So I’ve finished a rewire recently and I’ve come to testing the ring circuit for the down stairs sockets and I’m not getting what I’m testing in regards to the calculation

LL: 0.36
NN:0.36
EE:0.60(there abouts)

Now when I’m doing the r1+r2 crossing the opposite live and earths but the calculation for obtaining it isn’t what I’m getting when recording the results.

So 0.36+0.36/4= 0.18



But when testing at the sockets I’m getting readings of 0.30 ohms. I’m going to try another calibrated tester this weekend.


Any advice would be appreciated

Thanks
Looks like you are using the wrong figures Mate should be R1 PLUS R2 which on this case it would be 0.36 +0.6/4 you have calculated it with r1 +rn
 
If you are testing at the socket front, switch on the switch then off a few times, also put the plug in and out a few times your reading will drop as it will remove dust and poor contact at the switch.
As Vortigern. I recently installed a new RFC and on testing at the sockets just flicking the switch a few times can give quite significant drops in resistance.
 

Reply to Help or advice with r1+r2 ring. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock