Discuss Help with CPC size in the UK Electrical Forum area at ElectriciansForums.net

You may be overthinking this as it seems the question is asking for minimum cable size and as clipped direct it will be T&E, therefore having determined that a 6mm T&E is adequate the 2.5mm integral CPC will be adequate also as with the low Ze and type of OCPD deployed automatic disconnection under fault conditions will be achieved well within 'spec'.

Also I think every electrician would just use 10mm2 cable anyway. That way there is room for a future upgrade to maybe a 9kw device
 
Think you'll find the fat black lines stop at 0.1 sec, with the little box telling us to consult manufacturers data just below.
One is the loneliest number that I ever knew (a song ...)
 
I think it was a good pick by Sintra at #4 ... Using the graphic supplied we can only go to 0.1 sec. As Risteard says in #8 it will likely discon quicker, but it varies by manufacturer and mcb model. And using 0.1 sec leads us to the practical cpc of 2.5mm answer too :)

Reading the report, a couple of suggestions :
  • If Ib is 36.96A and In >= Ib, then In can't be 36A ...
  • The non impacting correction factors aren't 0, they must be ...
Hope that helps, and good luck Gigsy


I get it now, anything times 0 is 0. I guess you just don't factor them in or they must be 1?
 
Hey!

I noticed the question alludes to the cable being T+E which I'm sure BS 7671 has listed in Table 4D5 with all the relevant reference methods. It seems you have used the values from Table 4D2A.

If I have given any incorrect information, someone please correct me!
 
Hey!

I noticed the question alludes to the cable being T+E which I'm sure BS 7671 has listed in Table 4D5 with all the relevant reference methods. It seems you have used the values from Table 4D2A.

If I have given any incorrect information, someone please correct me!


I don't think I could use a 2.5mm CPC so, I used table 4D2A, 2 core cable.

There is not much difference anyway and it does not change my results. 47A flat cable with CPC and 46A 2 core cable.
 
In is the rated current or current setting of protective device, so that would be 40A BS EN 60898. Therefore your tabulated calculation is slightly off as it uses 37A as opposed to 40A. You could use Ib in this calculation if overload protection was NOT required.

The picture highlighting your first R1+R2 values also show 6mm plus 2mm, however your calculations take the values of 6mm and 4mm.

The final calculation for your S value also does not quite add up either.
 
In is the rated current or current setting of protective device, so that would be 40A BS EN 60898. Therefore your tabulated calculation is slightly off as it uses 37A as opposed to 40A. You could use Ib in this calculation if overload protection was NOT required.

The picture highlighting your first R1+R2 values also show 6mm plus 2mm, however your calculations take the values of 6mm and 4mm.

The final calculation for your S value also does not quite add up either.

Thank you, I think I have corrected the errors, apart from final S value, it comes out the same every time?
 
In is the rated current or current setting of protective device, so that would be 40A BS EN 60898. Therefore your tabulated calculation is slightly off as it uses 37A as opposed to 40A. You could use Ib in this calculation if overload protection was NOT required.

The picture highlighting your first R1+R2 values also show 6mm plus 2mm, however your calculations take the values of 6mm and 4mm.

The final calculation for your S value also does not quite add up either.


I agree the final S value does not seam right, because 6mm cable has a 2.5mm CPC. You should be able to use a smaller CSA conductor than what is recommended, or at least the same. I can't see where I went wrong tho :(
 
Previous posts must be right, I must be using the wrong value for (t)

I read this chart as saying I should use the value 0.01

Other posts say I should use 0.1

I don't see why

The current is well over 200A, at which point the breaker would trip in 0.01s ???????????????

View attachment 35637
 
I believe you'd use the 0.1 value for t, giving a more "worse case scenario" and at those times you really can't split it down anymore from the information you've been given. However having recently done this I was told that you can do a super ultra worse case scenario and plug the value of 200A in as your current in relation to the corresponding t value, if your cpc complies there then you can't go far wrong.

Using 200A and 0.1 for the and 115 for k - you get 0.54mm2 so it proves your choice of cables comply
 
I read this chart as saying I should use the value 0.01
You can't use the generic tables for 0.01 second disconnection - as I stated earlier this is the definite minimum operating time but requires the manufacturer's data (which you will note is stated at the bottom of that table). So you need to know what brand of device you are using and consult manufacturer's data before using a disconnection time of 0.01 seconds - although with a sufficient fault current it is likely this will be achieved and therefore 0.1 seconds would be unduly pessimistic.
 
Hi

Just use the 0.1, that is what the time current curves in BS7671 state.
You don't have to use the BS7671 generic data. If you have the manufacturer's data for the device you are using then that is what you should use for a more realistic result.
 

Reply to Help with CPC size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
556
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
674
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
409
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I am working on a RV Park and I have a question. I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and...
Replies
0
Views
221

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock