Discuss Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net

And sorry, I forgot to reply.

It was working just fine until I decided to have a Nest Thermostat installed, and it was downhill from there..

It seemed to be working fine for a while, but maybe I just didn't notice the boiler running & overheating constantly at first.. 🤷‍♂️
 
sure - do you mean the boiler label (below)?

I WAS TOLD THIS PCB IS NEW!! I paid £250 for it... did the guy rip me off bringing me a used one??

View attachment 100150
I just loaded a manual from Google instead of their website and it looks more like yours. It appears that it doesn't accept any switched live but expects a switched signal between 3 and 4. The orange and grey cores are the switched ones from the valves and could be used for that.

Do you have a meter to test that there is 230v on terminal 4?
 
I just loaded a manual from Google instead of their website and it looks more like yours. It appears that it doesn't accept any switched live but expects a switched signal between 3 and 4. The orange and grey cores are the switched ones from the valves and could be used for that.

Do you have a meter to test that there is 230v on terminal 4?

Ok, I see..

I don't have a meter at the moment, but can go buy one if it will help!
 
one like this?
 
sure - do you mean the boiler label (below)?

I WAS TOLD THIS PCB IS NEW!! I paid £250 for it... did the guy rip me off bringing me a used one??

View attachment 100150
The white flex appears to be connected in all the right places, albeit sub-standardly.
I would turn the heating and hot water to the off position and then check to see if there is any voltage between neutral and the grey wire. The boiler and pump should only fire up when there is a demand for either heating or hot water or frost protection situation, which is highly unlikely at the moment, due to all the glorious sunshine.
 
OK, just bought a meter.

V~ 200 and on 4 and 3?

I just loaded a manual from Google instead of their website and it looks more like yours. It appears that it doesn't accept any switched live but expects a switched signal between 3 and 4. The orange and grey cores are the switched ones from the valves and could be used for that.

Do you have a meter to test that there is 230v on terminal 4?
 
The white flex appears to be connected in all the right places, albeit sub-standardly.
I would turn the heating and hot water to the off position and then check to see if there is any voltage between neutral and the grey wire. The boiler and pump should only fire up when there is a demand for either heating or hot water or frost protection situation, which is highly unlikely at the moment, due to all the glorious sunshine.
Hi, thanks

ok, so on the meter V~ 200 and on the blue (N) and grey wire (4) on the PCB?

Thank you
 
Right. So measured between the blue (N) and grey wire (4) on the PCB - and it's always 244V

No matter if the boiler is running or not.
 
Last edited:
Yes - heating and hot water being off (on the Nest)!
I would now test between neutral and brown of both of your zone valves when heating and hot water is still in the off position. Hopefully you won’t have 230 volts there. I would then separate the oranges on your zone valves and measure between neutral and each of the oranges in turn to see if one of your zone valves has an issue. Could be a micro switch issue In one or both of your zone valves.
 
I would now test between neutral and brown of both of your zone valves when heating and hot water is still in the off position. Hopefully you won’t have 230 volts there.
I have 244V
I would then separate the oranges on your zone valves and measure between neutral and each of the oranges in turn to see if one of your zone valves has an issue.
They both have 244v

😳

any ideas?
 
If you have 244v between neutral and the terminal where your brown of the zone valves are connected in your wiring centre, when the heating and hot water are in the off position, then you have a problem possibly from the nest end.
I see...

So it could be the Nest's fault after all? (I spoke to Google who wants a "diagnostic" in order to send a replacement..)

Assuming you have seen the photo of the cabling at Nest? That seems correct?

Many thanks for your help!
 
I see...

So it could be the Nest's fault after all? (I spoke to Google who wants a "diagnostic" in order to send a replacement..)

Assuming you have seen the photo of the cabling at Nest? That seems correct?

Many thanks for your help!
You shouldn’t see 230v between neutral and brown when your heating and hot water are in the off position.
 
OK, so I checked again (my heart sunk before)

and

b/w Neutral and Brown on both ZV = 0v

b/w Neutral and Orange on both ZV = 244v

All while heating & HW OFF


Apologies, about the wrong info earlier...
 
I would remove the permanent live from the valves by disconnecting the orange from the top of 11 and move it to the spare of 5. The spare black looks like it goes to the boiler. I'd connect that to 5 in the junction box and connect the black to 3 in the boiler.
 
OK, so I checked again (my heart sunk before)

and

b/w Neutral and Brown on both ZV = 0v

b/w Neutral and Orange on both ZV = 244v

All while heating & HW OFF


Apologies, about the wrong info earlier...230v should only be present between neutral and orange when you select either heating or hot water after the valve has motored open
 

Reply to Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
619
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
444
It has become a common occurrence that my boiler is failing to respond when the thermostat kicks in. I hear an audible click from the heatlink...
Replies
16
Views
2K
So a customer changed his own stat and wired it wrong and blew 3/4 fuses. Then heating was stuck on so I changed the programmer and this resolved...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock