Read all posts !!!! so what was the cause of the lights not working live cable come out of junction box ?. well done for getting to the bottom of it how come you got a shock !.
I suggest now that you have made all these holes that you get an electrician in to rewire some of the lighting circuit as possible to get rid of all those junction boxes that are inaccessible sadly this is the problem with laminated flooring installed upstairs, use a M.F. Wango box above a light fitting as Tel posted at least you could still get to the connection by removal of fitting /make the connections at one of the downlights in a Hager 501 junction box but take this opportunity to improve the accessibility.
I suggest now that you have made all these holes that you get an electrician in to rewire some of the lighting circuit as possible to get rid of all those junction boxes that are inaccessible sadly this is the problem with laminated flooring installed upstairs, use a M.F. Wango box above a light fitting as Tel posted at least you could still get to the connection by removal of fitting /make the connections at one of the downlights in a Hager 501 junction box but take this opportunity to improve the accessibility.