Discuss Help with a 3 phase star delta motor in the Canada area at ElectriciansForums.net

S

sheriff78

I have been called out to replace a DOL starter that somebody fitted last year, It controls a 3 phase motor on an extraction unit. The customer has said that the fan used to start slow and then after 10 secounds it would speed up to full speed. The electrician that changed the starter replaced it with a standard DOL starter that just turns over at a slow speed. I have replaced this with a star/delta starter unit. I was hoping to find some spare cables when i opened up the unit but unfortunaley there wasnt any. So now i am puzzelled as to how it could of ever run at 2 speeds. The motor has got a 3 phase isolator mounted next to it that looks original so how could it of been wired up as star/delta if it only has the one set of cables(red,yellow,Blue)

To get the motor working with the new starter am i right in thinking that i will need 2 sets of cables 1 from the main contactor, and one from the the star/delta contactors. and then remove the links from inside the motor panel.

If this is the case will i need to mount a six pole isolator next to the motor or can i just extend the contol circuit through the isolator so that it cuts off the motor(the motor is mounted outside)

Hopefully this makes sense to somebody.

any help on this would be very appreciated
 
Usually with a DOL system there's only 3 wires between the motor and the DOL starter (four wire if you include the earth) With a star/delta system you need six wires between the motor and the star/delta control box (seven if you include earth).

I would only spec a star delta system if the motor is larger than 5.5KW 4-pole or if the blade set is plastic and is larger than 630mm diameter.

*Edit* The colours of the wiring can be confusing, rather think in terms of L1 L2 & L3 for supply and U1, U2, V1, V2, W1 and W2 for motor wiring.
 
Last edited:
Sounds like the motor used to have an inverter instead of a dol starter. This would mean the motor would be wired delta and only use 3 wires ( plus earth). This would mean the motor was 3 phase 230v. If a small motor that is. Or larger motors it could be a 3 phase inverter. This would start the motor slow and ramp up to Full speed.
 
star-delta.gif
Is this any help
 
yes there are currently 6 wires in the motor, They are linked out at the moment so that there are only 3 terminals. On the back of the plate it has got a diagram to show you how to link it out for star or delta. so it must be happy to be used either way.

My understanding is that when you connect the 6 wires up you remove the links becuase the contactors act as the links when they change over.

When i connect the motor up with 6 wires (star/delta) will this increase the speed of the motor when it changes over and if yes by how much?

also can you get 6 pole isolators for this type of motor or can i extend the control circuit to isolate it outside(the motor is mounted outside the controls are mounted internally)

If the system used to be run through an inverter. would this of increased the speed of the motor? or did the last electrician change it from star to delta because it was blowing the overload every time it started?

i ask this because the customer has told me that the fan used to start slow and then speed up. but now it just does the slow bit. but in my mind the motor will only run at one speed, either the star maximum speed or the delta maximum speed.

sorry to ask so many questions. your help is really appreciated
 
Unless I've read all this wrong then changing from DOL to YD won't gain you any speed... unless the fan is struggling to start in which you'd expect the overload to operate.

Why are you replacing the DOL exactly? What's the fault?

Can you show a picture of the motor plate or provide plate details please?

You say in post #8 "...or did the last electrician change it from star to delta because it was blowing the overload every time it started?" so what is the motor connected as now... star or delta?

So is the connection correct for the supply to the motor?

Obviously we do not know the history of the fan control. We do not know for sure whether the supply to the DOL is mains or comes from another source, perhaps an inverter or soft-start tucked away from sight in another panel. Perhaps the motor is/was a two speed motor that had a Dahlander connection
p076.gif


When fitting a six pole isolator for a YD motor ensure an isolator auxiliary is used so when the isolator is switched off it tells the YD control to stop. I've seen a few occasions where the isolator has been used to stop the motor then the motor restarts in delta when the isolator is switched back on! Nothing major on a 5.5kw motor but as you get bigger... :eek:



@ MARVO: is that your Boxer in your avatar?
 
Last edited by a moderator:
The customer may have mistaken the time taken for the motor to run upto full speed for it actually having two speeds....we all know that when a big fan starts up(dol) you get the usual rumbling humming noises until it gets to full speed then it usually quitens off a little. They may just think it had two speeds??? As fans starting loads are minimal compared to say silt pumps water pumps etc I would have expected a DOL starter as opposed to Soft start or VSD.
 
Last time I saw one was on some Baltimore Air Coil evaporative condensers on an ammonia refrigeration plant... not too long ago.

We had plenty of two speed motors though, on high shear mixers.
 
The old starter packed up about a year ago so they called an electrician to sort it, he installed a DOL starter which just turns the motor over at a slow speed. The motor is attached to a extraction fan which sucks the fumes out of 10 metal dipping tanks. the customer has tried to get the original electrician back to sort it but he has dissapered. The customer has said that the fan use to start slow for around 20 seconds and then it would speed up to full speed. I presumed that this was a star delta set-up so i have installed a new star delta starter. I need to replace the wiring because there are only 3 wires at the motor at the moment
I just need to check that the motor will increase speed when it changes from star to delta otherwise i will be back to square one
I cant remeber which way the motor is wired at the moment. It has 3 little links which can be swapped to change it from one to the other.
Which will increase the speed of the motor is it star or delta

thank for all your help and time on this
 
From what I remember if the links in the motor terminal box are in a straight line across three terminals its star...if the links are arcoss two terminals each link its delta.
Running in delta will get the max out of the motor.
 
I would also just wire the motor delta and run it on a 3-wire DOL system. At 5.5Kw Y-D isn't really necessary unless it's a large diameter plastic construction blade set. I would set the thermal overload in the DOL starter at the max run current on the motor plate minus 10%. If there's an overload tripping problem then look for the reason ie blade angle to high, fan running in reverse, blades trailing in grease build-up on the fan housing, motor bearings failing, poor winding insulation etc etc.

Soft starters, VFD's and Y-D starters are unnecessary complications and expense unless you see a good reason for them.
 
Thanks for everyones help on this.

Just one last question. if one of the windings had failed could this cause the motor to run slower ( if it was running on 2 phases instead of 3) or would it not run.

Also i have noticed that the last electrician has swapped the yellow and red phase over in the bottom of the contactor. would this cause the fan to run slower.

I am back out there on monday trying to sort things.

i will try and swap the windings from star to delta first

then if nessarcery i will wire it as star/delta.

The fan has taken out the overload after around 20mins of running a couple of times. the overload is set at 5A at the moment so i have incresed this slightly. what could cause this.

alos the fan that it is running is around 2.5foot wide
 

Reply to Help with a 3 phase star delta motor in the Canada area at ElectriciansForums.net

Similar Threads

Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
794
Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
971
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
331
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock