Guys, I have an assignment which I am struggling with but which should be easy and have read loads of books I keep going around in circles. Can you please put me back on the tracks.

The task is for the design of a RFC in a garage with the routing clipped a few centimetres below the ceiling and taken down single 20mm conduit from this height to each of the 4 double outlets. The conduit is to provide additional mechanical protection.

The Ref method is method B because of the conduit limiting the capacity for the 2,5mm cable to 23A (From 30A) [Table7.1(ii) or Table F5(i) OSG], as this is a ring to be protected by a 30 breaker this is still ok. However, as both cables go down the same conduit to the outlet there should be a grouping factor to consider. Looking at Appendix F (OSG) there is a general equation It=In/(CaxCgxCixCf), but I have three issues.

Firstly there appears to be no Cg factor for a conduit delivery in Table F3 OSG. Where can I find this info.

Secondly the numbers in table F3 get smaller the more cables, and as they go on the bottom line of the equation they will increase the It value where I would have expected it to decrease.

Thirdly once I get the grouping factor how do I apply it to the Ref Method B data to get a revised capacity.

Thanks
 
i don't think that grouping factor comes into it as it's only 1 circuit in the conduit.
 
As what Tel says.
 
The Ref method is method B because of the conduit limiting the capacity for the 2,5mm cable to 23A (From 30A) [Table7.1(ii) or Table F5(i) OSG], as this is a ring to be protected by a 30 breaker this is still ok. However, as both cables go down the same conduit to the outlet there should be a grouping factor to consider. Looking at Appendix F (OSG) there is a general equation It=In/(CaxCgxCixCf), but I have three issues.

Firstly there appears to be no Cg factor for a conduit delivery in Table F3 OSG. Where can I find this info.

Secondly the numbers in table F3 get smaller the more cables, and as they go on the bottom line of the equation they will increase the It value where I would have expected it to decrease.

Thirdly once I get the grouping factor how do I apply it to the Ref Method B data to get a revised capacity.

Thanks
I would agree with the above: single circuit, but just to explain.

The grouping factors in the case are the first row of the table "bunched in air, on a surface, embedded or enclosed" (the cable is enclosed).

As you have more cables close together any specific cable can take less current before overheating. Therefore when designing the circuit the current carrying capacity of the cable needs to be higher so that the current it is carrying does not overheat the cable.
When you have a grouping factor as a smaller number with more cables, then the calculation gives an increase in the minimum permitted current carrying capacity of the cable.
e.g. if you have a design current of 19A and a cable that can take 23A and a breaker of 20A this is fine as a single radial circuit. If you then have two circuits in the conduit, so grouping of 0.8, the current carrying capacity of the cable needs to be 20A/0.8 = 25A. So your cable is now too small (as it can take only 23A) so you need to increase the size of the cable to compensate.
 

Reply to Help With Circuit Design in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
917
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock