Discuss Help to wire washing machine cables into wall motor protection switch in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hello,

I have two electrical switches in my house that should be connected to the washing machine and the dryer machine, respectively. After having opened them I found 5 cables: black, white, red (connected to the central part) and yellow, yellow-green. I am nearly sure the yellow is the neutral, while the yellow-green is the ground. The black usually is the hot wire when I connect laps and similar, but I really don't know what are the other 2 cables.

After some research I understand this is a special setup that i am not familiar, but that seems pretty common for these type of switches. The switches are functional (the previous owner was using them), so I just need to know where to connect the wires from the washing and drying machines: these two machines have a classic 3 pole switch, so I expect when I cut the cable I will find 3 wires.

Could someone please help telling me whre to connect the washing machine cables? On the 3 sides of the central black part, there are the notes L1, L2, L3 and T1, T2, T3.

Many thanks for your help.

FYI: this is a Swiss house.



20220507_110259.jpg
20220507_110303.jpg




20220507_110310.jpg
20220507_110316.jpg
20220507_114003.jpg
20220507_114507.jpg
 
This is a 3-phase circuit so there are three line wires L1, L2 and L3; one neutral and the protective earth / ground. The colours follow the Swiss code that was used between 1970 and 1980.

L1: Black
L2: Red
L3: White
N: Yellow
PE: Green/Yellow

If your washing machine has a 3-core cable it is single-phase. You can use any of the three available phases L1, L2 or L3 to power it. These correspond to the switch outputs T1, T2 or T3.

Therefore:
Phase (Brown) > T1 (Black) or T2 (Red) or T3 (White)
Neutral (Blue) > Neutral (Yellow)
Earth (Grn/Yel) > Earth (Grn/Yel)

Three points to note.

Make sure the circuit is designed for the full load current of your machines. If the previous machine was 3-phase the load might have been spread across the 3 phases. E.g. old machine 3x 6A, new machine 1x 16A. Check the fuses / circuit breaker.

Related: It is probably best to connect the two machines onto two different phases so that the combined load is not drawn from one phase of the house supply. You might like to look at the way the other circuits in the house are allocated to the three phases and avoid the circuit with the highest load. This is often L1, in which case put one machine onto T2 and the other T3.

Voltage between any two lines is 400V, between line and neutral or earth is 230V

Die alten Kabelfarben sehen für mich nett aus, ebenso die Beschreibungen, wenn sie auf Deutsch sind. Außenleiter. Schutzleiter. J'aurais dû écrire tout ça en allemand, o forse francese o romancio, as I don't know where in Switzerland you are. Romansh is all Greek to me though.
 
This is a 3-phase circuit so there are three line wires L1, L2 and L3; one neutral and the protective earth / ground. The colours follow the Swiss code that was used between 1970 and 1980.

L1: Black
L2: Red
L3: White
N: Yellow
PE: Green/Yellow

If your washing machine has a 3-core cable it is single-phase. You can use any of the three available phases L1, L2 or L3 to power it. These correspond to the switch outputs T1, T2 or T3.

Therefore:
Phase (Brown) > T1 (Black) or T2 (Red) or T3 (White)
Neutral (Blue) > Neutral (Yellow)
Earth (Grn/Yel) > Earth (Grn/Yel)

Three points to note.

Make sure the circuit is designed for the full load current of your machines. If the previous machine was 3-phase the load might have been spread across the 3 phases. E.g. old machine 3x 6A, new machine 1x 16A. Check the fuses / circuit breaker.

Related: It is probably best to connect the two machines onto two different phases so that the combined load is not drawn from one phase of the house supply. You might like to look at the way the other circuits in the house are allocated to the three phases and avoid the circuit with the highest load. This is often L1, in which case put one machine onto T2 and the other T3.

Voltage between any two lines is 400V, between line and neutral or earth is 230V

Die alten Kabelfarben sehen für mich nett aus, ebenso die Beschreibungen, wenn sie auf Deutsch sind. Außenleiter. Schutzleiter. J'aurais dû écrire tout ça en allemand, o forse francese o romancio, as I don't know where in Switzerland you are. Romansh is all Greek to me though.

This is a 3-phase circuit so there are three line wires L1, L2 and L3; one neutral and the protective earth / ground. The colours follow the Swiss code that was used between 1970 and 1980.

L1: Black
L2: Red
L3: White
N: Yellow
PE: Green/Yellow

If your washing machine has a 3-core cable it is single-phase. You can use any of the three available phases L1, L2 or L3 to power it. These correspond to the switch outputs T1, T2 or T3.

Therefore:
Phase (Brown) > T1 (Black) or T2 (Red) or T3 (White)
Neutral (Blue) > Neutral (Yellow)
Earth (Grn/Yel) > Earth (Grn/Yel)

Three points to note.

Make sure the circuit is designed for the full load current of your machines. If the previous machine was 3-phase the load might have been spread across the 3 phases. E.g. old machine 3x 6A, new machine 1x 16A. Check the fuses / circuit breaker.

Related: It is probably best to connect the two machines onto two different phases so that the combined load is not drawn from one phase of the house supply. You might like to look at the way the other circuits in the house are allocated to the three phases and avoid the circuit with the highest load. This is often L1, in which case put one machine onto T2 and the other T3.

Voltage between any two lines is 400V, between line and neutral or earth is 230V

Die alten Kabelfarben sehen für mich nett aus, ebenso die Beschreibungen, wenn sie auf Deutsch sind. Außenleiter. Schutzleiter. J'aurais dû écrire tout ça en allemand, o forse francese o romancio, as I don't know where in Switzerland you are. Romansh is all Greek to me though.
This is a 3-phase circuit so there are three line wires L1, L2 and L3; one neutral and the protective earth / ground. The colours follow the Swiss code that was used between 1970 and 1980.

L1: Black
L2: Red
L3: White
N: Yellow
PE: Green/Yellow

If your washing machine has a 3-core cable it is single-phase. You can use any of the three available phases L1, L2 or L3 to power it. These correspond to the switch outputs T1, T2 or T3.

Therefore:
Phase (Brown) > T1 (Black) or T2 (Red) or T3 (White)
Neutral (Blue) > Neutral (Yellow)
Earth (Grn/Yel) > Earth (Grn/Yel)

Three points to note.

Make sure the circuit is designed for the full load current of your machines. If the previous machine was 3-phase the load might have been spread across the 3 phases. E.g. old machine 3x 6A, new machine 1x 16A. Check the fuses / circuit breaker.

Related: It is probably best to connect the two machines onto two different phases so that the combined load is not drawn from one phase of the house supply. You might like to look at the way the other circuits in the house are allocated to the three phases and avoid the circuit with the highest load. This is often L1, in which case put one machine onto T2 and the other T3.

Voltage between any two lines is 400V, between line and neutral or earth is 230V

Die alten Kabelfarben sehen für mich nett aus, ebenso die Beschreibungen, wenn sie auf Deutsch sind. Außenleiter. Schutzleiter. J'aurais dû écrire tout ça en allemand, o forse francese o romancio, as I don't know where in Switzerland you are. Romansh is all Greek to me though.
Hello Lucien,

This is so helpful, many thanks for you time responding to me! I am near Zurich, but I do not speak well German - my wife does.

The new washing machine is a Beko 9kg, and also the dryer is a Beko. I saw on the manual it should be 10A. I haven't cut the cables yet but I remember I saw 4 cables from the old dryer when they removed it. It was a Miele, but an old one.

I think most of the lines are on the black, like lamps etc. I never saw a white or red anywhere else, so it is really a good advice to connect those on the machine.

I'll write here if I need more help but I think I have enough info to try now :)

All the best

You are also right on the color code: my house is from 1981, so I think the cables are also from those years.
 
I think most of the lines are on the black, like lamps etc. I never saw a white or red anywhere else,

In single-phase circuits the unswitched line will be black regardless of which phase it is derived from. Only in 3-phase circuits do the white and red identification colours come into use. Therefore the presence of black wires throughout your installation is no indication of how the load is spread between the supply phases.
 
In single-phase circuits the unswitched line will be black regardless of which phase it is derived from. Only in 3-phase circuits do the white and red identification colours come into use. Therefore the presence of black wires throughout your installation is no indication of how the load is spread between the supply phases.
Hi Lucien,

Just wanted to thank you again. Your advice was perfect and I could do the work without any issue! Have a great day.
 
Thank you for the update!
 

Reply to Help to wire washing machine cables into wall motor protection switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
607
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
744
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
556
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
348

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock