must start by sayin am not too familiar with th forum...is there anythin in 17th that mentions the need to use steel conduit when the socket is at the other side of a wall of a classroom say...unless it is within 150mm from corner of a room, cornice or boxed in steel column etc
???????
 
If its less than 50 mm deep in the wall, or run outside of the safe areas (150mm from ceiling/wall corners) or is not run horizontally or vertically to a visible outlet, then the cable needs mechanical protection, i.e steel capping or conduit to prevent accidental damage or penetration from nails etc.
Hope this helps.
Randyrat
 
My mistake....of course I meant earthed steel trunking, or conduit, or armour sheathing (earthed).
Better to keep in the permitted zones....innit?
Randyrat
 
I'm not a fan of the Zones - they only work if everybody who is ever going to penetrate the wall knows about them.
Totally agree, seems to me there is too much crap in the regs and not enough to back it up. yeah fine we follow the regs and use the safety zones where practically possible, but how the hell does joe blogs know about them!!

obveriously common sense comes into it (i.e right above a light switch), but they have no clue about 150mm from celling or corner of walls.
 
The line has to be drawn somewhere with regard to zones.

However, it would make more sense to only allow cables (above 6A) to be installed from the floor up. Easily done, a little more expensive (with regard to solid floors), but lets face it, a lot safer.

But, why not insist on having a kind of instruction manual for a house explaining how cables are run for eg. the 150 rule?
 
Last edited by a moderator:
My reading of the 150 and permitted zones rules is that if we keep to these then we have a defence in a court as these are laid down by iee oir iet or whatever they call themselves. If an eejit wants to drill into a wall we can't be there every time to look after them. We can only do so much. If I'd wanted to be a superhero I'd have gone to SuperHero School.
 
i think the 150mm along the top of the wall and in the corner is more considered a safe zone for the likelihood that any person would require fixings this close to the ceilings or internal corners, as for the straight up, down and across coverage people have to rely on their own common senses

although the 17th edition considers that common sense will not always prevail, resulting in the 50mm deep & RCD rulings
 

Reply to hidden conduit question in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
935
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hello I’m new to the forum (posting on it anyway). I could do with some advice... Over the last 2 years I have been subcontracted (labour only)...
Replies
5
Views
3K
Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock