about 58 ohms which was pretty much bang on for the size of mat.

Hi,where were your voltages measured,and with what?
Has it got a temp sensor?
Has the joiner been water-boarded?

Correct voltages measured at cable that leaves programmer, odd voltages taken at the cable repair crimps. The cable that leaves the programmer is obviously not the same cable/wires that heats the mat, they obviously join at some point. Would be good to be able to get a reading where the cable changes but it's buried under the tiles somewhere! It has a floor sensor. Haha, joiner waterboarding is a great shout!

Thanks SSE is the fault the heating not working, tripping the RCD or CB, or what, sorry to be blunt but without knowing the exact fault it's hard to suggest what the problem might be.

She said it wasn't working but it seemed to me to be working ok but when she mentioned the repair that's when I noticed the odd voltage readings.

Sorry Mte read the thread , no mention of exact fault, but title says Nto E fault, could the chippy have damaged the cable you mentioned elsewhere?

Possibly yes but will never know now unless tiles are lifted!

If you've checked the resistance of the conductors and it's 'fine', and IR to earth is good, and there is full voltage at the cold tails then it'll work. As it doesn't one of the above is clearly amiss.
Apparently it works intermittently. Why the strange voltages at the repair crimps though?
 
you say IR value reading is good but no mention of the value, could you supply the IR value for L/E & N/E on the mat & test voltage used to measure.
sorry not saying you have not carried out correctly but would like to know the values.
 
Ok. Update, she doesn't seem to think it's working correctly as there's one area where a tile is cold, then one where a tile is a lot warmer than the rest. I redid all the tests today, resistance between the two conductors is as it should be, around the 58 ohms mark, I done an IR again live to earth >299, neutral >299. Reading at the programmer is still the same, 230v leaving programmer but still voltage between both conductors & earth at the join. A friend who is also an electrician looked at it today & he thinks it's ok, possibly something to do with the type of mat or the actual cable/wires that heat up but I'm not so sure. It's like the voltage (240ish) is split exactly over the two conductors, judging by readings at join. I also bypassed the programmer & results are still the same.
 
well if your readings are correct & the programmer is working, check the Resistance of the sensor with multi meter just to make sure.
next thing get the mat up hot for couple of hours & use IR camera then should be able to trace the heat pattern around the floor, this should show if any of the heat mat has been laid under the cold spot or not, same with the hot spot might have been the spare if any & have a more dense area of the heat mat in that area.
IR camera will tell you also you can check the joint same time.
 
Ever heard of volt drop across a resistor?

You think this is why I'm getting those readings?

Do you know how the mat is laid out ?
And how its's wired.
Is it just one continues run ?
Or are there several area's all coming together somewhere ?

Spoke to joiner today, says it's one big continuous run, one mat. It's only an area of 6m squared. He says hotter & colder tiles are common due to density of tile adhesive.

well if your readings are correct & the programmer is working, check the Resistance of the sensor with multi meter just to make sure.
next thing get the mat up hot for couple of hours & use IR camera then should be able to trace the heat pattern around the floor, this should show if any of the heat mat has been laid under the cold spot or not, same with the hot spot might have been the spare if any & have a more dense area of the heat mat in that area.
IR camera will tell you also you can check the joint same time.

Can I ask why I've to test the sensor? Afraid I've not got an IR camera. Thanks for the suggestion though, would have been ideal.
 

Reply to Heat mat fault, neutral earth reading... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Got to look at a job where the builder has cut through the underfloor heating mat and it’s gone right through the heated cable. Not...
Replies
3
Views
746
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock