Hi
What is min distance between hot water pipe and swa or cat6 cable? can be run in the same box or no? I Just asking because plumber said its ok.For me not .I told him to put insulation on hot water pipes to keep normal ambient temperature.he said i dont need. Please help
Thanks
 
Separation of LV and cat6 is required. They should not be in the same containment. If the SWA cct has been designed with the ambient temperature taken into account obviously higher with hot water pipe then its ok. However I would say it seems silly to purposefully place a current carryingt cable next to water especially hot water. The plumber is not competent to judge electrical matters anyway. I think its a matter of what is best practice. I would be reluctant to place them together personally.
 
Agree with V. If the SWA is in a temp environment hotter than the rating temp (e.g. 30 deg in table 4D2A) then it should be derated for CCC. Some folks run their HW at 70 deg and this is the max temp for lots of our cables, so it's not a good idea, cable needs to be kept away from heat sources. Far be it from me to tell a plumber what to do, but I thought all H/W pipes had to be insulated by building regs now?
 
Hi
What is min distance between hot water pipe and swa or cat6 cable? can be run in the same box or no? I Just asking because plumber said its ok.For me not .I told him to put insulation on hot water pipes to keep normal ambient temperature.he said i dont need. Please help
Thanks
Hi - sorry I know this was a few days ago - the relevant regulation is 528.3.1
 

Reply to Heating pipe and Swa cable in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
932
Electrician has done rewire, plumber with not much space has some central heating and hot water pipes touching in some places. See images...
Replies
4
Views
2K
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
432
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
536
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock